Trapezoidal footing length = 2m , B=1.7m D=0.5m and d-
0.15m. Can anybody help and calculate quantity of concrete
by explaining all formulas involved.
Answers were Sorted based on User's Feedback
Answer / kishore kumar
Input is insufficient.size of the column is missing.
If size of the column is 300 x 300 mm, then the volume will
be
= 2x1.7x0.15 + (0.5-0.15)/3 x ((0.3x0.3+2.0x1.7+sqrt
((0.3x0.3)(2.0x1.7))
=0.981 m^3
| Is This Answer Correct ? | 98 Yes | 37 No |
Answer / vishal gajjar
h(=D-d)\3 * A1+A2+SqrtA1A2 = Q1
A1*A2*thickness = Q2
Q = Q1 + Q2.
| Is This Answer Correct ? | 40 Yes | 11 No |
Answer / suresh,trichirapalli
Q1=2.1*1.7*0.5
Q2=(0.5-0.15)/3*((A1+A2)+(SQRT A1*A2))
A1=Area of bottom portion
A2=Area of top portion
TOTAL QTY=Q1+Q2
| Is This Answer Correct ? | 22 Yes | 8 No |
Answer / s s grewal
Before calculating the quantity of concrete required for size of pillar or size of footing at (D=0.5 m)
Formula :- L X B X d + D-d/3 x A1 + A2 + √(A1 X A2)
| Is This Answer Correct ? | 22 Yes | 9 No |
Answer / manpreet singh
suppose area at bottom A1 = (AxB) and area at top A2 (axb), where A,B,a,b are the respective lengths of footing top and bottom. further D is total depth and d is small depth of footing
formula is A1xd + (D-d)x(A1+A2 + sqroot {(A1xA2)/3}
| Is This Answer Correct ? | 18 Yes | 11 No |
Answer / r. dilli babu
Input is insufficient.size of the column is missing.
If size of the column is 300 x 300 mm, then the volume will be
=h/3(A1+A2+Sq root of A1square+A2square)
=((.5-.15)/3)(.09+3.4+(sq root of(.09 square + 3.4 square)))
=.116(3.49+(sq root of (11.5681))
=.116(3.49+3.401)
=.116*6.891
=.799 cum
| Is This Answer Correct ? | 8 Yes | 4 No |
Answer / sagar mistry
Here you have not given the column size.
So we assume column size 300mm X 300mm.
There is an Offset after the periphery of column & it is 75mm.
Rectangular Part
=L X B X H
=2 X 1.7 X 0.15
=0.51 cum
Trapezoidal Part
=(h/3)(A1 + A2 + SQRT ( A1 X A2 )
=((0.5-0.15)/3) ((2 X 1.7) + ((0.3+0.075)+(0.3+0.075)) + SQRT ((2 X 1.7) X ((0.3+0.075)+(0.3+0.075))
=0.12 ( 3.40 + 0.75 + 0.70 )
=0.57 cum
Total Concrete
=0.51 + 0.57
=1.08 cum
| Is This Answer Correct ? | 8 Yes | 4 No |
Answer / ashish parasiya
Question is not complete because one must require top are to calculate volume for trapezoid.
| Is This Answer Correct ? | 6 Yes | 3 No |
Answer / r. ansari
Formula for trapezoidal footing quantity
Q = h/3{(a+b)+√ab}, a&b is area of bottom and top portion
=0.5/3{2x1.7+0.15x0.15+√3.4x0.0225}
=0.583 Cu.m.
| Is This Answer Correct ? | 11 Yes | 10 No |
Answer / r. suresh
Input is insufficient.size of the column is missing.
If size of the column is 300 x 300 mm, then the volume will be
=H/3(A1+A2+sq root of A1+A2)
=((0.5-0.15)/3)(3.4+0.09+ Sq root of 3.4+0.09)
=0.621 Cum
| Is This Answer Correct ? | 4 Yes | 3 No |
a sewer which receives the discharge of no. of house sewer is called house sewer lateral sewer intrcepting sewer sub-main sewer
What Are The Different Type Of Slump Test Indications?
For fine aggregate which is most suitable River sand or crusher sand & why ?
1 building project (work in progress) and following are sum detail about his project 1) Using local rebar grade 415 2) Total built up area- 60000 sq.ft 3) Floors to be constructed – 21 storey 4) Estimated requirement of Steel per sq. foot – 7KG/sq.ft 5) Concrete grade – M35 6) Rebars mainly required (sizes)- 16,20,25,32 & (8 mm for stirrups) Wanted to ask u if this person uses 500D…what are the benefits he will be getting? Whether his per Sq. foot consumption can b reduce? If yes den around how much?
what isIS code no for preparation of BAR BENDING SHEDULE (BBS)
What is value of S.F at Point of contaflexure?
factor which affects design of concrete mix
i want to know the easy way to find the quantity of steel in a slab , coloumn
Why the finite element method is lower bound solution?
1) what is the seewage discharge per person per day taken for design purpose as per IS codes? 2) how to convert gauge to MM like if we measure 18G as our door frame then how much is it in MM ? 3) how much binding wire is required ti tie 100kg steel ? 4) while making rings in steel reinforcement , whether the corners of rings are deducted to take out cutting length ? 5) how much carbon content should be there in steel used for construction purpose? 6) what are fe415 & fe 500 and which bars are used in general civil works?
what is the minimum and maximum thickness of plaster.?
What is ratio if m30
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)