can we load Power capicitors on DG sets?

Answers were Sorted based on User's Feedback



can we load Power capicitors on DG sets?..

Answer / martin

No we need not connect the Capacitor to the DG as the DG
will have the AVR by which the constant voltage is
maintained even in case the load increase or decrease. When
the capacitors are connected they act as a load on the
sytem there by increasing the system load rather than
helping us.

Is This Answer Correct ?    26 Yes 4 No

can we load Power capicitors on DG sets?..

Answer / jigar shah

Capacitor requirement arises to effective utilization of
the generated power (to reduce the losses mainly-cu losses
& line losses) & all switchgear component.In general
practice Capacitors are not connected on DG Set.As per my
understanding following are the main reasons for which it
is not recommendation to run capacitors on DG set :

1. During no load condition capacitor will try to increase
the voltage level of genrated voltage which can damage the
insulation of wdg & wdg may get burnt

2. With increase in PF we will not ge much advantage as the
cable losses are negligle.Load is in nearest proximity of
the Equipment.

3. Capacitors can be installed at load side

Is This Answer Correct ?    22 Yes 0 No

can we load Power capicitors on DG sets?..

Answer / ram singh

no

Is This Answer Correct ?    16 Yes 3 No

can we load Power capicitors on DG sets?..

Answer / sudhir purandare

Yes, self working on DG for last 20 years and never had any
problem because of capacitors. Capacitors will help to
improve the power factor of the system and indirectly
reduce the load on alternator (which is mainly for
delivering the reactive power). only care shall be taken by
not allowing the power factor to go in leading. It is a
normal practise to switch on the capacitors after motor
starts and switch off immediately after motor trips.
Instead of maintaining the PF close to unity, it is better
to maintain it 0.9.

Is This Answer Correct ?    11 Yes 1 No

can we load Power capicitors on DG sets?..

Answer / suneetha

A DG is used to supply power when there is power failure
and not for power factor correction but a Power Capacitor
is mainly used for power factor correction and is usually
kept near unity to avoid penality.

Is This Answer Correct ?    15 Yes 6 No

can we load Power capicitors on DG sets?..

Answer / reshi

Not at all ,Since DG sets are already generating the rated
voltage required and the designed power factor. For the
sake of discussion if we agree to install the capacitor on
DG sets it will give rise to the overvoltage and the
nearest downstream equipments are most probably not safe by
this option of having the capacitor on the DG sets.
Capacitors are required when the power factor is required
to improve and the best practice is it shall be installed
as close possible to the load.

Is This Answer Correct ?    5 Yes 1 No

can we load Power capicitors on DG sets?..

Answer / amarnath

YES ! The DG Rating is always defined in KVA @ 0.8 Pf Lag.
Hence for optimum utilization of the DG power, it will be
best to have the PF regulated to 0.8 PF Lag. However, care
must be taken not to let the PF go into LEAD condition as it
can lead to instabilty of the system voltage. Suggest to
conduct a detailed load study and opt for Automatic PF
Improvement Relay panels wherein the DG target PF can be set
@ 0.8 and for EB the target setting can be 0.95 Lag or above
. (definitely not LEAD)

Is This Answer Correct ?    3 Yes 0 No

can we load Power capicitors on DG sets?..

Answer / sachin_pawaskar2001

Yes, but then Supply voltage will be higher than the
generated voltage due to ferrenti effect.

Is This Answer Correct ?    6 Yes 4 No

can we load Power capicitors on DG sets?..

Answer / t n srivastava kanpur

NOT FEASIBLE WITH DG SO ONLY OPTION TO RUN FACTORY AS IT
IS OTHERWISE SHUT DOWN PLANT.

IF ANY DOUBT PLS CONTACT TO ME.

THANKS

Is This Answer Correct ?    0 Yes 0 No

can we load Power capicitors on DG sets?..

Answer / amit

DG set dis-seined for 0.8 Pf and its capacity also dis-seined according to 0.8 pf so when we increase the pf loading capacity increase but the winding are dis-seined for 0.8 pf.so the winding damsge when the pf is rise.

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

could an induction motor be used for regenerative braking in electric-train control? in this type of application would some scheme have to be devised to obtain low synchronous speeds while braking? would induction-motor drive, therefore, be suitable for passenger service?

0 Answers  


A cylindrical wire is compressed in length by 10%. The percentage decrease in the resistance will be?????

8 Answers  


How can we decide cable size from HT panel to Transformer? Please give you reply with some examples.

0 Answers  


In a Capacitor the electric charge is stored in:

2 Answers   TELK Transformers And Electricals Kerala Limited,


how to calculate the cable current ratingand and how much of distance the rating will be ok will the distance is incresed what the action we take

0 Answers  






NOW A DAYS THE POWER SUPPLY IS VERY LOW.SO THE FLURESCENT TUBE LIGHTS ARE VERY DIM.IS THERE IS ANY WAY TO INCREASE ITS BRIGHTNESS?FOR EXAMPLE ANY CONVERTER,CONDENSER?

1 Answers   Bhel,


What is the required bending radius requied at the time of cable laying?

1 Answers  


What, in the construction of a transformer, controls KVA? For example 600/208/120 V transformer can be 10kVA or 45kVA!!! What do we change in the construction of a Transformer in order to change the rating but not the voltage.

1 Answers  


how do we connect mcb in our home?and how does it work?

3 Answers   IOCL,


why we ground the scondary of current transformer.

4 Answers  


how load of a turbo generator can be increased

0 Answers  


why slipring motor , at full speed run as squirrel cage motor?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)