I have a LT of 10000mmwc range. can i use this LT in 1000mmwc range of tank?? if yes than what happened???
Answers were Sorted based on User's Feedback
Your tx's range is 0~10000mmwc if u
use it at 0~1000mmwc head press tank
than it will indicate 10% level when tank
full. So just calibrate it (configure it) at
0~1000mmwc before take inservice for
actual reading of tank at output
| Is This Answer Correct ? | 17 Yes | 3 No |
Answer / ys
u can use this transmitter. but u should rerange the
transmitter.(ie if tank service is water and ur lt is dry
leg type,then LRV=0 and URV=1000MMH2O.. If ur lt is wet leg
calibrated, then LRV= -1000 AND URV=0 MMH2O)
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / carl_ellis
I have a LT of 10000mmwc range. can i use this LT in
1000mmwc range of tank?? if yes than what happened???
A change from a range of 10000 mmwc to 1000 mmwc is a turn
down of 10:1
If your transmitter supports a minimum range of 1000 mmwc
within the accuracy spec you require, then re-range the
transmitter and use it.
Most smart DP transmitters from major manufacturers will
support this.
Carl Ellis
Measure First
| Is This Answer Correct ? | 1 Yes | 0 No |
why generation of syncronized generator increases when frequency of grid is less then 50Hz & generation decreases when grid frequency goes up from 50 Hz, as comparision with set value entered in govering panel?
What is instrumentation instrumentation engineering?
What is difference between reset and initialization in industrial automation?
I faced several time siemens ps2 positioner automatically getting Chang in it's set point direction after auto calibration So is there any causes biside this or any permissives ?
What is loop checking ?
10 Answers Kharafi National, Petrofac, Samsung,
how u measure flow?orifice measurement?why all ft in square root?
If a differential pressure transmitter is calibrated for 0~2500 mmH2o and transmits a 4~20mA dc signal. The transmitter is placed across an orifice plate which is sized to create 2500 mmH2o differential at 5000m3/Hr a) what is the flow rate when the transmitter signal is 13.0mA DC? b) what is the signal output of the transmitter when flow rate is 2500 m3/Hr ?
What is the working principal of Mass flow transmitter?
in which principle pressure tx,level tx ,flow tx,temp tx ,control valve works?
How addressable fire systems work? Pl. send details with architect.(Loop), also send details regarding Gas system. Pl. help me.Thanks
how to calibrate mass flow meter (Coriolis)? Example calibration range: 0 to 2500 kg/hr line size 3" fluid: Etheline glycol (MEG)
SIR MAY I KNOW IF RADAR TYPE LEVEL TRANSMITTER SHOWING IN THE FIELD 0 % LEVEL AND IN DCS SHOWING 100% THEN WHAT IS THE CAUSE I CLEAN THE CHAMBER & TAKEN ONLINE BUT ONLY ONCE ITS BECOME ZERO IN DCS BUT AGAIN 100% SHOWING IN DCS,THEN I REMOVE THE POWER SUPLLY AND CONNECT IT AGAIN .IS IT OK BUT STILL IN THE DCS ITS 100% AND ON THE DISPLAY ITS INITILAZIATION PLEASE HELP ME READRING THIS?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)