In step down transformer (415/200V),mistakenly secondary
side is connected to 415V for some hours, what would be
result of this condition?
Answers were Sorted based on User's Feedback
Answer / ankaraju
The secondary side is rating of 200v,if you considering
loop the net current flowing throw winding increases hence
losses also increases and winding over heated,if it so on
for hours winding insulation may failed.And another one is
core is nearer to low winding,due to high voltage core
losses and core insulation between laminations also failed.
| Is This Answer Correct ? | 34 Yes | 5 No |
Answer / milan
secondary side winding turns is designed for 200 volts. If
we give 415v the secondary side winding turns will not
sustain the voltage . For which insulation and winding both
will damage .If we give 415v to secondary the primary will
get 816.125v
| Is This Answer Correct ? | 19 Yes | 3 No |
The current at 200v side will be more than what designed
for the transformer and core loss will be more. So
ultimately,transformer will be heated up more faster than
ordinary condition. Depends upon the insulation used for
core construction, and how long u are connected the supply,
there r chances of insulation failiure.
| Is This Answer Correct ? | 11 Yes | 1 No |
Answer / manoj
as 2ndary side winding is design for 2oo volt so when we
connect 2ndary side to 415 volt,then after some hour the
2ndary winding burnt.
| Is This Answer Correct ? | 9 Yes | 4 No |
Answer / neeraj
the whole transformer will burn up.
i do it practical one time.
but in future i will not do such thing.
| Is This Answer Correct ? | 4 Yes | 1 No |
if Secondary puts 415v, than primary wants to take the
voltage upto 850v, & it can burn the winding of the
transformer.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / partha
In this case, the transformer will undergo insulation
degradation. Also due to the increased voltage, the core
losses will increase. The core will be also subjected to
overfluxing which will cause saturation and increased core
losses.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / vino raju dee
200v induced in the primary.there is no application for
this induced voltage.
| Is This Answer Correct ? | 0 Yes | 0 No |
technically, what is the reason behind starting the motor star the delta connection .. and what other ways to do this rather than using " star-delta transformer"
How to distinguish between the armature wires with the field wires of a Dc motor ?
in my industry we are using 3 step up transformers for induction heaters..i.e 415/580v and other are 11/440v.in power consumption does a step trnsformer makes any difference compared to step up?? plz explain
Dear all, Can anybody tell me that how to choose CT for a specific load? I have a 200kw induction motor, which ratio CT should be installed? Is there a formula or calculation that determines the CT ratio for a load? Regards.
why alternator is used instead of dc generator and induction generator
Suppose the incoming power is 11 kw, but the load require only 8 kw means how can we save or use the excess power?
If we are given a 10 amp cable type and asked to calculate the number of cores used and the thickness of the cable, how do we do it?? please help...urgent!! i hope the question is clear enough!!
How equivalent impedance is calculated in thevenin theorem?
if we give 60 hz single phase supply to the transformer used in europe , than what will happen
How would u describe the function of a generator & motor?
how choose conductor&depending upon load
What is current & voltage ? Voltage perform at any load without current or not?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)