Answer / hirak patel
bcoz,in trans... Copper loss present in coil due to current and iron loss present in core due to voltage,so consideration of both(vol & current) ,the rating of transformer given in KVA,
| Is This Answer Correct ? | 17 Yes | 3 No |
bcz in transformer two types of losses
may occure they are copper loss and
iron loss. Copperloss depends on current
and ironloss depends on voltage. So the
rating is in kva or mva.
| Is This Answer Correct ? | 15 Yes | 3 No |
Answer / hayanan
The rating of any machine is given by its heat handling
capacity.Heat in a transformer is due to temperature rise
which is due to the power losses. These losses are constant
losses (core losses) and variable losses (copper
losses).Core losses are constant as they depend
proportionally on the system voltage which is
constant.Copper losses are variable as the load on the t/r
varies and hence the current varies.These two are
represented in VA rating which is apparent power.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / sai
in transformer the losses does not depend on power factor so
it is mentioned in kva
| Is This Answer Correct ? | 9 Yes | 6 No |
Answer / bimal sarkar
Copper loss in transformer due to current and iron loss due
to system voltage. There are no phase angle between voltage
and current so not depends on load power factor. So total
loss of transformer depends on volt-ampere (VA).
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / abhi
The real power(kW) also
depends on power factor on
load side,which varies frm
place to place,while the
apparent power will be cnst
at any place.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / shashank
Capacity of any machine is always specified in terms of its
apparent power handling capacity not just real power because
because both real and reactive components ensure power
transmission.
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / g s panda
The angle between voltage and current in primary side is
nearly equal to the angle between voltage and current in
secondary side. So there is not any need of power factor in
describing rating of transformer
| Is This Answer Correct ? | 0 Yes | 0 No |
how to calculate induction motor rating (HP) if name plate is missing from motor at site condition ?
6 Answers ABB, apatel, Bhel, Spatel, Voltas,
How to calculate 33 kv panther conductor line losses.
1 Answers Construction, Orange,
HOW WE KNOW IN PHYSICALLY THE CONTACT SURFACE OF A VACUUM INTERRUPTER IS GOOD OR GOING TO DAMAGE IN A VCB AFTER ABOVE 500 TIMES OPERATED.
what is breaking capacity
Why the unit sizes of hydro generating machines are not standardized as in case of thermal powerplants?
In which reason, one end of CT secondry get connected with Earthed? Normaly S1 of CT. Why????
what is the full form of XLPE adn there use.
RESISTONS R1 AND R2 in parallel = Total R.? 1-R=R1+R2 2-R=1/R1 + 1/R2 3-1/R + R1+R2 R=R1R2/R1+R2 select one
2 Answers BSNL, PGVCL Paschim Gujarat Vij Company Limited, TCS, Wartsila,
How many VSC based HVDC are there in India and the world
what is the length of air terminal in lightening arrester system.
What is the dc grounding system and what is diff between AC/DC grounding system?
How do you protect your appliances from harm in case of neutral failure in a three phase power supply set up.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)