wat is syncronization . wat parameter will take for
syncronization.
Answers were Sorted based on User's Feedback
when one Generator is running and suppose its rating is
1500 kva/1200 kw,and load increased and we wants to put
more load on GENERATOR . So then we have to run second
generator and to be shift some load on second generator,
otherwise the generator will be over loaded and tripped on
over-load fault. when we connect two generators parrallel,
this arrangement is called synchronisation.we connect the
out-put supply of both generators parallel by
synchronisation.In synchronisation we have to match these
parameters--phase sequence, frequency and voltage.when all
three parameters match we ON the breaker and
synchronisation complete and now we can put more load
(about 2000 kw) on generator.
Is This Answer Correct ? | 17 Yes | 1 No |
sychronisation is important when parrallel operation of two
generators or when we connect a generator to grid.
The generator supply must only be connected to a live
grid,
1. Phase angle difference
2. Voltage differnece
3. frequency diffenrence (slip)
between the generator and grid voltage are within
permissible limits and the phase sequence of both generator
and grid rotating field should be identical.
Is This Answer Correct ? | 3 Yes | 2 No |
1) What is difference b/w impedence relay and differential relay? 2) what are substations equipments? 3) what is difference b/w circuit breaker and isolator? 4)what are the types of circuit breakers? 5) which medium is mostlty used in circuit breakers and why it is used?
How calculate cable size & voltage drop for the following requirement connected load 150 KW distance cable length 1000 M voltage 3 phase 415 v.
thyristor controlled APFC panel design parameter?
if a 3phase motor runnig in star delta starter with full load of its,and its rated 15 amps.now we conneted over load thermal relay at its main contactor,here what will be our amps sittings?
what is the type of winding connection( star or delta) in 1HP to 5HP motors. How to check the motor winding connections( star or delta) if not provided in the nameplate?
Damping resistor provided in open delta (tartiary) winding of a measuring PT at the incoming of a MV inverter drive panel is getting heated up. Can any body explain the reasons and suggest the remedy?
what about the power of wattmeter at starting and loding?
how much Watt can we fully load a transformer
what is busbar. how many types of starter.what appartus will be used to improve voltage.what is the function of starter.what is b.h.p.what material is used for earthing.
what is 11kv cable
what the different between earthing and grounding?
why commutator are not used in rectification purpose in power electronics?