WHY THE TRANSFORMER VALUE MEASURES IN KVA INSTEAD OF KW.
Answers were Sorted based on User's Feedback
Meenakshi my view is also very much in line with you said
but addition to above i like to add that the transformet or
a generator are a source and are designed for the load
according to the characteristic & they have nothing to do
with the power factor . As the power factor is not counted
they rated in KVA ( Because KW = KVA x PF vise versa KVA =
KW/PF ) Please correct if something more can be added.....
Is This Answer Correct ? | 10 Yes | 3 No |
any device that acts as a source vil be rated in kva,n
hence transformer,generator,ups etc are rated in kva. n its
not becoz of copper loss n iron loss stories as mentioned
in some books.coz when i answered like this, i was told
wrong.if any improved answer, plz notify me.
Is This Answer Correct ? | 5 Yes | 2 No |
Answer / jk
POWER GENERATOR AND POWER USER RATING IN KW
AND POWER TRANSMITTAL DEVICE IN KVA BCOZ THERE IS NO ROLL
OF PF
Is This Answer Correct ? | 0 Yes | 2 No |
What is instrumental error?
What are documents to be required for export of the material?
Electricity sometimes can be dangers , sometime got shoked form it . It is because of volatge or Current
What is mean by power factor?
18 Answers Shreem Electric Ltd,
wil a dc motor run without a starter??
if dc excitation is used to produce manetic flux in rotating machines then ehy it is not used in transformers.
if a 3phase 100kva distribution transformer , 400 v,50 hz, 4-wire system is loaded at 160 k.w mostly 1-phase Lighting & Airconditioning split a.c load what will be the net effect on the power system in terms of voltage, powerfactor, current , efficiency of xformer
TRAFO 1. WHY BREATHER IS USED. 2. WHY OIL GOES DOWN IN CONSERVATOR TANK. 3. WHY WE ARE TAKING OIL SAMPLE TAKING FROM BOTTOM OF TRANSFORMER. 4. HOW TO CHECK IR VALUE OF TRANSFORMER. 5. WHY OLTC HAVING BUCHHOLZ TRIP ONLY; WHY NO ALARM. 6. OFF LOAD TAP CHANGER OPERATION PROCEDURE. 7. TR. SHUTDOWN / ISOLATION PROCEDURE. 8. WHEN THREE TRS. IN PARALLEL, ONE TR. IS NOT SHARING THE LOAD – WHAT IS REASON AND WHAT YOU WILL DO. 9. WHY TR. HAS OLTC IN HV SIDE. 10. WHAT IS % IMPEDANCE. 11. WHY TR. RATING IN MVA. 12. WHAT IS VECTOR GROUP IN TR. 13. CONDITION FOR PARALLEL OPERATION OF TRS. 14. WHAT IS TERTIARY WINDING. WHERE IT WILL BE. 15. IF TR. TRIP ON BUCHHOLZ OR TAP CHANGER RELAY, WHAT YOU WILL DO. 16. DIFFERENCE BETWEEN OIL TEMP. AND WINDING TEMP. PROTECTION 17. HOW WINDING TEMP. IS MEASURED IN CAST RESIN TR. 18. DIFFERENT TYPES OF FAULTS IN TR. Trafo - Page-1 of 2 19. WHAT HAPPENS WHEN TR. CHARGED FROM LV. 20. WHAT WILL YOU DO IF MEGGER READING SHOWS ZERO BETWEEN LV WINDING AND EARTH. 21. CAN WE INTERCHANGE BUCHHOLZ RELAY OF MAIN TANK AND OLTC TANK. 22. IF THE LINE BETWEEN BREATHER AND CONSERVATOR TANK 23. LOCKED, WHAT WILL HAPPEN DURING LOAD CYCLE. 24. WHAT IS THE FUNCTION OF OIL SEAL IN BREATHER. 25. WHAT ARE LOCATIONS FOR BUCHHOLZ RELAY FIXED IN POWER TR. 26. WHAT ARE CHECKS IN POWER TR. DURING MAINTENANCE. 27. WHAT IS IMPORTANT WHEN WE CHECK OLTC OPERATION DURING MAINTENANCE. Trafo - Page 2 of 2
What are the different types of trap used for Indian & western Toilets?
WHY SEPARATELY EXCITED MACHINE NEEDS EXCITATION BY DC SUPPLY WHY NOT BY AC
Why transformer rating in KVA? and Generator also?
6 Answers Bhel, IEEE, Toyo Denki, Toyo Engineering,
What is the difference between air & vaccum circuit breakers?