Answer / ekanadam naik
yes we ca operate dg set with transfer but voltage and
freqency must be matched, with help of PLC,
Is This Answer Correct ? | 20 Yes | 3 No |
Answer / a. venkatesh
All the power source it may be transformer or Alternator
(DG-DC power generator).
For parellel operation synchronisation is important. I.E
Voltage level, frequency, phase angle should be equal for
the both sources.
For checking the synchronisation previously DARK LAMP
METHOD was used. Now a days special relays used for this
purpose. Relays MES 120(Schneider), 7UT relays in Siemens.
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / sangram
yes, we can Theoretically do it. we want to use aditional
relay and some equipments like Reversepower relay, DF/DT.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / meka sekhar
theoretically DG can be operated parallelly with
transformer as long as voltage, frequqncy, phase angle are
within limits. However, in industrial practice, only
momentarily paralleling will be done between DG &
transformer. Sometimes if they want to check loading of DG,
it can be paralled with transformer so that it will not
affect loads which are connected to bus.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sangram patil
Yes, called as synchronizsation of DG & EB of both. for
this parallel operation we want to concentrate on Voltage,
Frequency & Phase angle of both of equal.
and for Auto loading & Autobalancing we want to use
Woodward, C&S OR scnhider make relay.
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / ram
no dg set can not be connected with x-mer DG can not give
constant freq.
Is This Answer Correct ? | 2 Yes | 9 No |
plz explain TSM and PSM.with example suppose ct ratio is 4000/5 and tsm is .15 and plug is at 3.75 if fault current is 8000A.so how i find relay oprating time.
2 Answers College School Exams Tests, ME,
when a 500kva-400hz single phase transformer operated on a 100hz supply then what will be kva required
where rlc series ckt used?
Why water bubbles when D.C. Current is passed through it? Why not when A.C. Current is passed?
why earth fault current is always less than the o/c
how will you determine the short circuit capacity of a network
what is units of resistance
In case of 3Phase Supply, Voltage R-Earth/Neutral - 220 Y-Earth/Neutral - 220 Z-Earth/Neutral - 220 Total is -> 660Volts Then Why it is said that 3Phase supply is 440
6 Answers Hindustan Unilever Limited,
Essential condition for parallel operation of two single phase transformer is that they should have same A polarity B kVA rating C voltage ratio D % impedance
EXPLAIN THE WORKING OF SERIES REACTOR IN HT CAPACITOR BANKS (FOR VOLTAGES & CURRENTS)
who is ohm's and his law ?
A commercial Building is designed with 14th floor levels with indoor substation of three phase transformer with rated capacity of 1000 Kva.The transformer delivered 65% of its rated capacity at 0.67 power factor lagging.Because of low power factor, the power customer was penalized and certain cost was charged accordingly based on every point percentage lower than 85%.This situation may repeatedly happen on the succeding energy bills of power customer.The power customer is desired to improve its historical power factor of 0.67 lagging and no further penalty be impose by the local power company on the next bill. Q: Identify the appropriate solution you want to offer to Client?.Justify SCIENTIFICALLY and MATHEMATICALLY the principles behind the solution.