Answer / m.gopinath
It will be better explained with a example:
The Geyser will have three terminals viz phase, neutrl and
earth. The phase and neutral are given to the Geyser coil
for heating and earth connected to Geyset body to avoid
body shock. If the earth and neutral are connected
together, the current will flow in the body not in the
geyser coil. Hence the geyser coil can not heated up.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / vijendra joglekar
We can short both earth and neutral notihng will hapen but
in case of any fault in the equipment the fault current will
flow directly to the earth .So as per the IEEE standard that
is not correct way to do the electrical coneection.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / kiran@c&selctric ltd
supporting that answer it also causes shock to human beings
when we toch the body
| Is This Answer Correct ? | 1 Yes | 0 No |
What is stacking factor? What is its approximate value?
how the testing of CT OF 400/200/100 done in33/11 kv s/s
what is the diffrance with elcb,rccb,mcb
If 440 V supply has given at the secondary winding of transformer at that time if we apply 11 KV at primery then what will happen???????
Two liquids hot and cold in two vessels are there and an metal bar acts as a conductor of heat between the two vessels. what happens then. what happens after 24 hrs?
which connection is safer series or parallel?usually which connection we prefer at home?
How can i calculate the Breaking capacity of molded case circuit breaker, is the breaking capacity of CB for Diesel generator shall be less than grid supply's breaker ?
What is T’Q and X’Q and X’D ? and what is saturated as well as unsaturated ?
how do we calculate length of starting time and repeated starting of a direct online starter?
what is the function of closing coil in air circuit breaker?
How can two 3 phase transformers of same KVA and Voltage be connected in parallel?
0 Answers Bernhard Schulte Shipmanagement,
While connecting the flood light plug on to the 415 V distribution panel,there was spark and the cable got burnt. Three ignitors of the flood light also burnt of. The lamps are of 400 W (total 6 lamps) connected through 1.5 mm2 cable. The plug was immediately removed from the circuit. There was a 30 mA RCD connected and a 250 A MCCB; however both did not trip. What could be the possible reasons for the circuit devices not to trip?Can someone assist please. Additional info if needed can be provided.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)