Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


I have a LT of 10000mmwc range. can i use this LT in 1000mmwc range of tank?? if yes than what happened???

Answers were Sorted based on User's Feedback



I have a LT of 10000mmwc range. can i use this LT in 1000mmwc range of tank?? if yes than what happe..

Answer / waqas ahmad

Your tx's range is 0~10000mmwc if u
use it at 0~1000mmwc head press tank
than it will indicate 10% level when tank
full. So just calibrate it (configure it) at
0~1000mmwc before take inservice for
actual reading of tank at output

Is This Answer Correct ?    17 Yes 3 No

I have a LT of 10000mmwc range. can i use this LT in 1000mmwc range of tank?? if yes than what happe..

Answer / ys

u can use this transmitter. but u should rerange the
transmitter.(ie if tank service is water and ur lt is dry
leg type,then LRV=0 and URV=1000MMH2O.. If ur lt is wet leg
calibrated, then LRV= -1000 AND URV=0 MMH2O)

Is This Answer Correct ?    2 Yes 0 No

I have a LT of 10000mmwc range. can i use this LT in 1000mmwc range of tank?? if yes than what happe..

Answer / carl_ellis

I have a LT of 10000mmwc range. can i use this LT in
1000mmwc range of tank?? if yes than what happened???

A change from a range of 10000 mmwc to 1000 mmwc is a turn
down of 10:1

If your transmitter supports a minimum range of 1000 mmwc
within the accuracy spec you require, then re-range the

transmitter and use it.

Most smart DP transmitters from major manufacturers will
support this.

Carl Ellis
Measure First

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

why generation of syncronized generator increases when frequency of grid is less then 50Hz & generation decreases when grid frequency goes up from 50 Hz, as comparision with set value entered in govering panel?

1 Answers  


What is instrumentation instrumentation engineering?

0 Answers  


What is difference between reset and initialization in industrial automation?

1 Answers   Marafiq,


I faced several time siemens ps2 positioner automatically getting Chang in it's set point direction after auto calibration  So is there any causes biside this or  any  permissives ?

0 Answers  


What is loop checking ?

10 Answers   Kharafi National, Petrofac, Samsung,


how u measure flow?orifice measurement?why all ft in square root?

1 Answers  


If a differential pressure transmitter is calibrated for 0~2500 mmH2o and transmits a 4~20mA dc signal. The transmitter is placed across an orifice plate which is sized to create 2500 mmH2o differential at 5000m3/Hr a) what is the flow rate when the transmitter signal is 13.0mA DC? b) what is the signal output of the transmitter when flow rate is 2500 m3/Hr ?

5 Answers  


What is the working principal of Mass flow transmitter?

1 Answers  


in which principle pressure tx,level tx ,flow tx,temp tx ,control valve works?

0 Answers   IOCL, JSW,


How addressable fire systems work? Pl. send details with architect.(Loop), also send details regarding Gas system. Pl. help me.Thanks

0 Answers   Siemens,


how to calibrate mass flow meter (Coriolis)? Example calibration range: 0 to 2500 kg/hr line size 3" fluid: Etheline glycol (MEG)

0 Answers   Honeywell,


SIR MAY I KNOW IF RADAR TYPE LEVEL TRANSMITTER SHOWING IN THE FIELD 0 % LEVEL AND IN DCS SHOWING 100% THEN WHAT IS THE CAUSE I CLEAN THE CHAMBER & TAKEN ONLINE BUT ONLY ONCE ITS BECOME ZERO IN DCS BUT AGAIN 100% SHOWING IN DCS,THEN I REMOVE THE POWER SUPLLY AND CONNECT IT AGAIN .IS IT OK BUT STILL IN THE DCS ITS 100% AND ON THE DISPLAY ITS INITILAZIATION PLEASE HELP ME READRING THIS?

4 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)