What's the difference between cold loop test and hot loop test?
Answers were Sorted based on User's Feedback
Answer / ravi
1.Cold Loop Check
This is an electrical continuity check to confirm wiring integrity from control panel's terminal block to the field instrument. Please note that field cabling starts from field instrument and goes through Junction boxes and marshaling cubicle to reach termianal blocks of the control panel
2.Hot loop check
After successful cold loop check, each I/O is subjected to hot loop check. In this testing entire loop functionality is checked by simulation of the signal with power up from DCS or PLC
1.Calibration range
2.Activation of inputs / outputs / Field switches / Solenoids
3.PLC/DCS register updates
4.SCADA updates
Is This Answer Correct ? | 102 Yes | 2 No |
Answer / jain
Cold loop check may also called as continuity test, to identify weather the cable are terminated at its correct terminal blocks from field side instruments to Control panel. At this time no power is present in the loop, or it may be isolated from the power source. It can be done using a Multi meter.
Hot loop check is done after cold loop test to identify the instrument is at correct range, units, and its dependency with the control instrument. so can be change and calibrate using a communicator or manually while the instrument is energized from the panel by 24 volt or vice versa.
Is This Answer Correct ? | 11 Yes | 0 No |
Answer / hasan
Cold loop checking = continuity test, ir test make sure the cables are damaged or un damaged
Hot loop checking = instrument functionality test its means the instrument is in running condition if any fault may occur r not its should be make sure
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / ajinkya
I think...
Cold loop test is done using simulator
Hot loop test is done actually in field
Is This Answer Correct ? | 6 Yes | 63 No |
Answer / jaydip khatri
hot loop mean instrument to J.B. & cold loop mean J.B. to panal.
Is This Answer Correct ? | 5 Yes | 73 No |
Working principle of vibration sensor?, Type of vibration sensor? , Can we use vertical instead of horizental or vice versa?, if not Reasons?
what barrier is used in process industry.
3 Answers ADMA OPCO, Process Industries,
for commissioning the DPT and Flow Transmitter , what kind of necessary activities we have to check and do? specially that orifice flange valve[ isolation valve}
What are the maximum packet size of: a) HART b) Profibus DP c)Profibus PA d) DeviceNet e) Foundation Fieldbus
What is diff between Ingral orifice and simple orifice?where it use?
in control valve is constructed as per API 6D or API 6A, then which standard is used for fire testing of valve?.
Boiler flame scanner working principle?
What are the cable come out from the paddle type flow sensor.and how is further connections
What are primary elements of measuring pressure? Which type of pressure can be measured by these elements?
i am preparing for BARC ,so plz mail me how to prepare for BARC. ALSO IF POSIBLE SOME RELATED QUESTIONS. MY MAIL ID IS khushi_4uall2003@yahoo.co.in
How many types of sensor
Exothermic reaction./ endothermic reaction