How to calculate the CFM to TR?
What is the Formula
Answers were Sorted based on User's Feedback
Answer / thirukumar
each TR = 400 CFM
thumb rule
200 Sq.ft = 1 TR ..... 150 to 200 Sq.ft = 1TR
| Is This Answer Correct ? | 304 Yes | 72 No |
Answer / shashi
inorder to calculate tr you can use following formula:
Delta T in F X Flow in USGPM / 24
| Is This Answer Correct ? | 74 Yes | 31 No |
Answer / sreenivasa rao avupati
We have to do Heat load calculation where we can achieve at
Grand total heat ( Sum of Grand Sen Heat + Grand Lat Heat).
TR = (GTH*1.05)/12000 TR - GTH in Btu/Hr
Calculation of TR from CFM is a thumb rule and dependa upon
inside design conditions. For Comform applications ( DBT-
Inside 2DegC & 55% RH we amy consider 400 Cfm per 1 TR).
In case of low temperature ( DBT:23+/-2 Deg C and RH <50%
this can be 250 to 300 Cfm per 1 TR.
But my recommendation is to do rough Heat load calculation
which can give the appropriate TR requirement.
Regards,
| Is This Answer Correct ? | 24 Yes | 5 No |
Answer / ramakrishna m.r.
each TR = 350 to 400 cfm as per manufacture
thumb rule
150 to 170 Sq.ft = 1 TR should not cross more than 180 sq.ft
| Is This Answer Correct ? | 35 Yes | 22 No |
Answer / mahesh
Actually we are following the 1 TR =400 CFM consider it should be re-circulation system, because of we consider less T.R compare to Once-through system ,so 200 to 300 CFM for 1 T.R suitable for Once-through system.
otherwise 400 CFM consider for Once-through system AHU Capacity will be increased.so better to consider 200 to 300 CFM for Once-through AHU's.
Any answer or formula recording above concept ,please share
| Is This Answer Correct ? | 4 Yes | 1 No |
Can we use droop CT in neutral in place of W phase of alternator ?
Why substation battery room is coulered black?
please tell me how a surge protector work on a DC 48Volt.? please describe briefly.
what would u consider to be the basic purchase order information you would need to proceed with a cable inspection assignment?
how to select the automotive wire size by mathematical calculation. for xenon headlamp with ballast. the ballast given data voltage 10-17v,current permenant 6amp, run up phase is 15amp, peak at swicth on max 400micro sec is 40amp.the sum of cable resistance is 150mohm.please provide referenc document if any for relating the peak at switch on current,time & wire wire size
WHAT IS THE CURRENT CARRYING CAPACITY OF 2.5/3 CORE HI TUFF CABLE,WILL IT SAFLEY CARRY 8.6 AMPS OVER 120 METRES,CAN YOU ALSO ANSWER WITH FORMULA FOR WORKINGS OUT ,THANK YOU 3RDYR APPRENTICE.
% voltage variation in distribution a)1% b)5% c)10% d)15%
Why do we use copper cable for HT Supply and why not Aluminium?
when we connect the capacitor bank in series
plz tell me in detail about c.t. and p.t. ?
What is the effect of atmospheric pressure & Temp; on efficiency of motor? Why NGR(Neutral Grounding Resistor) is used in 132/11 KV Transformer & how? What is the use of Auto T/F in Grid Station?
why in US MAINTAIN 60hz,110volts when compared with 50hz,220v in india
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)