What happen if 1200KW/1500KVA alternator runs at no load
and high R.P.M.for one minute?
Answers were Sorted based on User's Feedback
Answer / dr.d.m.kothari
This will never happen because AVR and giverning
arrangement.Governor always control speed according to load.
| Is This Answer Correct ? | 9 Yes | 0 No |
If prime mover runs very high speed (without any control)
within a fraction of second rotor damaged and after that
Excitation system damaged.It will goes very dangerous
mode.So Never run Alternator without control.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / gurucharan singh
Generator loading & No load running has no effect its
paramaters, means generator run at no load as required.
Second part of question, generator are normally designed to
1.2 to 1.5 times of nominal speed to run for one minute
without any problem. Very generation system has a speed
controller & voltage controller which responce to these
condition within 1 to 2 seconds. I suggest interviwer shall
not confuse to candidate at interview.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / k.prakashchandra
There are over speed and over voltage relays to
protect.Governor becomes helpless if there is sudden throw
off of load,then over speed relay of the governor shuts down
the prime mover.With AVR, voltage does not increase.However
generators are designed to withstand runaway speeds for
short periods. Bearings are first to get damaged under
prolonged high speeds.Governors can also be made not to
allow for undesired high speeds with the help of braking
systems, if they are employed.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / k.prakashchandra
The above is applicable to hydro-generator
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / n r@jesh
D.G runs No load condition out put voltage will generated
high so, system protection will damaged
| Is This Answer Correct ? | 0 Yes | 1 No |
Why two phase welding machine is used instead of three phase welding machine.
Cables Construction hi friends, 0.6/1/1.2 kV LV , DC and Control cables are concentric copper conductor what does its means and what is the use of concentric copper conductor,and are this with copper tape shield or copper screening, ? thanks
int a,b ; a=b=10 ; if(a>b){ printf ("%d",a)}; no error output is a=10
Can we use Motor protection CB while we use the VFD for Speed control?? if not means please tell the reason!!!
what is the working principale of air circuit breaker ?
when the direction of a 3phase induction motor is reversed , is there any losses increases?
Explain Analog and Digital signals?
what will happen if i commission a transformer without connecting the neutral?
what is the Earth Voltages in Power Plants, Sub-stations, Industries, Residential & Commercial Buildings.
in telecom we are using neutral?
Find active & Reactive Power transmitted in a transmisston line having Vs30 degree(sending end) to Vr(zero degree)at receving end with line inductance X ohm. Vs(30degree)-------------------Vr(zero degree) X ohm
can I connect 25KvA stepdown transformer(RYB-440V,UVW-240V) to the output of 15KvA,3-phase online UPS(440V phase to phase)please brief.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)