What are the typical values of characteristic impedences of
overhead line and underground cabel?
Why there is so much variation?
Answer / iamdon
Characteristic impedence of overhead line=400 ohm
Characteristic impedence of underground cable=40 ohm
Characteristic impedence= Square root of (L/C).
In case of overhead lines L dominates so higher
Characteristic impedence.
In case of underground cables C dominates(conductors are
very close to each other) so lower Characteristic impedence.
Author:arbelectbit@yahoo.com
Is This Answer Correct ? | 3 Yes | 0 No |
when u are given a timer,push buttons and contactor, how do i practically make a star delta control circuit and a direct online control circuit?
A TRANSFORMER 440/400V,DELTA/STAR CONNECTED.THE NEUTRAL CONNECTED WITH GROUND CABLE THAT IS DIRECTLY CONNECTED TO THE PANEL,FROM PANEL IT IS CONNECTED EARTH PIT.IS IT RIGHT? IF IT IS RIGHT LEAKAGE CURRENT AFFECTED.SECONDATY IS PROTECTED WITH EARTH LEAKAGE RELAY.
Is there any specialised book to refer about fault level calculation both in MV and LV side??
why magnetising curve not start with zero voltage?
What is meant by Guard relay ?
Im designing APFCR Panel for 600 KVAR.I need to calculate the full current so that i can choose the capacity of isolator/Breaker.Kindly suggest with formula.
What are the probable causes for failure of heating elements
we want to feed 3 phase supply to 70 ton AC load.what will be the size of (3 phase)cable require.
How is a capacitor bank is designed ?
I have a current transformer with 1 main reading meter with transformer outside the building and a control panel having 5 CT reading meters with black round coils inside the building. I want to know, A) when current pass through the Transformers, will the current be reduced or be the same and after that B) when current pass through the CT meters with black round coils, will the current be reduced or be the same. C) in the above process will the reading of the main meter be same or different, from the total reading of all the 5 CT meters.
for compensate 315mh inductance ,how many capaciance required?
why open-delta core of 11kv Potential Transformer is 11000v/1.732/110/3?