why do we use UPF watt meter in short circuit test of the
transformer and LPF watt meter in open circuit test of the
transformer
Answers were Sorted based on User's Feedback
Answer / pradeepkumar
In full load test, rated current
is made to flow and hence the
fraction of magnetising current
is less compared to the watt
component.. Hence power factor
would be nearly unity.. So UPF
wattmeter is used..
But whereas in no load test,
since the machine is not loaded,
watt component of current would
be negligible as compared to
magnetising component.. Hence
the power factor would be very
low.. So LPF wattmeter is
used..!!
Is This Answer Correct ? | 117 Yes | 12 No |
Answer / abhishek
if you calculate the power factor in the no load test conducted you will get a lower value (.2 to .5). In blocked rotor test or in load test the power factor will be usually higher if you calculate (around 0.7 to 0.8). So we use lpf and upf wattmeter respectively.
Is This Answer Correct ? | 4 Yes | 7 No |
Why Phase to Neutral get spark
How to calculate the CFM to TR? What is the Formula
does magnetic interlocking take place in an induction motor ?
which has more heat effect(dc or ac)
what is saturation kit?which use above 15 kw motors panel side.
what is the speed of the darkness?
What is auto reclose system in Circuit breakers
What is the function of lead sheath?
HOW TO SELECT THE COPPER CABLE SIZES OF MOTORS,TRANSFORMERS?
How vaccum is formed to create a vaccum interrupter or anything related with vaccum?
why the electrical plug point pin(earth) size in max
1 Answers Autoneum Nittoku, Bajaj,
please send me RRB electrical engineer previous year questions for Sr. Section Engineer