WHY THE TRANSFORMER VALUE MEASURES IN KVA INSTEAD OF KW.
Answers were Sorted based on User's Feedback
Meenakshi my view is also very much in line with you said
but addition to above i like to add that the transformet or
a generator are a source and are designed for the load
according to the characteristic & they have nothing to do
with the power factor . As the power factor is not counted
they rated in KVA ( Because KW = KVA x PF vise versa KVA =
KW/PF ) Please correct if something more can be added.....
| Is This Answer Correct ? | 10 Yes | 3 No |
any device that acts as a source vil be rated in kva,n
hence transformer,generator,ups etc are rated in kva. n its
not becoz of copper loss n iron loss stories as mentioned
in some books.coz when i answered like this, i was told
wrong.if any improved answer, plz notify me.
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / jk
POWER GENERATOR AND POWER USER RATING IN KW
AND POWER TRANSMITTAL DEVICE IN KVA BCOZ THERE IS NO ROLL
OF PF
| Is This Answer Correct ? | 0 Yes | 2 No |
block diagram of 2 ups system connected in hot stand by mode?
What are the factor to be consider for CT selection in 132kV substation?
What is majour reason of Electrical Arcing ?
HOW DO YOU PROVE THE HIGH VOLTAGE CABLES OR BUSBAR IS DEAD EVEN AFTER IT IS DE ENERGISED
formula for calculation of switchgears(i.e. contactor, fuse, cb, relay etc.), if load current is given?
How to calculate voltage drop in copper and aluminium cable? I have laid 240Sq.mm Aluminium cable for the length of 600 Mtrs in 1 Mtrs underground. Normal load is 150A. Transformer is 630KVA, 6.KV/433V. But, I am getting only 395 Volts when load. How to calculate voltage drop and what is the permissible voltge drop for this circuit?
what is the k var ratting of 1250kva
why EMF IS INDUCED IN A CONDUCTOR WHEN FLUX LINKING WITH IT CHANGES ACCORDING TO FARADAYS LAW.
say a transformer is designed for 33/11kv step down with ratio 0.33 for load 1 mva. if am giving 11kv as a input that same transformer what will happen to its o/p voltage. and whether it can be operated for 500kva
Where double earthing is required? Is there any power specification to have double earthing?
Which type of a.c motor is used in the fan (ceiling fan, exhaust fan, pedestal fan, bracket fan etc) which are find in the houses ?
hi pal, i am vengatesh from tamilnadu(chidambaram),i have called for the written test for the post of jr executive(ELECTRICAL) of AAI ,I dont know about the question paper pattern,so any kindly help me to face the examination,post me the model question papers and some tips to write my examination to (vengi.annadurai@gmail.com)
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)