How to calculate the motor winding resistance ?
Answer Posted / mike
you can find the resistane by using ohms law but that only
applies to a resistive load. ie.,electric heaters. for an
inductive load you'll have to call manufacture or use an
ohm meter. on a three phase motor the resistance on all
three legs should read the same or very close and on a
single phase the run and common should equal up to what
your start winding ohms are
Is This Answer Correct ? | 13 Yes | 5 No |
Post New Answer View All Answers
why capacitance effect is predominant in underground cable transmission and inductance effect is predominant in over head line transmission?
Differentiate between real and apparent power?
how to fit 3 HP crompton gear motor with conveyor with the use of staring delta starter or ordinary starter?
does the Trivector Meter of three phase automatically takes care of the low power factor and gives the reading accordigly or it does not take care of the Power factor while giving the readings please explain
how does high earth to neutral voltage affects electronic circuit?
If there are two transformer having rating of 2.5mva, 6.6kv/440v(satr-star),and the load is 600kw then what is better to maintain less losses in transformer having both transformer in parellel or only single transformer connected to load? Please give calculated answer
What is the basis for selecting Vk/2 or Vk/4 for REF and Differential protection of Transformer and What is the significance of magnetising current
What is ST and specify its range of voltage.
how can motor both beasrings insulation resistance can be check?
what is the electrical?
I HAVE A 50A MCCB AS PER DESIGN LINE WIRE CONNECT UPWORD SIDE AND LOAD IS CONNECTED TO DOWNWARD SIDE TO THE MCCB.IF NOW ANY ONE CHANGE SUPPLY & LOAD(WISEVERSA) WHAT HAPPENS ? DOES MCCB OPERATION OR WORKING FUNCTION NORMAL IF YES THAN WHY THERE ARE MARKED LINE & LOAD ON MCCB.
how we can calculate chiller required ampear?
sir i had plane to do some project with the base of hopkinson test in AC supply its possible
What is the limitation of kirchoffs law?
What are the special cables required for explosion proof wiring?