why is the vector group analysis done in transformer tests
Answers were Sorted based on User's Feedback
Answer / pratik
It is to be carried out to check whether the transformer
under test is suitable for parallel operation with another
transfomer having same vector group and voltage ratio but
difference in KVA rating.
| Is This Answer Correct ? | 192 Yes | 35 No |
Answer / sachin
Vector group analysis done in transformer test, so that we
can check the phase displacment and polarity of the
transformer.
| Is This Answer Correct ? | 119 Yes | 17 No |
Answer / fred jabagat
Vector Group can be used as basis in setting the phase
compensator factor for numerical transformer differential
relays, i.e. SEL387.
A 3-Ph Transformer is wired internally in different ways to
produce a desired phase position between primary and
secondary terminals.
IEC standards develop a transformer circuit configuration
and a corresponding vector group code which follows a clock
that represents a 30 degrees shift in every hour.
The CT's of a numerical transformer differential relays are
usually wired with its polarity mark facing away from the
protected winding. Because of the phase shift between the
primary and secondary terminals of the transformer it is
necessary to set a phase compensator factor to the
differential relay so that it will not trip on normal load.
| Is This Answer Correct ? | 38 Yes | 6 No |
Answer / saju thomas
Mostly using transformer phasing arrangements are
DYn11,DYn7,DYn5.This is related to phase
displacements.vector group test is doin for analaysing
transformer phaseangles as per the phasing arrangements
like DYn11 or DYn7 or ...
| Is This Answer Correct ? | 40 Yes | 11 No |
Answer / shrinivas
vector group are made to know at what position the secondary
winding of transformer we get star and delta voltages . and
it indicates the type of winding in primary and secondary
which helps in parallel operation of transformer with
different ratings having same vector group .
| Is This Answer Correct ? | 41 Yes | 13 No |
Answer / joe callaghan
Transformer vector relationship is tested by shorting the
primary A phase to secondary A phase, then applyying a
three phase voltage to the primary side of the transformer.
Voltage measurements are then taken as follows:
A-B
B-C
C-A
B-b
C-b
B-c
C-c
These values will then allow you to draw the vector diagram
of the transformer.
| Is This Answer Correct ? | 32 Yes | 9 No |
Answer / dinesh kumar
1,Vector group is done on transformer High voltage winding
with respect low voltage winding.
2,To find the phase angle/difference between different
connections in high voltage windings.
3,In three phase winding transformer there are 36 vector
groups.(1u1v1w 2u2v2w)
| Is This Answer Correct ? | 54 Yes | 39 No |
Answer / dhaval
to determine the primary and secondary winding of the
tranformer that how the winding is connected
| Is This Answer Correct ? | 20 Yes | 6 No |
Is there chopping current in resistive circuit
What happen if you keep open the Neutral Grounding Switch in open condition of the HT Generator at starting and again on load if it open then?
The reason why the sending end and receiving end voltage sare almost equal when capacitive load is added.
what is the different between HT auxillary relay resistance and transformer tripping relay resistance?
what is the use of breather in transformer?
what are the tests comes under the type test, what tests comes under routine tests.
Hydro P.P. run @ 600 rpm,8pole, Nucler P.P @ 1500rpm 4 pole , ThermlP.P @ 3000 rpm 2 pole.Why this diffrence??? when we can generate electricity @ 600 rpm then Why we had incresed speed in NPP & TPP???
why is the power generator connected as star earthed or star earthed through reactance and what its features ?
from 33kv to 440v 2mva transformer how much full load current will be at ht side and lt side and which range of ctpt will be used?
what will happen if phases are not shorted with neutral in transformer impedance test? and if neutral is not connected with ground?
how to calculate the mf of kwh meter,if ct the ratio on meter is 100/5A
What is the restart inhabit setting in ABB spam150c relay (Motor protection relay)
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)