What should be the voltage between Neutral and Ground in
secondary side of the step down transformer (230 V to 110 V)
with no load condition?
Answers were Sorted based on User's Feedback
Answer / katoch
it should be zero volts.but practicaly when we check
voltage b/w nutral and ground it is found near about 1 to 2
volts
Is This Answer Correct ? | 7 Yes | 1 No |
Answer / rams dharavath
The voltage between neutral and ground should be less than 5volts
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / kalidassallinterview
It should be zero. In power plant and substaton thay
maintain less then 1 ohm of earth resistence. So, to reduce
the voltae drop the neutral and body earth shold be perfect.
kd
9840159504
Is This Answer Correct ? | 0 Yes | 2 No |
Answer / k.p.sharma
it should be 55 volts if you keep isolated secondaries
(110v sIDE. REST ANSWERS ARE NOT RELEVENT WITH QYSTION
ASKED.
Is This Answer Correct ? | 0 Yes | 5 No |
why ht motors are star connected?
is ac supply can store
which plant has high load factor
2 v/500amp/hr to 1.80vpc at 20 degree celsious 2v/5ooamp/hr to 1.75 vpc at 77degree farren .this is the capacity of a battery .what is the meaning of this . can i get a detailed explenation
In UPFC,What is the need for Dc link ( DC capatior)?
There is 3phase power cable from 1 point to the other point which is 100m away. Two point equipped with power meter and recorded 1st point is 205kW while the 2nd is 202kW and each phase average carry 400amps. To calculate the resistance of the 3phase power cable, is the formula using will be P=I2R?
Which type of losses in transmission Line
In three pin plug 6 amp. 220V ac rating. Why earth pin diameter is higher than other two pin? What its purpose ?
I have a small system with two motors that are running on 380 vac, 60 hz. These motors are expensive and I usally get them from Brazil. I am adding another motor to the system, but I want to purchase a 480 vac, 60 hz motor to use. It will be on a VFD that is rated fro 380 thru 480. Is this posible and will I have to use a larger motor and derate it?
0 Answers US Electrofused Minerals,
Difference between hopkinson and swinburne's test
How much Fault current can be contributed by a motor?
What is limitedly stable system?