How to calculate the CFM to TR?
What is the Formula
Answers were Sorted based on User's Feedback
Answer / thirukumar
each TR = 400 CFM
thumb rule
200 Sq.ft = 1 TR ..... 150 to 200 Sq.ft = 1TR
| Is This Answer Correct ? | 304 Yes | 72 No |
Answer / shashi
inorder to calculate tr you can use following formula:
Delta T in F X Flow in USGPM / 24
| Is This Answer Correct ? | 74 Yes | 31 No |
Answer / sreenivasa rao avupati
We have to do Heat load calculation where we can achieve at
Grand total heat ( Sum of Grand Sen Heat + Grand Lat Heat).
TR = (GTH*1.05)/12000 TR - GTH in Btu/Hr
Calculation of TR from CFM is a thumb rule and dependa upon
inside design conditions. For Comform applications ( DBT-
Inside 2DegC & 55% RH we amy consider 400 Cfm per 1 TR).
In case of low temperature ( DBT:23+/-2 Deg C and RH <50%
this can be 250 to 300 Cfm per 1 TR.
But my recommendation is to do rough Heat load calculation
which can give the appropriate TR requirement.
Regards,
| Is This Answer Correct ? | 24 Yes | 5 No |
Answer / ramakrishna m.r.
each TR = 350 to 400 cfm as per manufacture
thumb rule
150 to 170 Sq.ft = 1 TR should not cross more than 180 sq.ft
| Is This Answer Correct ? | 35 Yes | 22 No |
Answer / mahesh
Actually we are following the 1 TR =400 CFM consider it should be re-circulation system, because of we consider less T.R compare to Once-through system ,so 200 to 300 CFM for 1 T.R suitable for Once-through system.
otherwise 400 CFM consider for Once-through system AHU Capacity will be increased.so better to consider 200 to 300 CFM for Once-through AHU's.
Any answer or formula recording above concept ,please share
| Is This Answer Correct ? | 4 Yes | 1 No |
Name of Hydrocarbon gases.
a 440v 60hz 03 phase 100kw generator can deliver how much power in kw for 220v 60hz 01 phase load?
What is expand formation of AYFY cable
How to decide the fuse ratings for potential transformer
what is a relay?
in alternator what is use of AVR ? how AVR is operating either AC or DC?
what is the formulae of calculating voltage drop?
how to calculate EXCITATION VOLTAGE & CURRENT in ALTERNATOR
What is the purpose of SOTF being used inspite of distance Protection given?
What is the rating of a circuit breaker needed for 300 kv load in 33KV supply line of 33/415 transformer ? Whether 800/1200 amp vaccum circuit breaker can perform for a 33 KV line in input in 415 volt in output of the transformer ?
what is power system.........?
how megger step up the DC voltage
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)