In step down transformer (415/200V),mistakenly secondary
side is connected to 415V for some hours, what would be
result of this condition?
Answers were Sorted based on User's Feedback
Answer / pillay
your transformer had become a step up transformer for some
hours, if you have not connected any load to it than there
is no damage to your load.your transformer itself would not
have undergone any damage and safe to use.Please inform us
what actually happened.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / girish naik
The transformer secondary is designed for 220V..Its having
lesser turns than 415V side..so if we apply 415V it
experiences overfluxing and damages the insulation losses
and also the temparature..
Is This Answer Correct ? | 3 Yes | 4 No |
Answer / pillay
this is a case of a stepdown transformer being used as
step up transformer.
as mr milan has said 816.12 would be at the other side.
generally nothing would have happened to the transformer
other than being warm.the transformers insulation class
would be able to take care of the higher voltage.
If the other side the 816.12 volt have been connected to
the
load (suppose to be 200 volts)than damage would have
happened
to the load, the extent depending on what type of
load.
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / manjeet kumar
if u connect 415 secondary side for some hour your load not
operate and transformer secondary side is damage.
Is This Answer Correct ? | 0 Yes | 2 No |
Answer / sanket patil
First of all primary and secondary of a transformer are
decided after putting it in the service. Hence the windings
of transformer are referred as HV and Lv windings.
Now if the HV winding is connected as a secondary then
the xmer will work satisfactorily
In the another case if 220V wdg is connected to the 415V
supply the answer is same as explained by other friends.
Is This Answer Correct ? | 2 Yes | 6 No |
Answer / maan
Most of electrical equipment are rated at 220v,there
working seriously affected if they recive power at haigher
voltage(415v), also losses in primery side increases and
core loss in secondary side , that may damage winding and
insulation.
Is This Answer Correct ? | 1 Yes | 9 No |
where is the need for short circuit test for 3 see is required and why? can you explain in brief with application
whose the first invented AC voltage or DCvoltage
if 20 hp motor starts directly stars and contenious run . what will be the effect.
11 Answers HP, Ohsung Electronics,
An 11kv system consisting of an underground cable to a sub station about 300 meters away was shut down for about 10 hrs. On energising, it tripped off on earth fault about 10---20 mins later 6 times but since than it is not tripping.its already 3 weeks now. The SPAJ was found to be fine. what could be the cause.No test had been done to determine the cause of the trippings till now because of demand.
In what voltage EHT works(133/132/33/66kv?
what is the unit of current
Why a single-phase induction motor not an inherently self-starting machine?
11 Answers ETC, Hindustan Shipyard,
what kind of technical test that i need to learn because i have an interview tomorrow.. please someone help me..
I am designing new project sub station with 220 kV / 11 kV, 40 MVA capacity. This project have many recifier sets, which can generate 3rd harmonics. Now I have to select vector group of This transformer. To minimise 3rd harmonics, what care should I take in selection of Transformer Vecrtor group? If it is Y-Y with open Delta tertiary then what should be the rating & voltage of Tertiary Winding?
what is Aircraft earthing and what does it do?
what is sevice settings for mccb?How can be it setted?
What is the full form of CNC in electrical mechines.......?