Answer / ravi
1.Cold Loop Check
This is an electrical continuity check to confirm wiring integrity from control panel's terminal block to the field instrument. Please note that field cabling starts from field instrument and goes through Junction boxes and marshaling cubicle to reach termianal blocks of the control panel
2.Hot loop check
After successful cold loop check, each I/O is subjected to hot loop check. In this testing entire loop functionality is checked by simulation of the signal with power up from DCS or PLC
1.Calibration range
2.Activation of inputs / outputs / Field switches / Solenoids
3.PLC/DCS register updates
4.SCADA updates
| Is This Answer Correct ? | 102 Yes | 2 No |
Answer / jain
Cold loop check may also called as continuity test, to identify weather the cable are terminated at its correct terminal blocks from field side instruments to Control panel. At this time no power is present in the loop, or it may be isolated from the power source. It can be done using a Multi meter.
Hot loop check is done after cold loop test to identify the instrument is at correct range, units, and its dependency with the control instrument. so can be change and calibrate using a communicator or manually while the instrument is energized from the panel by 24 volt or vice versa.
| Is This Answer Correct ? | 11 Yes | 0 No |
Answer / hasan
Cold loop checking = continuity test, ir test make sure the cables are damaged or un damaged
Hot loop checking = instrument functionality test its means the instrument is in running condition if any fault may occur r not its should be make sure
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / ajinkya
I think...
Cold loop test is done using simulator
Hot loop test is done actually in field
| Is This Answer Correct ? | 6 Yes | 63 No |
Answer / jaydip khatri
hot loop mean instrument to J.B. & cold loop mean J.B. to panal.
| Is This Answer Correct ? | 5 Yes | 73 No |
Technician A says the brake warning light is connected into both the parking and service brake systems. Technician B says the brake warning light will come ON only if the service brake system fails. Who is correct?
what will be the output of a temperature transmitter if temperature is 120 degree celcius?
1.can you use SCADA instead of DCS,DCS instead SCADA 2.Difference between DCS and PLC,can their role be reversed i.e. role interchange 3.Difference between RTU and PLC
0 Answers IOCL, Lakshmi Machine Works,
how many maximum enter 2mm Dia solid cylindrical pipe into 8mm Dia hollow cylindrical pipe. give answer with calculation.
If a flow transmitter (magnetic type FT) that can measure flow and temperature, then why in some industries people use flow transmitter and temperature transmitter in the same line 1 after another? Even after 1 single flow FT is capable of measuring flow as well as temperature.
1 Answers Process Control Technologies,
how to work gas chromatography explain principle ?
How to calculate mmwc values into tonnes?
what happen if i install my pressure transmitter below the elevation of pipe in natural gas service. Also support your answer
Flame scanner
HOW CAN I CONNECT ROSEMOUNT 3300 LEVEL TRANSMITTER TO Allen-Bradley SLC500
define feed forward control loop with example and drawing?
I need circuit for RTD senser?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)