Explain types soft starters?
Answers were Sorted based on User's Feedback
Answer / kumarabharathi
Soft starters nothing but thyristor control starters,this
different form VFD drives,All VFD drives are soft starters
but All soft starters are not Drives,In VFD we can adjust
the speed,Torque & master-slave operation,But in soft
starters is used only to reduse starting current of motor
And for soft starting of motors.
| Is This Answer Correct ? | 16 Yes | 7 No |
Answer / karthik
so many soft starters is available in market.fews are abb
siemens,power boss etc.soft startesused to minimise the
starting time of a motor and limit the current also.in
starting time aalso we limit the input voltage of the motor.
Ramp Up
Ramp Down
Pedestal
Step Down
Supply Frequency
Current Limit Time
Current Limit Level
Kick Start Time
Kick Start Level
Arc-less Switching above all parameters also we adjustable n
soft starters.
| Is This Answer Correct ? | 12 Yes | 7 No |
Answer / hari
1)air cored reactor soft starters(hormonic effect free)
2)Iron core reactor soft starters(hormonic effect will be
there)
2)flux compensating magnetic amplifier starters(FCMA)
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / sunil guru
there are various soft starters for both AC and DC machines...
for DC motor>>>>>
1.three point starter
2.four point starter
for AC motor>>>>>
1.star -delta starter.
2.auto transformer starter
3.rotor resistance starter
4.direct on line starter
soft starters are used>>>>>>
to reduce the starting current
to reduce the starting voltage
simultaneously to increase the torque of motor as it gains speed
soft starters are not only used to give a soft start to the motor but also 2 give protections like >>>>>>>>
1.in the absence of the starter the starting current will be too high so it would effect the parallel loads connected and may blow out the fuse
2.if the motor fails to start due to cogging then the circulating current may burn the armature winding of motor
3.as at start the starting current is 10-15 times high so starting torque also 10-15 times high so that torque may damage the motor getting if higher speed than rated.
so the soft starter's are used to start the motor in a safe way
| Is This Answer Correct ? | 6 Yes | 3 No |
Answer / rex
one type of starter for three phase squirrel cage motors is
a star delta starter switching the stator windings to star
connection to start ,707 of supply volts across each phase
winding when full speed is reached the stator windings are
then connected in delta connection full supply voltage
across each phase winding.
the inrush current during initial starting is limited with
the reduced voltage thus less current
| Is This Answer Correct ? | 0 Yes | 4 No |
why all selected supply voltage are multiple of 11
a 25kvar capacitor bank connected to the secondary side of transformer.then why the capacitor draws more current then rated
Which standard we are following earthing resistance test
What happens on the secondary of a 33kV/11kV when one phase of the primary fuse blows?
what is negative phase sequence
What are the typical values of characteristic impedences of overhead line and underground cabel? Why there is so much variation?
what is breathing?
In what circumstanced the CT used for protection relay will be saturated?and what will happen to the relay is the CT is saturated?
What type of wiring series or parallel is used for conventional and addressable type FAS & why?
i want to know is it possible to generate usefull power by coupling generator with motor & supply gives to motor by battery source then generator generates power. remove the battery source given to the motor & feed the supply from some of the generated power supply to the motor & motor runs continously. generator generate power contnously.is it possible ?
what will happen if a 3 phase motor is connected to a single phase circuit and vice versa?
I am new guy as an electrical engr. in a 100MW HFO based power project. I am in operations division. I have noticed from last few days, my supervisor sends the last 24 hours energy generation calculation to my plant manager. I have noticed, he calculated last 24 hour's generated energy differences in KWH then he multiplied it with a multiplying factor 960. for example: total difference =2.685 KWH*960= 2577.6 MWH. but he does not not know what is multiplying factor 960?? can anybody explain it??
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)