We do have a problem in the company that is one PT connected to PlC which is mean 1 out of 1 in PLC system we do have the PAHH is 55 mbar and PALL 8 mbar with a timer of 15 sec for the PAHH the problem started when PAHH goes more than the set point which is 55 it reached up to 71 but due to timer doesn't trip . We force it and we checked everything nothing there . We replaced the transmitter problem still there the reading goes more than the 55 bar the range for transmitte is 0- 60 mbar . So we did loop check , aculaizing valve , wiring all are okay . What the possible causes for this ???
Answers were Sorted based on User's Feedback
Although the post has lots of information, it isn't clear
exactly what the problem is.
I think the problem is that the PLC does not alarm when the
pressure exceeds (goes above) 55mbar. But I'm not sure.
Given this description: when PAHH (pressure alarm High High)
goes more than the set point which is 55 it reached up to 71
but due to timer doesn't trip . We force it and we checked
everything nothing there, let's suppose that the PLC is not
indicating an alarm state.
a) what should the PLC do at the alarm condition?
b) How is an alarm indicated? A digital output (DO) goes
high? A lamp is driven by a DO lights up?
c) What exactly does not work as it should?
If the PLC does not indicate an alarm, yet the indicated
pressure goes higher than a high alarm, the problem is NOT
the field transmitter, the problem is in the alarm setup or
alarm annunciation.
Troubleshooting depends on
- an explanation of exactly what should be happening
- an explanation of how you know it is not working; that is,
what the evidence is that it is not working.
Yes, the pressure went above 55mbar.
How do you know that?
The transmitter's local display?
A milliampmeter in the analog input circuit?
Did the alarm ever work? Or is this a new commissioning and
you're trying to get the alarm to work?
Carl Ellis
Measure First
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / jigar anadkat
Dear,
As you mentioned pressure shot up to 71 mBar which means channel goes to BAD state and it might not activate the logic. (Truly speaking it should but depends on how the logic has been created and what are the parameters set in IO assignment for failure situation).
If you you are using Yokogawa Prosafe RS the please make sure to take Chanel status as well in the logic configuration. So in case of IOP(+) as well as IOP(-) it will actuate the logic.
Moreover, there is a setting in IO parameter builder regarding input processing at fault situation. Please go through that as well.
Hope this will help you in trouble shooting.
Regards,
Jigar Anadkat
Instrument Engieer
IBN RUSHD
A SABIC affeliate.
| Is This Answer Correct ? | 1 Yes | 1 No |
In VVVF DRIVES VOLTAGE IS ALSO VARY WITH THE FREQUENCY. HOW? WHAT IS THE DIRECT FORMULA RELATING THESE TWO.
what is formula for calculating flow if i have pressure and pipe diameter?
plz send me placement paper of ongc
if a dp transmitter has range 100 in H2O and flow is 20mmcf and if the flow is changed to 25 mmcf then what is the formula to determine new range of transmitter
What is the purpose of the analyzer in petrochemical plant?
0 Answers ENI, Lakshmi Machine Works,
What is the working principle of the magnetic meter?
can we copy the software from a transmitter using hht(hart 275) ?
defination of plc? why we use plc? application of plc? advantage of plc?
we have LPG spherical Tank and we want to install DP Xmtr for level measurement.below are the physical measurements Total height of tank is 1850 mtr but 0% level is 1000mm above bottom and 100% level is 450 below upper side.What is the LRV and URV and please mention the formula .The SG of LPG is 0.53 and Wet Leg method will be used.
if we mount flow tube in arrow direction then flow comes in negative & if we mount it another direction then flow comes positive,So what will be the problem
Explain about relays.. Can we give both AC and DC to the same relay... How it is energising.. Explain its working..
Can combine control system for Emergency control system (ESD)and Fire & Gas System ( F & G) is possble to built and offer to client? Can such system is as per Norms in India?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)