Answer / blake australia
To detect earth faults:
Zero sequence refers to the current flowing during an earth
fault. 2methods of decting earth fault.
-Measure the current on the earth return cable
-Measure the current imbalance on the 3x phase cables (do
this by putting all three through the same core balance CT.
Is This Answer Correct ? | 24 Yes | 5 No |
Answer / prabhakar
For 51G protection we normally use the CBCT(Core balance
current transformer)for to detect the unbalance current
caused due to earth fault
Is This Answer Correct ? | 8 Yes | 3 No |