Answer / ravi
1.Cold Loop Check
This is an electrical continuity check to confirm wiring integrity from control panel's terminal block to the field instrument. Please note that field cabling starts from field instrument and goes through Junction boxes and marshaling cubicle to reach termianal blocks of the control panel
2.Hot loop check
After successful cold loop check, each I/O is subjected to hot loop check. In this testing entire loop functionality is checked by simulation of the signal with power up from DCS or PLC
1.Calibration range
2.Activation of inputs / outputs / Field switches / Solenoids
3.PLC/DCS register updates
4.SCADA updates
| Is This Answer Correct ? | 102 Yes | 2 No |
Answer / jain
Cold loop check may also called as continuity test, to identify weather the cable are terminated at its correct terminal blocks from field side instruments to Control panel. At this time no power is present in the loop, or it may be isolated from the power source. It can be done using a Multi meter.
Hot loop check is done after cold loop test to identify the instrument is at correct range, units, and its dependency with the control instrument. so can be change and calibrate using a communicator or manually while the instrument is energized from the panel by 24 volt or vice versa.
| Is This Answer Correct ? | 11 Yes | 0 No |
Answer / hasan
Cold loop checking = continuity test, ir test make sure the cables are damaged or un damaged
Hot loop checking = instrument functionality test its means the instrument is in running condition if any fault may occur r not its should be make sure
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / ajinkya
I think...
Cold loop test is done using simulator
Hot loop test is done actually in field
| Is This Answer Correct ? | 6 Yes | 63 No |
Answer / jaydip khatri
hot loop mean instrument to J.B. & cold loop mean J.B. to panal.
| Is This Answer Correct ? | 5 Yes | 73 No |
who discoverd ohms law?
What are the interlocks we have to check during the start up of LP/HP compressor?
who's take first position in process in the timing of new installation flow transmitter and control vavle. give the answer with logical trick.
HOW CAN I CONNECT ROSEMOUNT 3300 LEVEL TRANSMITTER TO Allen-Bradley SLC500
What are the charecterstics of control valve.
What is the difference bitween control net scaner and device net scaner
how to measure draft pressure in transmitter pl. give its single line digram
What kind of feedback is used in DP cells.
what is solenoid valve?
what is maximum temprature in instrumentation
i want to Measure the Difference pressure of Packed distillation Column of height 3 mtr. h.p. side connected to bottom & L.P. side connected to the top , so tell me what will be THE URV & LRV of that D.P. transmitter?
i want know about capillary type LT transmitter installation. we can install any location in between to HP and LP leg?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)