if a damaged 500kva transformer with %impedance 2.6 is
replaced by two transformers of 250Kva with different %
impedance will they be able to catter the load. what will
be the ratio of load on the two transformers if the %
impedance is in the ratio 1:2
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
The above is correct.But transformers with same capacity and
voltage having % impedances in the ratio 1:2, is not
believable.The load sharing will be in 2:1 ratio if they are
connected in parallel.
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / aamod tripathi
This should not be done ideally (Parallel operation not
permitted) . However the load can be distributed exclusively
and independently on each transformer (Each Transformer
connected to indivisual (incomer) feeder and independent
loads(outgoing))
| Is This Answer Correct ? | 4 Yes | 5 No |
why we do occ & scc test in transformer ?how we can do it ?
How Load Factor, Demand Factor, Diversity Factor etc best applied in designing an electrical circuit? Is it allowed to consider these factors in each and every panel in an electrical distribution system? Can any body suggest a good book for reference?
Dear All, Can anybody please tell me which value(saturated or unsaturated) of sub-transient reactance(Xd") we take for the calculation of fault current of the system?
in what type of applications v can use q meter?
a. void main() { char a[6] = "INDIA"; while(*a) { printf("%c",*a); a++; } } 1. india 2. I N D I A 3. no output 4. error 5.Null
Please help me regarding my one concern. - During earth pit testing we noticed that the Clean earth pit and dirty earth pit showing continuity (Resistance value - 5ohm) . I want to know that if both earth pit have separate location and there is not internal looping between PIT then why such continuity is showing on it . Because of this issue the field side all earthing point showing short. In PLC panel we are providing two types of earthing cable which is coming from separate earth pit (Clean and Dirty earth pit) because of earth PIT showing short our PLC is not complying spec . please help regarding this issues.
what is the earthing condition between earth & phase.
What Should be the value of Vector Surge angle at Tripping and how to calculate it?
Can 60 Hz transformer be used inplace of 50 hz transfromer?
What is ONAN/ONAF1/ONAF2 for transformer cooling
in our transmisison sub station why we step down firstly 132kv\33kv then 33kv to 11kv. can we direct step down 132kv to 11kv.
(1) From the following option, which option is correct for largest size transformer.? a)1KVA,25Hz , b)1KVA,50HZ , c)1KVA,60Hz , d)1KVA,100Hz
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)