Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


can we load Power capicitors on DG sets?

Answers were Sorted based on User's Feedback



can we load Power capicitors on DG sets?..

Answer / martin

No we need not connect the Capacitor to the DG as the DG
will have the AVR by which the constant voltage is
maintained even in case the load increase or decrease. When
the capacitors are connected they act as a load on the
sytem there by increasing the system load rather than
helping us.

Is This Answer Correct ?    26 Yes 4 No

can we load Power capicitors on DG sets?..

Answer / jigar shah

Capacitor requirement arises to effective utilization of
the generated power (to reduce the losses mainly-cu losses
& line losses) & all switchgear component.In general
practice Capacitors are not connected on DG Set.As per my
understanding following are the main reasons for which it
is not recommendation to run capacitors on DG set :

1. During no load condition capacitor will try to increase
the voltage level of genrated voltage which can damage the
insulation of wdg & wdg may get burnt

2. With increase in PF we will not ge much advantage as the
cable losses are negligle.Load is in nearest proximity of
the Equipment.

3. Capacitors can be installed at load side

Is This Answer Correct ?    22 Yes 0 No

can we load Power capicitors on DG sets?..

Answer / ram singh

no

Is This Answer Correct ?    16 Yes 3 No

can we load Power capicitors on DG sets?..

Answer / sudhir purandare

Yes, self working on DG for last 20 years and never had any
problem because of capacitors. Capacitors will help to
improve the power factor of the system and indirectly
reduce the load on alternator (which is mainly for
delivering the reactive power). only care shall be taken by
not allowing the power factor to go in leading. It is a
normal practise to switch on the capacitors after motor
starts and switch off immediately after motor trips.
Instead of maintaining the PF close to unity, it is better
to maintain it 0.9.

Is This Answer Correct ?    11 Yes 1 No

can we load Power capicitors on DG sets?..

Answer / suneetha

A DG is used to supply power when there is power failure
and not for power factor correction but a Power Capacitor
is mainly used for power factor correction and is usually
kept near unity to avoid penality.

Is This Answer Correct ?    15 Yes 6 No

can we load Power capicitors on DG sets?..

Answer / reshi

Not at all ,Since DG sets are already generating the rated
voltage required and the designed power factor. For the
sake of discussion if we agree to install the capacitor on
DG sets it will give rise to the overvoltage and the
nearest downstream equipments are most probably not safe by
this option of having the capacitor on the DG sets.
Capacitors are required when the power factor is required
to improve and the best practice is it shall be installed
as close possible to the load.

Is This Answer Correct ?    5 Yes 1 No

can we load Power capicitors on DG sets?..

Answer / amarnath

YES ! The DG Rating is always defined in KVA @ 0.8 Pf Lag.
Hence for optimum utilization of the DG power, it will be
best to have the PF regulated to 0.8 PF Lag. However, care
must be taken not to let the PF go into LEAD condition as it
can lead to instabilty of the system voltage. Suggest to
conduct a detailed load study and opt for Automatic PF
Improvement Relay panels wherein the DG target PF can be set
@ 0.8 and for EB the target setting can be 0.95 Lag or above
. (definitely not LEAD)

Is This Answer Correct ?    3 Yes 0 No

can we load Power capicitors on DG sets?..

Answer / sachin_pawaskar2001

Yes, but then Supply voltage will be higher than the
generated voltage due to ferrenti effect.

Is This Answer Correct ?    6 Yes 4 No

can we load Power capicitors on DG sets?..

Answer / t n srivastava kanpur

NOT FEASIBLE WITH DG SO ONLY OPTION TO RUN FACTORY AS IT
IS OTHERWISE SHUT DOWN PLANT.

IF ANY DOUBT PLS CONTACT TO ME.

THANKS

Is This Answer Correct ?    0 Yes 0 No

can we load Power capicitors on DG sets?..

Answer / amit

DG set dis-seined for 0.8 Pf and its capacity also dis-seined according to 0.8 pf so when we increase the pf loading capacity increase but the winding are dis-seined for 0.8 pf.so the winding damsge when the pf is rise.

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

On what basis primary and secondary of a transformer is chosen?

2 Answers  


sugest any typical project ?

0 Answers  


What is use of starter and choke in tube light

0 Answers  


How to take vector group test of a transformer? Suppose we dont know the vector group of transformer, how to check its vector group through test? I have 3 transformer DYn11 & DYno& Ynd11, how to confirm its vector group?

1 Answers  


for 11KV OH system what will be typical per KM "R" "L" "C" parameter. for 33KV OH system what will be typical per KM "R" "L" "C" parameter. for 33KV UG system what will be typical per KM "R" "L" "C" parameter.

0 Answers   wbsedcl,


if one potential missing in energy meter , how much % slow the energy meter?

1 Answers   NTPC, SK,


why we use shunt in a rectifier system ?

1 Answers  


How Size of Busbar is determined for a particular load.

2 Answers  


HOW MUCH CURRENT CAN A 3 -1/2 CORE 100 MM WIRE CARRY

2 Answers   Focus Energy, San,


I try to check the three phase voltage in multimeter, in 125A isolator switch incommer. first i touch R phase, and then i touch Y phase using multimeter, the moment i touched, it blasts and that moment i got blindness. multimeter selector position is correct(750V AC MODE AND RED PROBE WASS IN v AND BLACK PROBE WASS IN COM. MODE. COULD ANYBODY GIVE ANSWER FOR THIS TO AVOID FURTHER ACCIDENTS PLEASE?

2 Answers  


what is the preventing maintenance of transformer

1 Answers  


if earthing is not connected to computers any problem ?

2 Answers   HP,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)