Answer / reddy
gnerally DG requires servicing like B-Check, C-check and D-
check.after 300 running hrs/ one month b check will be
done, in this they will clean all the filters and change
the oil just like bike servicing. in c-check(after
1500hrs), they change gaskit of chambers. in D-check(after
6000hrs, they will check b+C checks, and they will check
cylinders and injection ckts
| Is This Answer Correct ? | 73 Yes | 15 No |
Answer / rajeev
after 6000hrs, check total genset(A+B+C=D Check).
| Is This Answer Correct ? | 17 Yes | 1 No |
Answer / raj saini
A Check : Coolant check, battery volt, all connection ,
lube oil level, cleaning, air filter on daily.
B Check : A+ all filter except air filter (lube oil
filter , fuel filter , by pass filter, coolant filter) &
lube oil change after 300 Hrs or 6 month
C Check : A+B+Taped setting, Air filter change after 1500
Hrs or One Year.
D Check : All engine over holing after 2000 Hrs or Two Year
if we do not done the A+B+C check as per the above
mentioned time frame .If it has been done routinely then D
check don't required.
| Is This Answer Correct ? | 17 Yes | 3 No |
Answer / s.rajeshkumar
gnerally DG requires servicing like B-Check, C-check and D-
check.after 300 running hrs/ one month b check will be
done, in this they will clean all the filters and change
the oil just like bike servicing. in c-check(after
1500hrs), they change gaskit of chambers. in D-check(after
6000hrs, they will check b+C checks, and they will check
cylinders and injection ckts
| Is This Answer Correct ? | 14 Yes | 5 No |
Answer / sanath shetty
D-check (Every 3000- 5000 Hrs.)
1. Complete DG set should be dismental.
2. Turbo charger service
3. Injector Pin service
4. Cylinder Head service
5. PT Pump sevice &
6. Repeat the B-Check process.
If your DG set running hours more than 10,000 then in D-
Check You should
1. Change Piston Bearing,
2. Change nozels,
3. Piston Cylinder also need to be change.
4. Change Canopy filter if require
5. Check polution level
| Is This Answer Correct ? | 9 Yes | 0 No |
Answer / shubham mathur
"A" - Daily Checks
"B" - 300 Hrs or 6 Months
"C" - 600 Hrs or 12 Months
"D" - 1200 Hrs or 24 Months
and Sanath Shetty is correct
D-check (Every 3000- 5000 Hrs.)
1. Complete DG set should be dismental.
2. Turbo charger service
3. Injector Pin service
4. Cylinder Head service
5. PT Pump sevice &
6. Repeat the B-Check process.
If your DG set running hours more than 10,000 then in D-
Check You should
1. Change Piston Bearing,
2. Change nozels,
3. Piston Cylinder also need to be change.
4. Change Canopy filter if require
5. Check polution level
| Is This Answer Correct ? | 9 Yes | 0 No |
Answer / vikas
D check after 6000hrs
check all gasket ,cylinder parts etc
| Is This Answer Correct ? | 16 Yes | 8 No |
Answer / cheppestaara ?
A,B,C and D checks details will be available in check lists
or else i will give you after i have learnt about that .
| Is This Answer Correct ? | 1 Yes | 0 No |
what is the difference between thermal magnetic release and microprocessor based release breakers. what are the advantages of latter over the first one...
5 Answers Jackson, Karthik Industries, McD BERL, TCS,
Why did lightening arrestor solid copper rod head is sharp on mobile tower top?
what is the diffrence between kav and kvar?
In alternator generally we give DC voltage to field of alternator but field (excitor)produce Ac & converts into DC by rotating rectifier(RR ) then fed to rotor .my question is why we cannot give dc voltage directly to rotor instead of Excitor & RR ?
What will happen if the generator turns in a wrong direction?
how many types of ACB breakers, describe briefly..?
how calculate gd2 of ht motors
0 Answers Hindustan Copper Limited,
what will happen if the secondary of current transformer kept open....
cable selection formulas for electrical load.
In legging current reactive power is arise but in leading current which power will be arise ? and in this case, is active power more than rated ?
How the current flows in dc circuit?
What is the difference between shortcircuit current, rated current of cable & MCB with example? What will be the size of cable required for 5.5 KW motor (Full load current 10 Amps approx.), Starting current with DOL is 120 Amps. Aprrox. Short circuit current with LLLG fault is 2000 Amps Approx.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)