Capacitor panel CT is normally fixed on Y phase of the main
panel.why???
Answers were Sorted based on User's Feedback
no my friend,it depends on APFC relay,
1.in L&T make APFC relay ct is looped in R-phase.
2.in Sentron make APFC relay ct is looped in Y-phase.
3.in Sycon make APFC relay ct is looped in B-phase.
if you have any dout see all above relays wiring diagram.
For measuring PF APFC relay required any two phases & one CT sence on remaining phase from main PCC Phase.
Eg.(R-Y phase & BCT from Main Panel)
From--Rajendra Sawant
Miraj.
| Is This Answer Correct ? | 9 Yes | 0 No |
Answer / zia
Good day friends
some time some of factory's lode not same in R,Y,B.
Example R=155amp, y=140amp, b=145amp which one we selected
for apfc relay for sense observing p-f . we are selected the
maximum amp flow phase.it can be R or Y or B. for good pf
rating.
so its a CT depends on the flowing amp of the phase
| Is This Answer Correct ? | 3 Yes | 1 No |
Thanks Zia Mam,For Sharing Additional information,but what about the manufacturing relay companys who manufacture the relay which has R,Y,B phase Selection of CT which i have mentioned in above answer,should we select our relay as per our Phase Load.
From-Rajendra Sawant
| Is This Answer Correct ? | 0 Yes | 1 No |
how point on wave controller works.
pre arcing time of ehv breaker
how to combine two linear transformers...............
In 3phase power= Root*3*v*i*cos@ What is the power in 2phase....??? and Derive it
How can you start-up the 40w tube lite with 230v AC/DC without using any choke/Coil?
What is block diagram?
Hi frnds :) plz tell me that i have 100 KVA 3 phase generator so by thumb rule 100*1.4 = 144 amps and generaly we can operate at 80% load...so it will 144*0.8 =112 amps.... so now i m confused about single phase load.....if we use that generator only for single phase the that 112 amps is total single phase load or i can give 112 amps at red 112 amps at yellow and 112 amps at blue.... i mean that total single phase load that 100 KVA generator will take is 112+112+112=336 amp ??
what is impedence of transformer? its formula
why we do not switched on capicitor panel with DG Supply
How many straight through joint is permissible in single core 33kv XLPE cable for a length of 985 mtr.
What is on delay and off delay timers
how fault in an electric system is detected & hw protection of equipments is done ?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)