Answer / k.prakashchandra
As per IE Rules 1956,for EHT line the clearance above ground
of the lowest conductor shall not be less than 5.2 m + 0.3 m
for every 33000 V or part thereof by which the voltage
exceeds 33000 V ,provided the minimum clearance along or
across any street shall not be less than 6.1 m. So for 400
KV line, it works out to be 8.8 m
Is This Answer Correct ? | 49 Yes | 5 No |
Answer / alap
ground clearence means the height of middle of line between
two towers from ground... it is so designed as the sag is
minimum and stress on transmittion line is also minimum....
Is This Answer Correct ? | 27 Yes | 9 No |
8.8m As per IE Rules 1956,for EHT line the clearance above ground
of the lowest conductor shall not be less than 5.2 m + 0.3 m
for every 33000 V
Is This Answer Correct ? | 16 Yes | 3 No |
Answer / sutapa
Rohit Sing is a pure GANDU.......... Pls click yes or no
Is This Answer Correct ? | 13 Yes | 3 No |
Answer / rohit singh
here is list of height of tower according to the voltage....
11kv--7meter
33kv--11meter
132kv--20 meter
220kv --35 meter
400kv -- 50 meter..
if any one have problem then go see yourself at any 400kv substation...
Is This Answer Correct ? | 9 Yes | 13 No |
An 8 pole, 50 Hz, 3-phase IM is loaded to a poing where pull out torque will occur. The rotor resistance per phase is 0.3 ohm and motor stalls at 650 rpm. The slip when motor stalls is A 1 B 0 C 13.33% D 10.33%
In auto transformer if power transferred inductively and conductively are same, the ratio of output/input voltage is A 1 B 0.7 C 0.5 D none of above
how do u calculate CT rating for 10 mva transformer
What are the Application of CT & PT ?
Difference between megger test equipment and contact resistance meter test instruments?
what is the difference between earth and unearth cable?
Why generally the Rating of Transformers are in additions of 11 i.e. 11 kVA, 22 kVa, 33 kVA, etc........
how the percentage impedance affect the transformer loading when connected in parallel.?
What are the tests to be conducted in the electrical installations
Explain the fundamental difference between emf (electro motive force) and pd (potential difference) ?
What is mean by earthed & unearthed cable? Voltage grade of 1.9/3.3 kV(E), 3.3/3.3 kV(UE), 3.8/6.6 kV(E)what it indicates??
we have one oven for 12 zone we are installed ir lamp in oven we control load from thyrister and 0 to 5vdc so our zone no 8 getting bright in fraction of second so what we do.. Please answer