How to calculate the CFM to TR?
What is the Formula
Answers were Sorted based on User's Feedback
Answer / thirukumar
each TR = 400 CFM
thumb rule
200 Sq.ft = 1 TR ..... 150 to 200 Sq.ft = 1TR
Is This Answer Correct ? | 301 Yes | 72 No |
Answer / shashi
inorder to calculate tr you can use following formula:
Delta T in F X Flow in USGPM / 24
Is This Answer Correct ? | 73 Yes | 31 No |
Answer / sreenivasa rao avupati
We have to do Heat load calculation where we can achieve at
Grand total heat ( Sum of Grand Sen Heat + Grand Lat Heat).
TR = (GTH*1.05)/12000 TR - GTH in Btu/Hr
Calculation of TR from CFM is a thumb rule and dependa upon
inside design conditions. For Comform applications ( DBT-
Inside 2DegC & 55% RH we amy consider 400 Cfm per 1 TR).
In case of low temperature ( DBT:23+/-2 Deg C and RH <50%
this can be 250 to 300 Cfm per 1 TR.
But my recommendation is to do rough Heat load calculation
which can give the appropriate TR requirement.
Regards,
Is This Answer Correct ? | 24 Yes | 5 No |
Answer / ramakrishna m.r.
each TR = 350 to 400 cfm as per manufacture
thumb rule
150 to 170 Sq.ft = 1 TR should not cross more than 180 sq.ft
Is This Answer Correct ? | 35 Yes | 22 No |
Answer / mahesh
Actually we are following the 1 TR =400 CFM consider it should be re-circulation system, because of we consider less T.R compare to Once-through system ,so 200 to 300 CFM for 1 T.R suitable for Once-through system.
otherwise 400 CFM consider for Once-through system AHU Capacity will be increased.so better to consider 200 to 300 CFM for Once-through AHU's.
Any answer or formula recording above concept ,please share
Is This Answer Correct ? | 4 Yes | 1 No |
how to identyfy cable sizes?
What is Automatic interlocking circuit dighram between two contactor for DG SET panel.
how kva rating of transformer is calculated.
6 Answers Fluor Daniel, Siemens,
Purpose of lighting transformer.
At which time Synchronous generator act as a Synchronous Condenser?
what is the purpose of using battery in dg sets, please specify in details.
why transmission voltage is 230kv and not 220kv which is a multiple of 11
1 Answers Mettur Thermal Power Station, Siemens,
Hysteresis loss in a core is due to what reason or property of the material used for that core?
what are the checks of diesel gensets
Why earthing is required for diesel tank?
Pls explan the OLR setting in VCB at HT yard
how to calculate the cable size depending on the amps?