I am new guy as an electrical engr. in a 100MW HFO based
power project. I am in operations division. I have noticed
from last few days, my supervisor sends the last 24 hours
energy generation calculation to my plant manager. I have
noticed, he calculated last 24 hour's generated energy
differences in KWH then he multiplied it with a multiplying
factor 960. for example:
total difference =2.685 KWH*960= 2577.6 MWH.
but he does not not know what is multiplying factor 960??
can anybody explain it??
First of all you will find CT & PT ratio using for this
power measurement then you can find MF what your supervisor
apply.
Suppose that---
you are using a 33 kV CT having ratio 50/1 Amp. and 33 kV
PT. so multiplying factor= 50/1 * 33000/110 = 15000 (in watt)
Is This Answer Correct ? | 2 Yes | 0 No |
Could you measure voltage in series?
what is the illumination level required for child play area?
How to select the cable size for the given load ?Pls explain the Formulae
Can I parallel 1 MVA generator with 1kVA Generator? if V, F, Ph Seq and Ph angles are same
How current is reduced in STAR connection?
say a transformer is designed for 33/11kv step down with ratio 0.33 for load 1 mva. if am giving 11kv as a input that same transformer what will happen to its o/p voltage. and whether it can be operated for 500kva
Why wind turbines wheels rotate constantly
a room heater is connected in serise with a 100w bulb.if the 100w bulb is replaced by a 40w bulb then the output of the heater is increase/decrease/remain same?
9 Answers College School Exams Tests,
how to calculate the settings for shaft ct protn in hydro generators
what is resistance
what is meant by slip & where its occur ?
What is the difference between Generator Differential Relay and Transformer Differential Relay?