why transformer rating in kva ?
Answers were Sorted based on User's Feedback
Answer / panda n.n
Transformer has two type of loss.1-Iron Loss ,2-Copper Loss.
Iron loss depend upon Voltage where as copper loss depend
upon Current. ther is no significant role of power factor
on these losses.So transformer are rated on KVA or MVA.
| Is This Answer Correct ? | 65 Yes | 5 No |
Answer / srinu
in tf core lossdepends on voltage rating and cu loss
depepends on current ,as the rating of any machine depends
on it's heating that is losses. so in tf heating is
proportional to product of v and i.so tf rating is in terms
of kva rather than kw.
and one more reason is as the load on tf is not constant,we
dont know the exact power factor value.that is also one of
the reason to express tf rating in kva.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / pritesh
simple, the load which is joint with the transformer is not
known so that we dont know the actual power factor because
of reasion the rating of the transformer is in the kva not
in kw.
| Is This Answer Correct ? | 12 Yes | 10 No |
Answer / rcv
It is because of load power factor,Transformer is always
designed on unity power factor. It has only 2 type of
losses Iron loss due to voltage, I2R loss and Stray loss
due to load and there is no involment of powerfactor. Thats
why transformer is rating in KVA.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / aditya shirbavikar
The power factor of transformer is unknown and is derived according to the load connected. Therefore the rating of transformer is in KVA
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / syed vikhar ahmad
power factor is not constant it varies in different load
thats why manufaturer can not keep the rating in kw.suppose
the transformer rating is 500 kva we can put 500 kw load at
unity power factor but at .8 power factor we can put only
400 kw load as per formula kw= kva* pf
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / saida shaik
KVA is the unit for apparent power
Apparent power consists of Active and Reactive power. Active power is transmits energy from the source to the user. Reactive power is represents a usless oscillation of energy from the source to the user and back again. Reactive power occurs when on account of some inertia in the system there is a phase shift between voltage and current. This means that the current dose not change polarity synchronous with the volage but the heat generated in a winding as well as the eddy current losses generated in a t/f core depend on the current only ,regardless of whether it aligns with the voltage or not. Therefore the heat is always propotional to the square of the current amplitude irrespective ofphase angle so a t/f has to be rated by apparent power.(it means KVA instead of KW)
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / a.alexander
do n't know the connecting load .for inductive load ,
capacitive load and Reactive load. transformer is copper
loss dependable for I and core loss dependable for v .told
Kva.
| Is This Answer Correct ? | 9 Yes | 12 No |
Answer / joseph
since it has no load losses, transformer rating in KVa
| Is This Answer Correct ? | 1 Yes | 7 No |
tell how current tranfomer works
What is meant by harmonic distortion?
what is the difference between starter and control panel..?
how many types of ratings are there of transformer
WHY IS RESTRICTED EARTH FUALT PROTECTION NEEDED?? WHY CANT DEIFFERENTIAL PROTECTION SUFFICE???
what is the prinsiple of dc motor and construction and working ,application of dc motor.
I am in last year of Engineering.I want to apply for ONGC on GATE based score.They require Certificate of Competency as Electrical Supervisor.How can i get this certificate so I can apply for AEE(ELECTRICAL) in 2016
What happen if in three phase 440 v , when you check voltage by testor it glows except one phase and in the same time when you check by multimeter it shows 440 v in any two phase.what will be the reason...
what are the C&D CHECK OF DG set
What is motor type DG starter
what are the difference between protection class CT and Class PS CT
An 8 pole, 50 Hz, 3-phase IM is loaded to a poing where pull out torque will occur. The rotor resistance per phase is 0.3 ohm and motor stalls at 650 rpm. The rotor reactance at stand still is A 2 ohm B 1.25 ohm C 3.15 ohm D 2.25 ohm
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)