why is the vector group analysis done in transformer tests
Answers were Sorted based on User's Feedback
Answer / pratik
It is to be carried out to check whether the transformer
under test is suitable for parallel operation with another
transfomer having same vector group and voltage ratio but
difference in KVA rating.
| Is This Answer Correct ? | 192 Yes | 35 No |
Answer / sachin
Vector group analysis done in transformer test, so that we
can check the phase displacment and polarity of the
transformer.
| Is This Answer Correct ? | 119 Yes | 17 No |
Answer / fred jabagat
Vector Group can be used as basis in setting the phase
compensator factor for numerical transformer differential
relays, i.e. SEL387.
A 3-Ph Transformer is wired internally in different ways to
produce a desired phase position between primary and
secondary terminals.
IEC standards develop a transformer circuit configuration
and a corresponding vector group code which follows a clock
that represents a 30 degrees shift in every hour.
The CT's of a numerical transformer differential relays are
usually wired with its polarity mark facing away from the
protected winding. Because of the phase shift between the
primary and secondary terminals of the transformer it is
necessary to set a phase compensator factor to the
differential relay so that it will not trip on normal load.
| Is This Answer Correct ? | 38 Yes | 6 No |
Answer / saju thomas
Mostly using transformer phasing arrangements are
DYn11,DYn7,DYn5.This is related to phase
displacements.vector group test is doin for analaysing
transformer phaseangles as per the phasing arrangements
like DYn11 or DYn7 or ...
| Is This Answer Correct ? | 40 Yes | 11 No |
Answer / shrinivas
vector group are made to know at what position the secondary
winding of transformer we get star and delta voltages . and
it indicates the type of winding in primary and secondary
which helps in parallel operation of transformer with
different ratings having same vector group .
| Is This Answer Correct ? | 41 Yes | 13 No |
Answer / joe callaghan
Transformer vector relationship is tested by shorting the
primary A phase to secondary A phase, then applyying a
three phase voltage to the primary side of the transformer.
Voltage measurements are then taken as follows:
A-B
B-C
C-A
B-b
C-b
B-c
C-c
These values will then allow you to draw the vector diagram
of the transformer.
| Is This Answer Correct ? | 32 Yes | 9 No |
Answer / dinesh kumar
1,Vector group is done on transformer High voltage winding
with respect low voltage winding.
2,To find the phase angle/difference between different
connections in high voltage windings.
3,In three phase winding transformer there are 36 vector
groups.(1u1v1w 2u2v2w)
| Is This Answer Correct ? | 54 Yes | 39 No |
Answer / dhaval
to determine the primary and secondary winding of the
tranformer that how the winding is connected
| Is This Answer Correct ? | 20 Yes | 6 No |
i have faced a problem in ro plant grunfos make bm30type pump it is 22kw pump. We start this pump using siemens 3rw 4423-ibc44, 30kw softstarter but this soft starter will frequently failier so we planed to change dol starter. So pls tell anybudy its possible or not.
How RTCC panel is working and give single line diagram for RTCC with transformer?
what is the minimum winding resistance of 30hp compressor, to run or to switch on
for 12KW motor which cable size has to select for ex.10 meter.
We all have seen transmission and Distribution lines In transmission lines the voltage is high and current is low(to reduce I^2r loss) and in distribution lines voltage is low but current is high however the size of transmission wires is bigger than that of distribution wires even though the amount of current carried by the distribution lines is more than that of transmission lines why?
How amny AH battery required for 600va inverter ?And how many hours it will give backup for ceiling fan ?
is there any phase difference occurs while primary and secondary side mutual induction occurs?
What is difference between SMC supportg and Glass Fibre Reinforced Plastic Support.
flurescent bulb rating is to 230v,50HZ.now flurescent connected 230v,25HZ.whether nreduced frequency will affect the glowing properties of flurescent.
how electronic energy meter works?
Why frequency changes due to load variation in power system ? i.e why when load increases frequency decreases?
In HT overhead line why should provide top conducter which is not connected whith insulater..?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)