We have one Energy meter for Measuring the
voltage,current,power,energy(KWH,KVARH,KVAH) & power
factor.The problem is that the meter does not show whether
the PF is lagging or leading.So i want to know that is
there any way or calculation to find out that whether the
PF sign (lagging or leading) depending upon the above
mentioned parameters?
Answers were Sorted based on User's Feedback
Answer / john
Is this a revenue meter from the utility company or a power
quality meter? In the case of a power quality meter, there
should be something letting you know if your PF is in a lead
or lagging. I have an Amprobe DMII Pro and it showes an i
after the PF to indicate lagging, .98i, and a c to indicate
leading, .98c. I have also seen meters with lagging PF -0.98
and leading +0.98. Another simple thing you can do is look
at your VAR, if it is in the negative, your in a lead.
As far as a revenue meter from the utility company is
concerned, call the utility company and ask them.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ram
please check the meter must be indicating sign as +
(leading) or - (Lagging) power factor.
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / ds01151
By using the formula KW/KVA you can find the pf
| Is This Answer Correct ? | 2 Yes | 4 No |
Answer / ashwini
by using formula p=vicos(pf) v can calculate power factor......
| Is This Answer Correct ? | 1 Yes | 9 No |
sir i have applied for isro-09. still i did not got the HALL TICKET.
is there any difference in reading or error in value, if we connect the R phase in Y terminal and Y phase in R terminal of electronic energy meter of 11 kv feerders???
if flux and load static in dc motor and supply voltage increases 20% then what happened in speed
What are the factors to be considered during the Synchronization?
374kvar capacitor bank connected across 600kw,6.6kv motor.what will happen if motor run at 50% , whether full kvar applied or half?
Capacitor panel CT is normally fixed on Y phase of the main panel.why???
What happen if an alternator rotates in reverse direction?
11 KV distribution system where neutral is produced ?
4 Answers ciss, TATA, Tata Motors,
wat is syncronization . wat parameter will take for syncronization.
what heppend if we are connected u1-v1-w1 as a star point in the place of u2-v2-w2 in power genration
What are the different towers used in 132kv transmission line? what are the differences between the P,R,S towers used in 132KV and detailed explanation
i had aplied Hindustan Petroleum corporation limited for the post of maintenance technician -Electrical,i want model questions,if anybody have please send it or please advice?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)