what is the diffrence between mmwc and kg/cm2 for pressure
measurment when we are using mmwc and when kg/cm2 and why?????
?? what is the reason
Answers were Sorted based on User's Feedback
Answer / subodh
1 Kg/cm2(g) = ? mmWC(g).
is mmWC is always absolute?
Is This Answer Correct ? | 13 Yes | 4 No |
Answer / anmol chute
MMWC and Kg/cm2 both are pressure measuring units but difference between both unit is in pressure range ,means MMWC unit used to measurement of low pressure and Kg/cm2 used for High pressure measurement.Because,
1Kg/cm2=10000 MMWC
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / vikesh mourya
Unit Conversion :-
1 kg/cm2 = 0.98 bar
1 kg/cm2 = 98.06 kPa = 0.098 MPa
1 kg/cm2 = 980.665 mbar = 10000 mmwc = 735.56 mmhg = 29 inhg
1 kg/cm2 = 14.22 psi (lb/in2)
1 bar = 1.01 kg/cm2
1 bar = 100 kPa = 0.1 MPa
1 bar = 1000mbar = 14.50 psi
BY:-
Vikesh mourya
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / tara chandra sah
To measure low pressure we need to use this unit of
pressure Hence 10000mmwc=1kg/cm2
1 Kg/cm2 is 1.033 bar or 1.033x10^5 N/m2
10000 mmwc= 1 kg/cm2
low pressure can also be
used for but the error in values will be more.
Basically 10000 mmwc is 1 kg/cm2 a.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / bipin
When use minimum pressure than mmwc & Higher press kg/cm2g
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / manimaran
when we r measuring very low pressure :: mmWC and general terms is Draft pressure and measuring high pr. :: kg/cm2/bar/psi...for example we r measuring like boiler furnaces pressure and flue gas path (draft) i.e very low pr.(250mmWC) so we r measuring in mmWC, and when we are calibrating the flow, draft and level transmitters we will indicate the range in mmWC. The error value for FSD will be higher side for the transmitters which are calibrated in mmWC.
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / sk singh
We are using the mmWC for very low or lower than 0 and more than 0 we are using Kg/cm2.
Is This Answer Correct ? | 4 Yes | 7 No |
Answer / vaibhav v t
First of all using kg/cm2 for pressure is absoltely
wrong.pressure is force per unit area and unit of force is
newton, so pressure unit is N/cm2 and not kg/cm2.MMwc is
used for low pressure measurement and N/cm2 is used for
high pressure measurement.
Is This Answer Correct ? | 29 Yes | 50 No |
What is the difference between intrinsic instruments and ATEX instruments?
I am applied 100 % pressure on to the air to open control valve,but the valve is not fully closed..and 10-15% is open the valve. how to calibrate the control valve?
Yokogawa CENTUMVP R6.09 unable to download to Engineering Station with ExaOPC R3.75 The issue is when I try to download the common project section to the Engineering Station (STN) from the HIS in System View, it is unable to connect. The error displayed is: WARNING: Could not connect to equalize destination. (7001) Retrying. Number of retries = 0/1 ERROR: LdXopsLoadMain: connect error 10060 ERROR: Processing terminated due to connection error. (7002) Equalization end with errors. STN0149 ---- ERROR = 2 WARNING = 1 ---- Background: >Updated the ExaOPC software on the STN from 3.60 to 3.75 >STN operating system is Windows Server 2008 R2 >HIS operating system is Windows Server 2016 Stanard Solutions attempted include: >Ensuring all IP addresses are correct and all networked devices can be pinged. >The ability to ping a device using its host name from another device (<ping STN0149> from HIS) >Ensure both devices firewalls are disabled. >The antivirus installed on the STN is disabled. >Ensuring both devices are within the same workgroup. >Added both devices to each other's Host and LMHost files. >Running IT Security tool after changing any administrative settings.
when an eddy current probe is installed inside of a turbine or compressor in case of probe problem same as:crash of head of probe,changing the scale factor because of low measuring gap(physical gap is ok(example=1.14mm)but voltage is reduced(example=-6 volts),is any way to check the probe,when the ohm of probe is ok.thank you,(Karim Tavakoli)
How to rerange a dp type level transmitter after installation?
What is the difference between sdv and bdv ?
what is droop mode n frequency mode in wood ward governor?
I am a instrument technician. recently i attend interview and face one of question for DP transmitter ,the client asking about the calibration of DP transmitter ,am answer the calibration procedure, they will ask one more question. why open LP side in atmosphere? i did not answer that question. so please help me and explain the particular question. Dear firends waiting for your valuable replay
3 Answers Qatar Petroleums, Samsung,
what is DCS?
what is sliding spool valves?
i have one temperature TX in my loop check time once i was remove elament temp gose maximum then i am conect corectly but still now temp showing maximum what can i do this problem?
how to relay switch sense the fault?