I have a LT of 10000mmwc range. can i use this LT in 1000mmwc range of tank?? if yes than what happened???
Answers were Sorted based on User's Feedback
Your tx's range is 0~10000mmwc if u
use it at 0~1000mmwc head press tank
than it will indicate 10% level when tank
full. So just calibrate it (configure it) at
0~1000mmwc before take inservice for
actual reading of tank at output
Is This Answer Correct ? | 17 Yes | 3 No |
Answer / ys
u can use this transmitter. but u should rerange the
transmitter.(ie if tank service is water and ur lt is dry
leg type,then LRV=0 and URV=1000MMH2O.. If ur lt is wet leg
calibrated, then LRV= -1000 AND URV=0 MMH2O)
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / carl_ellis
I have a LT of 10000mmwc range. can i use this LT in
1000mmwc range of tank?? if yes than what happened???
A change from a range of 10000 mmwc to 1000 mmwc is a turn
down of 10:1
If your transmitter supports a minimum range of 1000 mmwc
within the accuracy spec you require, then re-range the
transmitter and use it.
Most smart DP transmitters from major manufacturers will
support this.
Carl Ellis
Measure First
Is This Answer Correct ? | 1 Yes | 0 No |
How do you calibration D.P transmitter? ?
Differentiate between ultrasonic flowmeter and radar type flow meter
what is the role of proportional in process control?
what is IEC code in cables & how to selecting cables?
What is protocol ?
can we replace a slot sensor (inductive type) with limit switch (potenial free contact / no-nc type).
In bently nevada vibration monitoring system,what is the reason to maintain the Resistance of the probe + extension cable equal to 95 ohm? If possible explain the basic principle of measurement with detail electronic circuits.
can i use capillary type dp transmitter converted to capillary type pressure transmitter. if i removed one side capillary tube its work correctly?
WHAT IS SELF CLEAN ELCTRODE IN MAGNETIC FLOWMETER?? WHAT DO YOU MEAN BY THIS TERM??
How servomotor controls throttle valve of TURBINE?
Explain the mechanism behind the turbine meter.
what are the problem's will accure in dcs or plc hadware and what are the solution for it?