i want to know how to calculate the battery capacity based
on the UPS . ex i want to run have one kva UPS Which should
run 10 hours ? in that case how many batteries to be
installed and what will be the AH Value .
Answers were Sorted based on User's Feedback
Answer / markandeya
total number batteries=votage required/votage of indivedual
cell
Ah value of indivedual battery=1.5*current*time(hours)
for an example:
votage required is 240
cell voltage is 12
then we require 20 cells.
if load is 1 kVa time is 10 hrs
we need 60 ah is required
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / jagdish raval
UPS KVA= 1. Then KVA= VA/1000. So I=KVA*100/V. If the V=48,
Then I=21. The load of UPS is 21Amp and it have run for 10
Hours, So Battery Capacity should 210Ah.
Is This Answer Correct ? | 1 Yes | 0 No |
State four advantages of hydro power station over nuclear power station.
what is meant by damper winding ?
What are eddy current and define rms value?
Explain about Leakage Test.
Atwhat condition reverse power relay will act?
What is the arc. I saw word arc in between sf6 & vcb brakers
difference between substation & grid substation?
Which are the types of breakers used in High Tension (HT) side?
When One Phase PT Missing (voltage drop ) this time current is zero of This phase(PT Missing Phase) and current is Not Zero of other Phase but PF is always Low That Why
What tests should i carry over on a newly rewinded DC Generator with voltage rating of 38 volts and current rating of 350 amps, to certify that the machine is OK?
In an electrical power supply,why if neutral phase of a 3phase supply fail over current occur but if it's single phase supply neutral phase fail low current occur?
power transmission pole used one support , that only for support or earthing