I am getting differential earth fault in my transformer
realy , i have checked all its CT & control wiring but do
not get fault, Please help
Answers were Sorted based on User's Feedback
Answer / jiten sharma
Hi, some times when you charge the transformer after some
duration, trafo will take high inrush current. Due to that
it will trip on overcurrent but some times it can be also
give the triping on differential protection with
overcurrent.
So keep the setting slight high and then charge the
transformer. N after charging keep the setting as it is.
It might solve your problem but before that do the all test
on your trafo and then if nothing will found follow this.
Regards,
Jiten
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / arun
Do all the tests in the transformer windings then you will
get the fault.
Differential protection is given mainly to isolate the
circuit when there is fault inside the transformer.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / engineer
Check all your system(Incuding Cables and trandformer and
control circuit) From 1st CT (at HV Side)to 2nd CT at(LV
side).
| Is This Answer Correct ? | 1 Yes | 0 No |
I think it is REFR which picks up only if there is earth
fault whithin the transformer .i.e. between LT an HT
CTs.and an NCT is to be provided
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / k.prakashchandra
Dif relay acts even for faults anywhere between cts .check
cable glands and all others between cts on primary and
secondary
| Is This Answer Correct ? | 1 Yes | 0 No |
AC 230V BULB GIVING DC SUPPLY WHAT HAPPENS?
Can we operate a DG Set in paralell with Transformer ?
6 Answers NDDB, Sobha Developers,
how can maintaince the acb contactor moveing and fixing kit
can you plz send l&t aptitude questions if available its urgent plz plz plz
what is the working principle of a DG Set, Alternator, & exiter
What is principal to reduce earth leakage current with isolation transformer? When isolation transformer is installed in input stage of system, earth leakage current is reduced. the reason is why the leakage current of 2nd stage of isolation transformer does not affect the 1st stage's leakage current. I would like to know the reason. As you know, earth leakage current is a kind of AC. So, How to reduce earth leakage current in case that isolation transformer is used?
what is the difference between ground and neutral?
what is the most permissible winding temp when we conducting a generator load test?(condition no load)
in GEAFOL Cast-Resin trnaformer of 11/.72kv which has tapping of 11550v,11250,11000,10246v in primary side. To obtain 700v. which tapping should be used of HV side as we have 11000v/720v tapping now .
what is working parincipal of a ht transformer
What is PF? Formula for calculating PF in HT side?
What is the angle of inclination for the oil connection from transformer conservator to Bucholz relay and why?
0 Answers Alam Group of Companies,
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)