i want to know how to calculate the battery capacity based
on the UPS . ex i want to run have one kva UPS Which should
run 10 hours ? in that case how many batteries to be
installed and what will be the AH Value .
Answer Posted / markandeya
total number batteries=votage required/votage of indivedual
cell
Ah value of indivedual battery=1.5*current*time(hours)
for an example:
votage required is 240
cell voltage is 12
then we require 20 cells.
if load is 1 kVa time is 10 hrs
we need 60 ah is required
| Is This Answer Correct ? | 2 Yes | 0 No |
Post New Answer View All Answers
I have 2 KW electric water heater.I am gonna use it in controlling water temp.so I needed to increase or decrease the heating capacity.is there any electrical-electronic circuit for varying the resistance & so current?
what things to be considered when designing UPS
how to compute kAIC? with formulas...
what is meant by k-rating in isolation transformer?what is k9, k14 stands for?
How capacitor improves pf
What happens if the series current double?
any one guide me to reduce the power factor of diesel Generator from 0.97 Leg to 0.8 Leg.with out any change in my load.
Why do we perform an open-circuit test and short-circuit test on the transformer?
is there any lightning by passer is arranged in ship like buildings?
Explain the working principle of Synchronous Generator and Assynchronous generator?
Write the force balance equation of m ideal mass element.
List out the the types of Mounting Light fixture?
hey guys i scored 910 on GRE and 67 on TOEFL respectively.I have an aggregate of about 74%in my B tech.For which colleges should i apply for an MS program in electrical engineering.I am looking for colleges in NJ,SC,NC,GEORGIA, NY. Please reply with a good response.....
hi frnds what is meant by harmonics & what is meant by third hormonics,where its will occur ?thank u
in star-delta tranformer,if the input of star connection is 400/7v 3 kva then what is the output of delta connection?