Difference in load break switch, isolator and circuit breaker.
Answer / jithendra
Load break switch (LBS) will operate on load only over current protection (FUSE) needs to replace the fuses
Isolater will operate for ON/OFF NO ANY TYPE OF protection
Circuit Breaker types 1.MCB 2.MCCB 3.ACB
1. trips for only over load.
2. trips for over load,short circuit.
3. trips for over load,short circuit,ground fault
Is This Answer Correct ? | 2 Yes | 0 No |
WHAT IS THE DIFFERENCE BETWEEN VOLTage and potential diff
1.why are not using acb 33kv ht side? is there any problem 2.what is difference between acb,vcb,sf6 breackers? 3.what is the function of invertor and convertor in ups?
What is an isolation transformer?Why do we need isolate circuits?Where do we use them?
It is used or not HT cable single core 630 sqmm in LT 3 phase capacitor bank which is used in PCC(power control center).
What will be happend if we not ground CT secondary?
3 Answers Enercon, Engro, THDC,
Is it true that in the 3 phase transformer, the limbs of the core are at 45 dgrees to each other. if true, why?
how the reverse power relay acts..
What is the meaning of maximum demand
Which type of air compressor is used now a days in the market. Keeping in mind of energy efficiency and maintenance points. Relevant documents may also be sent on mentioned email ids.
how to calculate overall efficiency of diesel generator set? give us a formula with an example.
Why the resistance grounding (NGR) is better than Solid grounding?
what is the purpose of slope in the differential relay?why we are using two slope?but in busbar differential we are using only one slope.why?