Capacitor panel CT is normally fixed on Y phase of the main
panel.why???
Answers were Sorted based on User's Feedback
no my friend,it depends on APFC relay,
1.in L&T make APFC relay ct is looped in R-phase.
2.in Sentron make APFC relay ct is looped in Y-phase.
3.in Sycon make APFC relay ct is looped in B-phase.
if you have any dout see all above relays wiring diagram.
For measuring PF APFC relay required any two phases & one CT sence on remaining phase from main PCC Phase.
Eg.(R-Y phase & BCT from Main Panel)
From--Rajendra Sawant
Miraj.
Is This Answer Correct ? | 9 Yes | 0 No |
Answer / zia
Good day friends
some time some of factory's lode not same in R,Y,B.
Example R=155amp, y=140amp, b=145amp which one we selected
for apfc relay for sense observing p-f . we are selected the
maximum amp flow phase.it can be R or Y or B. for good pf
rating.
so its a CT depends on the flowing amp of the phase
Is This Answer Correct ? | 3 Yes | 1 No |
Thanks Zia Mam,For Sharing Additional information,but what about the manufacturing relay companys who manufacture the relay which has R,Y,B phase Selection of CT which i have mentioned in above answer,should we select our relay as per our Phase Load.
From-Rajendra Sawant
Is This Answer Correct ? | 0 Yes | 1 No |
What is the electrical difference between Earthing Switch (ES) and Maintenance Earthing Switch (MES)?
what is a breaker fail relay
Details about Flux Compensated magnetic Amplifer starter for motors
why do we have 230v a.c. as general voltage for domestic supply rather than others?
what is the relationship between current&voltage in practical purpose ?
What happens if the negative to earth voltage is greater than positive to earth voltage in the battery of substation?
what does a string of resistors in a series will do?
What kind of battries are generaly used with Disel Generator?
can any one provide me a connection wiring diagram for a DG set control panel along with BOM?
what is the name of transformer oil.
Two CTs 1600/1 and 35/1 are in series. while checking the ratio test of a CT(1600/1),same 1600A will also pass through the CT having ratio 35/1. Will it be harmfull to the ct(35/1),if yes , what will happen.CT secondary is shorted
Give me check-list for electrical preventive maintenance of machine tool.