Answer / amit kumar
Becoz we cant store the ac supply and at the time of fault
we need fast tripping of the coil, which can be done by dc
only.
| Is This Answer Correct ? | 38 Yes | 5 No |
Control circuits are sensing the healthy status of the
system, and there are many areas, where the system is to be
monitored even if there is no power supply at all.(eg: in
sub stations. during lightning stroke its very necessary
that, the system to be isolated.)
In this case, DC is the only choice that, we can provide
with battery supply. So most critical control systems
designs with DC only( pref. 24 to 48 volts DC)
| Is This Answer Correct ? | 21 Yes | 6 No |
Answer / girish kumar samal, hindalco,h
main thing is tripping ckt is alwayws dc as if ac fail & it
is urgent to trip an equipment we cannt do.
| Is This Answer Correct ? | 17 Yes | 10 No |
Answer / shafi kukkad
for controling we need continue supply in any condition
so,in Electrical Storage only by Using Battery which input
and output is DC. so whn our normal system fail this DC
comes from direct from Battery bank (which chareged by DC
UPS.) no any other arragment required.
if we using AC Controling we used AC UPS syestem, which
done first AC to DC and charged Battery. and whn Fail
normal control supply (which is AC), thn first Battery
output DC convert into AC and give control supply.which is
not reliable and complex arragement.
| Is This Answer Correct ? | 8 Yes | 6 No |
Answer / zulfiquar wani
DC supply we are using for the control circuit becoz it is
a continous supply for control circuitary for signaling and
even for tripping even if the AC fails.... becoz DC is
always available and also we are using DC backup for
emergency tripping of lighting system
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / vishal
In control ckt ,tripping ckt plays very imp role. Let us consider circuit breaker when fault occurs our relay gives trip command which lasts for fraction of second since AC has zero crossing probably DC is used & which is reliable...!
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / pankaj
DC supply used for control ckt because the system which we are protected by fault(i.e. o.c.,earth fault etc.)is working on A.C. at 50Hz frequency,if their is any fault & if our control system is also same on A.C. then we cant protect the H.T.line.
Hence D.C.supply which are not dependent on A.C.
(i.e.Storage Battery)is used for control ckt.
| Is This Answer Correct ? | 3 Yes | 4 No |
Answer / arjun kumar shukla
DC supply can be store on battery but AC supply can't store in simply DC used. Main supply, control supply would not be same.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / sethar12
Can we supply AC from UPS to control circuits?
| Is This Answer Correct ? | 4 Yes | 6 No |
Answer / prakash suhane
Control ckts are design on DC because
1) unlike to AC, DC is constant wrt time hence no
fluctuation provide better stability in control ckt device.
2) As there is no frequency hence no leagkage current again
safety of control device.
3) DC as compare to AC is quickest means of isolation.
| Is This Answer Correct ? | 3 Yes | 7 No |
In our domestic single phase line if you don't have a ground connection (earthing)how will you separately use earth in a specific power supply board.
what is the multi strand cable size? 0.45mm is area of one strand & 370nos of strand.
Why lose 1 phase voltage in 33kv to 415v stepdown transformer
In transformer how measure the winding temperature ?
The height to which the liquid in a tank to be maintained for a certain constant velocity?
how steam converted into electricity in power plant
How is the connection of the tap changer on the HV side been made?
working principle of induction motor is similar to transformer. but what makes it to rotate? then why the transformer doesnt?
How to improve fuel cell in a distribution system?
give types of Air conditioners commonly used &its use?
what is the difference between linear choke and suction choke?
What will happen if primary of transformer is fed with Square wave instead of sinsoidal wave ?Will it operate or Not?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)