Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


I am getting differential earth fault in my transformer
realy , i have checked all its CT & control wiring but do
not get fault, Please help

Answers were Sorted based on User's Feedback



I am getting differential earth fault in my transformer realy , i have checked all its CT & co..

Answer / jiten sharma

Hi, some times when you charge the transformer after some
duration, trafo will take high inrush current. Due to that
it will trip on overcurrent but some times it can be also
give the triping on differential protection with
overcurrent.

So keep the setting slight high and then charge the
transformer. N after charging keep the setting as it is.

It might solve your problem but before that do the all test
on your trafo and then if nothing will found follow this.

Regards,
Jiten

Is This Answer Correct ?    3 Yes 0 No

I am getting differential earth fault in my transformer realy , i have checked all its CT & co..

Answer / arun

Do all the tests in the transformer windings then you will
get the fault.

Differential protection is given mainly to isolate the
circuit when there is fault inside the transformer.

Is This Answer Correct ?    2 Yes 1 No

I am getting differential earth fault in my transformer realy , i have checked all its CT & co..

Answer / vaidegi

yes

Is This Answer Correct ?    1 Yes 0 No

I am getting differential earth fault in my transformer realy , i have checked all its CT & co..

Answer / engineer

Check all your system(Incuding Cables and trandformer and
control circuit) From 1st CT (at HV Side)to 2nd CT at(LV
side).

Is This Answer Correct ?    1 Yes 0 No

I am getting differential earth fault in my transformer realy , i have checked all its CT & co..

Answer / k.prakashchandra

I think it is REFR which picks up only if there is earth
fault whithin the transformer .i.e. between LT an HT
CTs.and an NCT is to be provided

Is This Answer Correct ?    1 Yes 0 No

I am getting differential earth fault in my transformer realy , i have checked all its CT & co..

Answer / k.prakashchandra

Dif relay acts even for faults anywhere between cts .check
cable glands and all others between cts on primary and
secondary

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

AC 230V BULB GIVING DC SUPPLY WHAT HAPPENS?

2 Answers  


Can we operate a DG Set in paralell with Transformer ?

6 Answers   NDDB, Sobha Developers,


how can maintaince the acb contactor moveing and fixing kit

0 Answers   Gulf Cement,


can you plz send l&t aptitude questions if available its urgent plz plz plz

0 Answers   HPCL,


what is the working principle of a DG Set, Alternator, & exiter

0 Answers  


What is principal to reduce earth leakage current with isolation transformer? When isolation transformer is installed in input stage of system, earth leakage current is reduced. the reason is why the leakage current of 2nd stage of isolation transformer does not affect the 1st stage's leakage current. I would like to know the reason. As you know, earth leakage current is a kind of AC. So, How to reduce earth leakage current in case that isolation transformer is used?

2 Answers  


what is the difference between ground and neutral?

2 Answers  


what is the most permissible winding temp when we conducting a generator load test?(condition no load)

0 Answers  


in GEAFOL Cast-Resin trnaformer of 11/.72kv which has tapping of 11550v,11250,11000,10246v in primary side. To obtain 700v. which tapping should be used of HV side as we have 11000v/720v tapping now .

1 Answers  


what is working parincipal of a ht transformer

0 Answers   Pidilite,


What is PF? Formula for calculating PF in HT side?

10 Answers   HSL,


What is the angle of inclination for the oil connection from transformer conservator to Bucholz relay and why?

0 Answers   Alam Group of Companies,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)