What's the difference between cold loop test and hot loop test?
Answers were Sorted based on User's Feedback
Answer / ravi
1.Cold Loop Check
This is an electrical continuity check to confirm wiring integrity from control panel's terminal block to the field instrument. Please note that field cabling starts from field instrument and goes through Junction boxes and marshaling cubicle to reach termianal blocks of the control panel
2.Hot loop check
After successful cold loop check, each I/O is subjected to hot loop check. In this testing entire loop functionality is checked by simulation of the signal with power up from DCS or PLC
1.Calibration range
2.Activation of inputs / outputs / Field switches / Solenoids
3.PLC/DCS register updates
4.SCADA updates
| Is This Answer Correct ? | 102 Yes | 2 No |
Answer / jain
Cold loop check may also called as continuity test, to identify weather the cable are terminated at its correct terminal blocks from field side instruments to Control panel. At this time no power is present in the loop, or it may be isolated from the power source. It can be done using a Multi meter.
Hot loop check is done after cold loop test to identify the instrument is at correct range, units, and its dependency with the control instrument. so can be change and calibrate using a communicator or manually while the instrument is energized from the panel by 24 volt or vice versa.
| Is This Answer Correct ? | 11 Yes | 0 No |
Answer / hasan
Cold loop checking = continuity test, ir test make sure the cables are damaged or un damaged
Hot loop checking = instrument functionality test its means the instrument is in running condition if any fault may occur r not its should be make sure
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / ajinkya
I think...
Cold loop test is done using simulator
Hot loop test is done actually in field
| Is This Answer Correct ? | 6 Yes | 63 No |
Answer / jaydip khatri
hot loop mean instrument to J.B. & cold loop mean J.B. to panal.
| Is This Answer Correct ? | 5 Yes | 73 No |
what is ment by PID controllers? explain with example?
what is the difference between DELTA-V & FOUNDATION FIELD BUS
what is the Difference betwee the Hart and smart series Pressure transmitter
1 Answers HPCL Mittal Pipelines Limited HMEL, Kastech Instrumentation,
A valve in series with an orifice plate (DP transmitter), is aligned for constant pressure in the pipeline, if there is an error dx, How to align it in process.
how to calibrate Necleuonic level transmitter.?
what is the deference bitween DCS and PLC SCADA HMI System for Power Process Industry.
Is there any relation between Artificial Intelligence and Instrumentation?
What is two wire system and how it work
If an Instrument has 550 ohm internal resistance and the cable used for that instrument is 0.5 ohm per meter resistance. If the voltage is 12volt.How much length cable can be used?
How do Foundation Fieldbus works? how the Communication Carries out from Foundation field bus,Field Devices and Controller? Were it's Application in the Field? For Which Signals this is Used? PLease Find this answer for this Question Detaile wise because i want to clear the Concept Regarding Foundation Field Bus,if Possible please attach the link of Document with Contails Diagramatic So that more esier for me.
how to derive kg/cm2 to mmwc? complete derivation.
Yokogawa CENTUMVP R6.09 unable to download to Engineering Station with ExaOPC R3.75 The issue is when I try to download the common project section to the Engineering Station (STN) from the HIS in System View, it is unable to connect. The error displayed is: WARNING: Could not connect to equalize destination. (7001) Retrying. Number of retries = 0/1 ERROR: LdXopsLoadMain: connect error 10060 ERROR: Processing terminated due to connection error. (7002) Equalization end with errors. STN0149 ---- ERROR = 2 WARNING = 1 ---- Background: >Updated the ExaOPC software on the STN from 3.60 to 3.75 >STN operating system is Windows Server 2008 R2 >HIS operating system is Windows Server 2016 Stanard Solutions attempted include: >Ensuring all IP addresses are correct and all networked devices can be pinged. >The ability to ping a device using its host name from another device (<ping STN0149> from HIS) >Ensure both devices firewalls are disabled. >The antivirus installed on the STN is disabled. >Ensuring both devices are within the same workgroup. >Added both devices to each other's Host and LMHost files. >Running IT Security tool after changing any administrative settings.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)