Answer / gaurav kale

you can use 0.5 Sq mm shieled for analog .....Upto 600 m no
problem ....but generally as per standerds above 500m you
will have to go with Fibre optic cable

Is This Answer Correct ?    9 Yes 6 No

When a field input to plc is coming from 400 to 600 meters and the input is in 24 V DC? So signal ..

Answer / laxit

For this type of circuit, use Relay output instead of
direct driving through the PLC output. As these SOV's are
not the low power wattage, Prefer to use 2.5 Sq.mm as a
general for such digital output.Relay contact shall be
selected accordingly.

Is This Answer Correct ?    0 Yes 0 No

When a field input to plc is coming from 400 to 600 meters and the input is in 24 V DC? So signal ..

Answer / jayeshpateler

as per the 1cm3 core wire will be find also check the
current require then as per the current if it is higher
than you can carry but if current is low then you need to
use the repeater for that.

Is This Answer Correct ?    4 Yes 5 No

When a field input to plc is coming from 400 to 600 meters and the input is in 24 V DC? So signal ..

Answer / mwah

yes gaurav kale is right about 0.5 sq.mm twisted pair
shielded cable but u have to install repeater to make sure
theres no degrading of the signal at the end.

Is This Answer Correct ?    2 Yes 3 No

When a field input to plc is coming from 400 to 600 meters and the input is in 24 V DC? So signal ..

Answer / janes

It is all depends on the Load of the Field Instrument.
After Getting the load apply the Voltahe Drop Formula.
Also the input is 24VDC but define the Amp. is it 20A/ 10A.
that is 24Vdc 10A.

For 24VDC 10A Power supply and the Field Instrument is SOV
with 18 Watts, and the Distance is 600 meter then use the 2
Core 2.5 Sqmm Cable as per below Formula.

% Voltage Drop = Length X Current X R Cos0 + X sign0 /
Number of run X Voltage X 10.

Is This Answer Correct ?    2 Yes 5 No

Post New Answer

More Instrumentation Interview Questions

how magentic flow tx. vortex flow tx & ultrasonic flow tx works and its prinicle?its callibtration prosedure?

1 Answers  


what is different between 2,3&4 wire rtd and how much maximum distance using plc to field.

0 Answers  


How can we test a bently nevda 3500/42M accelerometer monitor card by simulating it with test equipment?. what king od of signal (milli volts or volts or or resistance ) we should feed in the terminals of the card?

0 Answers  


compare the thermocouple and pyrometer,which one is the best?why?

4 Answers   Ramco,


whats the abbreviation of IOP? is it instrument of power or input open problem?

0 Answers  






WHAT DO YOU MEAN BY LOOP IN C.

2 Answers   Wipro,


Which of the following instruments consumes maximum power during measurement?

3 Answers  


what is zero and span ?

0 Answers  


If an Instrument has 550 ohm internal resistance and the cable used for that instrument is 0.5 ohm per meter resistance. If the voltage is 12volt.How much length cable can be used? Please tell me its Calculation formula.

5 Answers   MOL,


what is the procedure to isolate flow a transmitter and flushing it?

8 Answers   Petrofac,


why the discharge pressure of ID fan showing negative at fan running condition.(boiler operating condition.)

5 Answers  


Waht is surge in compressors and how to control it?

1 Answers   DEWA,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)