I am getting differential earth fault in my transformer
realy , i have checked all its CT & control wiring but do
not get fault, Please help
Answers were Sorted based on User's Feedback
Answer / jiten sharma
Hi, some times when you charge the transformer after some
duration, trafo will take high inrush current. Due to that
it will trip on overcurrent but some times it can be also
give the triping on differential protection with
overcurrent.
So keep the setting slight high and then charge the
transformer. N after charging keep the setting as it is.
It might solve your problem but before that do the all test
on your trafo and then if nothing will found follow this.
Regards,
Jiten
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / arun
Do all the tests in the transformer windings then you will
get the fault.
Differential protection is given mainly to isolate the
circuit when there is fault inside the transformer.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / engineer
Check all your system(Incuding Cables and trandformer and
control circuit) From 1st CT (at HV Side)to 2nd CT at(LV
side).
Is This Answer Correct ? | 1 Yes | 0 No |
I think it is REFR which picks up only if there is earth
fault whithin the transformer .i.e. between LT an HT
CTs.and an NCT is to be provided
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / k.prakashchandra
Dif relay acts even for faults anywhere between cts .check
cable glands and all others between cts on primary and
secondary
Is This Answer Correct ? | 1 Yes | 0 No |
Hello friends i am facing one problem in lighting panel. Frequently neutral link near to MCCB is burning(firing. What may be the reason for this one. Please answer me.
why we are using large cross section cable at load side and small at other (11kv to trsfr)side of transformer? when the load increses current at both side increases,right?
Triping principle of ELCB&RCCB? wht is the difference between these two?
How to check 11000/1.732 to 110/1.732 Potentila transformer (PT)?
Explain what are inter-poles and why they are required in a dc machine.
1)we have 1000 cfm Blower,Dia-1Mtr,Velocity of air 94 m/s 2)We have Natural Air velocity 94m/s 3If i Put Wind Mill in natural air ,speed is 94m/s Then it will generate Assume 100kw 4)If i put same wind mill across the Blower,air speed is same 94m/s now the Question is Will it generate 100 kw?
if we appling capacitor at above rated what are looses and what will be happen
4 Answers Radiant, Real Estate,
what is the need of representing AC power in sinusoidal waveform? why not in square or rectangular etc...
what is Insulation monitoring device. where it is used? (in switchgear room or control panel or in field equipment)
What is the impedence of Transformer?
1) What are your personal strength? 2) What are your personal areas of improvement? 3) What are your expectations from from a particular job? 4) what are your carrier objectives?
during the period of armature reaction ,if the brush shift is not accomplish, what happen?