why the transformer ratings in kva
Answers were Sorted based on User's Feedback
Answer / hirak patel
bcoz,in trans... Copper loss present in coil due to current and iron loss present in core due to voltage,so consideration of both(vol & current) ,the rating of transformer given in KVA,
| Is This Answer Correct ? | 17 Yes | 3 No |
bcz in transformer two types of losses
may occure they are copper loss and
iron loss. Copperloss depends on current
and ironloss depends on voltage. So the
rating is in kva or mva.
| Is This Answer Correct ? | 15 Yes | 3 No |
Answer / hayanan
The rating of any machine is given by its heat handling
capacity.Heat in a transformer is due to temperature rise
which is due to the power losses. These losses are constant
losses (core losses) and variable losses (copper
losses).Core losses are constant as they depend
proportionally on the system voltage which is
constant.Copper losses are variable as the load on the t/r
varies and hence the current varies.These two are
represented in VA rating which is apparent power.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / sai
in transformer the losses does not depend on power factor so
it is mentioned in kva
| Is This Answer Correct ? | 9 Yes | 6 No |
Answer / bimal sarkar
Copper loss in transformer due to current and iron loss due
to system voltage. There are no phase angle between voltage
and current so not depends on load power factor. So total
loss of transformer depends on volt-ampere (VA).
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / abhi
The real power(kW) also
depends on power factor on
load side,which varies frm
place to place,while the
apparent power will be cnst
at any place.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / shashank
Capacity of any machine is always specified in terms of its
apparent power handling capacity not just real power because
because both real and reactive components ensure power
transmission.
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / g s panda
The angle between voltage and current in primary side is
nearly equal to the angle between voltage and current in
secondary side. So there is not any need of power factor in
describing rating of transformer
| Is This Answer Correct ? | 0 Yes | 0 No |
What is electrical energy ,power?
Why the generating station rating is in KW though the rating of generators in KVA?
What do you mean by distribution transformers?
what is meant by motor protection relay & its working principle ?k
defination of loads
how to calculate cable size in transformer, distribution side?
WHAT DO U MEAN BY THERMAL OVER LOAD RELAY& WHERE THEY ARE BUSED
what is open star connection or open delta.
In my project i am layout cables under the Maintainance bay /Maintainance yard in the TG Building. Whether in this route i can lay the H.T.Cables??? i am taking all H.T cables from the H.T Transformer to the TG Building..
what type of insulation is used for over head lines?
what is power factor?
It is desired to flood light the front of a building 42 meters wide and 16 meters hig.Projectors of 30 degree beam spread and 1000 watt lamps giving 20 lumen/watt are availabl.If the desired level of illumination is 75 lumen/m and show a suitable scheme.Assume the cofficient of utilization, deprecitation factor and waste light factor are 0.4, 13 and 1.2 respectively.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)