374kvar capacitor bank connected
across 600kw,6.6kv motor.what will
happen if motor run at 50% , whether
full kvar applied or half?
PF is better at full load . You may have to connect full KVAR at 50 % load
| Is This Answer Correct ? | 0 Yes | 0 No |
why ct's&pt'S out put called as burden,why compelsary short ckt the secondary of ct's while removing the burden?
what is the rating of Insulation tester for measure 15 KW, 3 phase 415V 50 HZ induction motor?
show the single line diagram of star delta starter with single phase preventer
What are the limitations of Kirchoff's laws?
In three pin plug 6 amp. 220V ac rating. Why earth pin diameter is higher than other two pin? What its purpose ?
Why you want to join non technical field when you are an engineer?
how meger function
What is the maximum allowed kwa through 2.5mm cable. Electric company installed 2 electric meter at my premises . Two jumper wires of 2.5 mm are used to connect . 2 single phase meters with allowable load 6 and 3 kwa. These jumper wires are taken from a 3 phase electric meter. Meters are in open Sun. What max load these wires can take.
Why only plate(copper) Earth pit given for neutral earthing? why not pipe(G.I) Earth pit?
What is gain margin?
why is electricity produced and distributed in multiples of 11. 440V, 11KV, 22KV, 132KV etc
1.wat is the advantage of induction motor? 2.wat is diffrence between 1-phase and 3-phase induction motor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)