why do we use UPF watt meter in short circuit test of the
transformer and LPF watt meter in open circuit test of the
transformer
Answers were Sorted based on User's Feedback
Answer / pradeepkumar
In full load test, rated current
is made to flow and hence the
fraction of magnetising current
is less compared to the watt
component.. Hence power factor
would be nearly unity.. So UPF
wattmeter is used..
But whereas in no load test,
since the machine is not loaded,
watt component of current would
be negligible as compared to
magnetising component.. Hence
the power factor would be very
low.. So LPF wattmeter is
used..!!
| Is This Answer Correct ? | 117 Yes | 12 No |
Answer / abhishek
if you calculate the power factor in the no load test conducted you will get a lower value (.2 to .5). In blocked rotor test or in load test the power factor will be usually higher if you calculate (around 0.7 to 0.8). So we use lpf and upf wattmeter respectively.
| Is This Answer Correct ? | 4 Yes | 7 No |
What are the two types of compensation?
if an insulated power and control cables of a running gas diesel gensets laid direct in an open trench i.e, trench bed is not rcc of a power house in which rain water, spillage water alwas exists and all power control cables remains submerged even when gas gensets of 480 kw each runningin on load. These power &control cables runs from power house to switchgear room through these trenches in which water remains most of the time. pl explain its merit & de-merit
What is the differences in phase to phase voltages between star and delta connections of stator?
DO MEGGER TEST APPLIED ON SURGE ARRESTOR? IF YES THEN WHAT ARE THE ACCEPTED R VALUE REQUIRED FOR SURGE ARRESTORS FOR VOLTAGE LEVEL 11KV, 33KV
length of 4 core cable 95mm from substation LV VFD panel to Motor at field approximately 150 meter. Motor stop and power has been isolated from LV MCC ( Substation )to disconnect Motor for services. After Motor completed service propose to reinstall and reconnect Motor Cable, found earth cable sparkling during touching at metal / motor body. Inspect by clamp meter found earth cable have current flow AC 1-2amps and all earth cable at MCC LV also have current flow as same value. why it is happen?
ho w to make Incident and accident reporting
what is sevice settings for mccb?How can be it setted?
234 MVA Generator 3 phase Short circuit current Values required? Gen set Rating-234 MVA, Gen Voltage-18kv, PF;0.8, Xdv:23.5 %, Transformer Rating-18/380KV, 680MVA,Yndd1 two winding, Step up TR, ZT:35.50 %,X/R 4.33 Gen CB Position, CB open ,Disconnected open, Generator Running Voltage 18 Kv, Bi mistakes generator side earth switch Closed during that time short circuit current level in 3 Phase required, and how to test on site 234MVA Generator Short circuit current,
what is meant by negative conductor?
what is the size of ht cable of 33kv ht line and transformers ratings are 2.5mva and 5.5mva.please send formula also.
Why in ESP Positive earthed
what is SMDB
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)