We have one Energy meter for Measuring the
voltage,current,power,energy(KWH,KVARH,KVAH) & power
factor.The problem is that the meter does not show whether
the PF is lagging or leading.So i want to know that is
there any way or calculation to find out that whether the
PF sign (lagging or leading) depending upon the above
mentioned parameters?
Answers were Sorted based on User's Feedback
Answer / john
Is this a revenue meter from the utility company or a power
quality meter? In the case of a power quality meter, there
should be something letting you know if your PF is in a lead
or lagging. I have an Amprobe DMII Pro and it showes an i
after the PF to indicate lagging, .98i, and a c to indicate
leading, .98c. I have also seen meters with lagging PF -0.98
and leading +0.98. Another simple thing you can do is look
at your VAR, if it is in the negative, your in a lead.
As far as a revenue meter from the utility company is
concerned, call the utility company and ask them.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ram
please check the meter must be indicating sign as +
(leading) or - (Lagging) power factor.
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / ds01151
By using the formula KW/KVA you can find the pf
| Is This Answer Correct ? | 2 Yes | 4 No |
Answer / ashwini
by using formula p=vicos(pf) v can calculate power factor......
| Is This Answer Correct ? | 1 Yes | 9 No |
Weather power factor correction needed for synchronous motors?
How many points does a Circuit can have?
1. what is the power factor of a purely inductive load? 2. Which type of transformer connection is preferred in case of power supply transformers? 3. In power transformer usually which winding is closer to the core? 4. what will happen to the generated emf if the no. of poles of an alternator is increased?
What is the field weakening mode of a ac motor?
WHAT IS MEANT BY vfd(VARIABLE FREQUENCY DRIVE )HOW CAN WE APPLY VFD TO MOTOR ? I WANT FULL DETAIL IF ANYBODY KNOW THE WEBSITE FOR THAT PLZ SEND .THANK U
how CBCT works?
What should be the minimum and maximum ohmic value for earthing?
how meger function
How much inductance or resistance require as a starter in series with induction motor of specific capacity(e.g. 5 hp) ? What is formula for it ?
solar inverters was not connected to the nuteral link .this nutwral possible to any other systems
what is slip?
While connecting the flood light plug on to the 415 V distribution panel,there was spark and the cable got burnt. Three ignitors of the flood light also burnt of. The lamps are of 400 W (total 6 lamps) connected through 1.5 mm2 cable. The plug was immediately removed from the circuit. There was a 30 mA RCD connected and a 250 A MCCB; however both did not trip. What could be the possible reasons for the circuit devices not to trip?Can someone assist please. Additional info if needed can be provided.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)