Can we operate a DG Set in paralell with Transformer ?

Answers were Sorted based on User's Feedback



Can we operate a DG Set in paralell with Transformer ?..

Answer / ekanadam naik

yes we ca operate dg set with transfer but voltage and
freqency must be matched, with help of PLC,

Is This Answer Correct ?    20 Yes 3 No

Can we operate a DG Set in paralell with Transformer ?..

Answer / a. venkatesh

All the power source it may be transformer or Alternator
(DG-DC power generator).
For parellel operation synchronisation is important. I.E
Voltage level, frequency, phase angle should be equal for
the both sources.

For checking the synchronisation previously DARK LAMP
METHOD was used. Now a days special relays used for this
purpose. Relays MES 120(Schneider), 7UT relays in Siemens.

Is This Answer Correct ?    4 Yes 0 No

Can we operate a DG Set in paralell with Transformer ?..

Answer / sangram

yes, we can Theoretically do it. we want to use aditional
relay and some equipments like Reversepower relay, DF/DT.

Is This Answer Correct ?    2 Yes 0 No

Can we operate a DG Set in paralell with Transformer ?..

Answer / meka sekhar

theoretically DG can be operated parallelly with
transformer as long as voltage, frequqncy, phase angle are
within limits. However, in industrial practice, only
momentarily paralleling will be done between DG &
transformer. Sometimes if they want to check loading of DG,
it can be paralled with transformer so that it will not
affect loads which are connected to bus.

Is This Answer Correct ?    0 Yes 0 No

Can we operate a DG Set in paralell with Transformer ?..

Answer / sangram patil

Yes, called as synchronizsation of DG & EB of both. for
this parallel operation we want to concentrate on Voltage,
Frequency & Phase angle of both of equal.
and for Auto loading & Autobalancing we want to use
Woodward, C&S OR scnhider make relay.

Is This Answer Correct ?    0 Yes 1 No

Can we operate a DG Set in paralell with Transformer ?..

Answer / ram

no dg set can not be connected with x-mer DG can not give
constant freq.

Is This Answer Correct ?    2 Yes 9 No

Post New Answer

More Electrical Engineering Interview Questions

plz explain TSM and PSM.with example suppose ct ratio is 4000/5 and tsm is .15 and plug is at 3.75 if fault current is 8000A.so how i find relay oprating time.

2 Answers   College School Exams Tests, ME,


when a 500kva-400hz single phase transformer operated on a 100hz supply then what will be kva required

2 Answers  


where rlc series ckt used?

0 Answers   ABB,


Why water bubbles when D.C. Current is passed through it? Why not when A.C. Current is passed?

0 Answers  


why earth fault current is always less than the o/c

2 Answers  






how will you determine the short circuit capacity of a network

3 Answers   Dalkia,


what is units of resistance

3 Answers  


In case of 3Phase Supply, Voltage R-Earth/Neutral - 220 Y-Earth/Neutral - 220 Z-Earth/Neutral - 220 Total is -> 660Volts Then Why it is said that 3Phase supply is 440

6 Answers   Hindustan Unilever Limited,


Essential condition for parallel operation of two single phase transformer is that they should have same A polarity B kVA rating C voltage ratio D % impedance

1 Answers   wbsedcl,


EXPLAIN THE WORKING OF SERIES REACTOR IN HT CAPACITOR BANKS (FOR VOLTAGES & CURRENTS)

1 Answers  


who is ohm's and his law ?

1 Answers  


A commercial Building is designed with 14th floor levels with indoor substation of three phase transformer with rated capacity of 1000 Kva.The transformer delivered 65% of its rated capacity at 0.67 power factor lagging.Because of low power factor, the power customer was penalized and certain cost was charged accordingly based on every point percentage lower than 85%.This situation may repeatedly happen on the succeding energy bills of power customer.The power customer is desired to improve its historical power factor of 0.67 lagging and no further penalty be impose by the local power company on the next bill. Q: Identify the appropriate solution you want to offer to Client?.Justify SCIENTIFICALLY and MATHEMATICALLY the principles behind the solution.

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)