the distance from my office to d.g is aprox 400mtrs and
voltage drops ibn my office near about 40 volt what should
i do p[ls suggest.
Answers were Sorted based on User's Feedback
Answer / ps win
The drop in voltage from the origin of the circuit to any point in the circuit should not be more than 4% of the nominal voltage. I would like to suggest you that you should re-size the cable.
| Is This Answer Correct ? | 4 Yes | 0 No |
Friend
You can either shift ur DG near to ur office, or u change
the size of the cable connecting from DG terminal to switch
board, preferably with a copper cable. Present cable size
is very low compared to the distance and the load taken by
the cable, and hence u have a voltage drop of 40V.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / ssreenu
please tell me why we can't use capacitors in DG power?
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ps win
(+ or - 4% of nominal voltage can be acceptable.)
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / sree
Add capacitors in load side, which improves your PF as well
as voltage.
| Is This Answer Correct ? | 0 Yes | 2 No |
Consider three heater bank connected in 3 phase star with neutral.Each heater bank connected in each phase.So each phase get 230 volts supply.my question is,during balance condition, current flow in neutral or Not
What will be the effect if I use inverter as UPS mood?
what solid earthing means?
why is efficiency of transformer more than that of other rotating machines?
where any change in supply line due to the incipient faults in three phase induction motor
Diff between power trans and generating transformer?
Bus-bar is made of which material & name of mostly used material in bas-bar design ?
Resistance of low voltage side of transformer compared to high voltage side is A less B equal C more D depens on design
what is the use of megger? and types
11 Answers TNEB Tamil Nadu Electricity Board,
What is the difference between ground & earth or neutral
Why is starter necessary for a three-phase induction motor?
37 Answers BMM, Essar, Hero MotoCorp, ITI, Maruti Suzuki, Supertech, Watt,
How can the direction of a three phase induction motor be reserved
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)