why transformer rating in kva ?
Answers were Sorted based on User's Feedback
Answer / panda n.n
Transformer has two type of loss.1-Iron Loss ,2-Copper Loss.
Iron loss depend upon Voltage where as copper loss depend
upon Current. ther is no significant role of power factor
on these losses.So transformer are rated on KVA or MVA.
Is This Answer Correct ? | 65 Yes | 5 No |
Answer / srinu
in tf core lossdepends on voltage rating and cu loss
depepends on current ,as the rating of any machine depends
on it's heating that is losses. so in tf heating is
proportional to product of v and i.so tf rating is in terms
of kva rather than kw.
and one more reason is as the load on tf is not constant,we
dont know the exact power factor value.that is also one of
the reason to express tf rating in kva.
Is This Answer Correct ? | 5 Yes | 1 No |
Answer / pritesh
simple, the load which is joint with the transformer is not
known so that we dont know the actual power factor because
of reasion the rating of the transformer is in the kva not
in kw.
Is This Answer Correct ? | 12 Yes | 10 No |
Answer / rcv
It is because of load power factor,Transformer is always
designed on unity power factor. It has only 2 type of
losses Iron loss due to voltage, I2R loss and Stray loss
due to load and there is no involment of powerfactor. Thats
why transformer is rating in KVA.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / aditya shirbavikar
The power factor of transformer is unknown and is derived according to the load connected. Therefore the rating of transformer is in KVA
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / syed vikhar ahmad
power factor is not constant it varies in different load
thats why manufaturer can not keep the rating in kw.suppose
the transformer rating is 500 kva we can put 500 kw load at
unity power factor but at .8 power factor we can put only
400 kw load as per formula kw= kva* pf
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / saida shaik
KVA is the unit for apparent power
Apparent power consists of Active and Reactive power. Active power is transmits energy from the source to the user. Reactive power is represents a usless oscillation of energy from the source to the user and back again. Reactive power occurs when on account of some inertia in the system there is a phase shift between voltage and current. This means that the current dose not change polarity synchronous with the volage but the heat generated in a winding as well as the eddy current losses generated in a t/f core depend on the current only ,regardless of whether it aligns with the voltage or not. Therefore the heat is always propotional to the square of the current amplitude irrespective ofphase angle so a t/f has to be rated by apparent power.(it means KVA instead of KW)
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / a.alexander
do n't know the connecting load .for inductive load ,
capacitive load and Reactive load. transformer is copper
loss dependable for I and core loss dependable for v .told
Kva.
Is This Answer Correct ? | 9 Yes | 12 No |
Answer / joseph
since it has no load losses, transformer rating in KVa
Is This Answer Correct ? | 1 Yes | 7 No |
How to check phase R,Y,B
What are the functions of temperature scanner in power transformer?
what is per unit impedance?
why do we use bundle conductors instead of using single conductor of larger size for high voltage transmission?
Distribution transformer we provided 2 separate earthing pit for Body and 2 separate earthing pit for neutral,we can not connect separate body earthing pit to other earthing pit but we do metal glanding in secondary side cable termination in both side, transformer and PCC panel (LT Panel), is this safe for transformer and other equipment?
Do these factors (settling time, peak time, steady state error, overshoot, rise time, MPOS (Maximum percent over shoot)) are the part of first order, second order, higher order, linear, non-linear, open-loop, closed-loop, homogeneous & non-homogeneous systems ?
What is the need of earthing transformer for delta side of a transformer. (Think of a line section between a star/delta transformer at a grid substation and delta/star transformer at a village. An earthing transformer is there at the delta side of the star/delta transformer at grid substation). As there are no ground reference there will not be fault current if a one phase is grounded. Further L-L phase will be sensed by the primary side of star/delta transformer as a L-G fault. So why an earthing transformer is required at delta side
what happen if we supply ac to the field of a alternator?
why 6.6,11,22,33,66kv? what basis they have considered?
how to calculate EXCITATION VOLTAGE & CURRENT in ALTERNATOR
What will happen if I apply DC to AC transformer? please send detailed answer at habib_rahman_habib786@yahoo.com