Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


What happen if 1200KW/1500KVA alternator runs at no load
and high R.P.M.for one minute?

Answers were Sorted based on User's Feedback



What happen if 1200KW/1500KVA alternator runs at no load and high R.P.M.for one minute?..

Answer / dr.d.m.kothari

This will never happen because AVR and giverning
arrangement.Governor always control speed according to load.

Is This Answer Correct ?    9 Yes 0 No

What happen if 1200KW/1500KVA alternator runs at no load and high R.P.M.for one minute?..

Answer / subodhkhivsara

If prime mover runs very high speed (without any control)
within a fraction of second rotor damaged and after that
Excitation system damaged.It will goes very dangerous
mode.So Never run Alternator without control.

Is This Answer Correct ?    5 Yes 1 No

What happen if 1200KW/1500KVA alternator runs at no load and high R.P.M.for one minute?..

Answer / gurucharan singh

Generator loading & No load running has no effect its
paramaters, means generator run at no load as required.
Second part of question, generator are normally designed to
1.2 to 1.5 times of nominal speed to run for one minute
without any problem. Very generation system has a speed
controller & voltage controller which responce to these
condition within 1 to 2 seconds. I suggest interviwer shall
not confuse to candidate at interview.

Is This Answer Correct ?    2 Yes 0 No

What happen if 1200KW/1500KVA alternator runs at no load and high R.P.M.for one minute?..

Answer / k.prakashchandra

There are over speed and over voltage relays to
protect.Governor becomes helpless if there is sudden throw
off of load,then over speed relay of the governor shuts down
the prime mover.With AVR, voltage does not increase.However
generators are designed to withstand runaway speeds for
short periods. Bearings are first to get damaged under
prolonged high speeds.Governors can also be made not to
allow for undesired high speeds with the help of braking
systems, if they are employed.

Is This Answer Correct ?    1 Yes 0 No

What happen if 1200KW/1500KVA alternator runs at no load and high R.P.M.for one minute?..

Answer / k.prakashchandra

The above is applicable to hydro-generator

Is This Answer Correct ?    1 Yes 0 No

What happen if 1200KW/1500KVA alternator runs at no load and high R.P.M.for one minute?..

Answer / n r@jesh

D.G runs No load condition out put voltage will generated
high so, system protection will damaged

Is This Answer Correct ?    0 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

Why do you have to use Protecion relay with the function MTB ( Mechanical Trip Button ) for electrical system.

0 Answers   DT Technologies,


if there is fire alarm,what is ur activity?

4 Answers  


How stabilizer works??

0 Answers  


explain supply side and demand side energy management with advantages & disadvantages

0 Answers  


In our factory so many iron pillors are exists for supporting the shed/Hangar. If do more no of earthings at one piller instead of doing more earth pits in many locations and running earth strip around the hanger, I can save the money. Please suggest this method is acceptable as per Is specifications though the Earth resitance of the farthest piller is with in the limits as per IS specifications.

0 Answers   HAL,


why we are using earth pit in sub stations.?

0 Answers  


which protection function should measure RMS value of current&DFT value of current?

0 Answers  


What consists of 2 or more thermocouples to be connented series?

0 Answers  


how and where megger works?

9 Answers   Power Grid,


Dear Sir, we met a disaster with our 62.5 kva genset, after rewinding we informed by our contract engg that due to return current coming in neutral & impropper earthing this happend. But after all set up & load balance we checked & found again we have about 20 to 32 amp return current on neutral. we have 12 airconditioner + 12 mini fridge on single phase line. Pl suggest any idea to solved this problem

3 Answers  


whay we used silica gel in Transformer

3 Answers  


How single phase & 3 phase motor select rotating direction ie clockwise/anticlockwise

6 Answers   DRJ ARDE,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)