what is difference between differential protection and
distance protection and how we calculate the sloop?
Answers were Sorted based on User's Feedback
Answer / vel
differential relay works on the principle of kirchoff
current law. i.e incoming current = outgoing current if it
is not equal relay will give trip signal.it is used for
transformer and generator protection.
distance relay works on the principle of z=v/i. when z
value of the line fall below the set value relay will give
trip signal. it is used for tranmission line.
| Is This Answer Correct ? | 100 Yes | 6 No |
Answer / mohanraj
Differential protection is a unit protection, relay works
on the principle of Kirchoff's current Law.
Measuring element is Current Transformer.
The differential current measured between the incoming
current and Outgoing current must be negligible current
during stable and through fault condition. In case of
inzone fault or unstable condition (due to CT saturate)
relay will sense the differential current and issue the
trip signal.
Application: Transformer, Generator and Cable Protection.
**********************************************************
Distance protection is widely used in the transmission
network, its also called impedance protection because relay
operates with respect to fault impedance of the
transmission line. (Z=V/I)
Measuring element is Current Transformer and Voltage
Transformer.
Usually relay having 4 zones of the transmission line.
Zone1,Zone2,Zone3 will be forward zones (Towards the Line)
and zone 4 will be Reverse zone (Towards the Source).
| Is This Answer Correct ? | 51 Yes | 1 No |
Answer / jacob
A differential protection compares the currents flowing
into and
out from the transformer. Auxiliary current
transformer “aux.ct:s”,
for adjusting the phase angle and ratio are necessary.
Ratio correction
is normally calculated for tap changer at middle position.
Distance protection relays are the most common relays on
transmission
lines. The reason for this is the simple measuring
principle,
the built-in back-up and the low requirement on
communication with remote end.
The Distance protection relay is a directional
underimpedance
relay. Normally two to four measuring zones are available.
Basically the Distance protection relays measures the
quotient
“U/I”, considering also the phase angle between the
voltage “U”
and the current “I”. The measured “U/I” is then compared
with the
set value. The relay will trip when the measured value is
less than
the value set
| Is This Answer Correct ? | 46 Yes | 5 No |
Answer / raju t
Differential Protection:
1. It simultaneously compares the phaser difference & magnitude of the current entering & leaving the protected zone.
2. It works on kirchoff's current law
3. It is a unit protection scheme i.e. it needs current inputs from minimum two different sources.
4. Differential current = |I1+I2| --> Vector sum
5. It cannot be used to provide backup to other relays
6. %Slope = (Id2-Id1)/(Ib2-Ib1)
Distance Protection:
1. It calculates the apparent impedance of a line with the help of voltage & current input connected to the relay. If measured impedance falls below set impedance trip command is issued to clear the fault.
2. It works on impedance measuring principle
3. It is a non-unit protection but can be easily used as an unit protection by co-ordinating distance protection with PLCC
4. Z=V/I
5. It can be set to provide backup to adjoining lines & bus bar depending on the requirement.
| Is This Answer Correct ? | 30 Yes | 0 No |
Answer / gopal1986
define thermal overload protection and how to calculate tripping time in ABB relays.
| Is This Answer Correct ? | 0 Yes | 0 No |
What is meant by rotor?
suppose if oil in transformer is not used than what constructional change you will do,for insulation and cooling?
How to calculate cable sizing
when we catch any one of the phases with our both hands in air(without touching ground),our body acts as a conductor.is it correct.please clarrify it.
BRIEFLY EXPLAIN THE STORAGE CLASSES AND THEIR TYPES IN C
what is current check gurd relay?
What is servo motor? what is its purpose?
checklist of ELCB
why transformer is rated in KVA ?
One of our gas turbine generator unit "1st stage rotor ground fault" alarm was occured several times. we tried to measure some voltage vulue ground fault protection relay (UNS3020a made by ABB and we measured the value of: Ground: 0.9VDC 5V: 5.8VDC 24V: 23VDC u+: 300 – 350mVAC Rf1: 17.5mVAC Rf2: 17.6mVAC The unit still running and the alarm was reset. As of 6pm yesterday and unitl now no alarm happened again. I our protection relay was defective?
WHAT IS THE DIFFERENCE BETWEEN VOLTage and potential diff
why generator efficiency is more in swinburnes test?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)