In step down transformer (415/200V),mistakenly secondary
side is connected to 415V for some hours, what would be
result of this condition?

Answers were Sorted based on User's Feedback



In step down transformer (415/200V),mistakenly secondary side is connected to 415V for some hours,..

Answer / ankaraju

The secondary side is rating of 200v,if you considering
loop the net current flowing throw winding increases hence
losses also increases and winding over heated,if it so on
for hours winding insulation may failed.And another one is
core is nearer to low winding,due to high voltage core
losses and core insulation between laminations also failed.

Is This Answer Correct ?    34 Yes 5 No

In step down transformer (415/200V),mistakenly secondary side is connected to 415V for some hours,..

Answer / milan

secondary side winding turns is designed for 200 volts. If
we give 415v the secondary side winding turns will not
sustain the voltage . For which insulation and winding both
will damage .If we give 415v to secondary the primary will
get 816.125v

Is This Answer Correct ?    19 Yes 3 No

In step down transformer (415/200V),mistakenly secondary side is connected to 415V for some hours,..

Answer / rvg

The current at 200v side will be more than what designed
for the transformer and core loss will be more. So
ultimately,transformer will be heated up more faster than
ordinary condition. Depends upon the insulation used for
core construction, and how long u are connected the supply,
there r chances of insulation failiure.

Is This Answer Correct ?    11 Yes 1 No

In step down transformer (415/200V),mistakenly secondary side is connected to 415V for some hours,..

Answer / manoj

as 2ndary side winding is design for 2oo volt so when we
connect 2ndary side to 415 volt,then after some hour the
2ndary winding burnt.

Is This Answer Correct ?    9 Yes 4 No

In step down transformer (415/200V),mistakenly secondary side is connected to 415V for some hours,..

Answer / deepakeee

winding will burn

Is This Answer Correct ?    8 Yes 3 No

In step down transformer (415/200V),mistakenly secondary side is connected to 415V for some hours,..

Answer / neeraj

the whole transformer will burn up.
i do it practical one time.
but in future i will not do such thing.

Is This Answer Correct ?    4 Yes 1 No

In step down transformer (415/200V),mistakenly secondary side is connected to 415V for some hours,..

Answer / binay agrawal

if Secondary puts 415v, than primary wants to take the
voltage upto 850v, & it can burn the winding of the
transformer.

Is This Answer Correct ?    3 Yes 1 No

In step down transformer (415/200V),mistakenly secondary side is connected to 415V for some hours,..

Answer / partha

In this case, the transformer will undergo insulation
degradation. Also due to the increased voltage, the core
losses will increase. The core will be also subjected to
overfluxing which will cause saturation and increased core
losses.

Is This Answer Correct ?    1 Yes 0 No

In step down transformer (415/200V),mistakenly secondary side is connected to 415V for some hours,..

Answer / amit choudhary

IT'll as a step up transformer.

Is This Answer Correct ?    0 Yes 0 No

In step down transformer (415/200V),mistakenly secondary side is connected to 415V for some hours,..

Answer / vino raju dee

200v induced in the primary.there is no application for
this induced voltage.

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

Metal covered multiconductor cables shall employ a marker tape located within the cable running for its complete length in lieu of cable surface marking. Is it true or false?

0 Answers  


What do you mean by screen of power cables?

0 Answers  


what is called inrush current??

1 Answers   KSEB,


What is a current transformer?

2 Answers   KEPL,


How to calculate VCB current rating for 2000 KVA transformer

1 Answers   Yamuna Power and Infrastructure Ltd,






What is the starting current of a DC Motor?

2 Answers  


principle of power export and import in captive power plant.Is it depends upon voltage,current or frequency?Plz explain briefly.

1 Answers  


In a single phase converter, the no. of SCR conducting during overlap? a.1 b.2 c. 3 d. 4

3 Answers  


i have a roll dia aprox.43 inches and gear box ratio is 14.3.so my question is how was decide the kw rating of motor.

1 Answers  


where this neutral connection goes after returning from the load(home ,factory,industries).Is it grounded at the transformer side or atthe generator side .If it is grounded then we also ground the earth connection.is there any problem with this.

1 Answers   IOCL,


how freewheeling diode improves the powerfactor

0 Answers  


WHAT IS THE WINDING PROCEDURE OF ELECTRICAL MOTOR

0 Answers   GE,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)