if a damaged 500kva transformer with %impedance 2.6 is
replaced by two transformers of 250Kva with different %
impedance will they be able to catter the load. what will
be the ratio of load on the two transformers if the %
impedance is in the ratio 1:2
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
The above is correct.But transformers with same capacity and
voltage having % impedances in the ratio 1:2, is not
believable.The load sharing will be in 2:1 ratio if they are
connected in parallel.
Is This Answer Correct ? | 3 Yes | 2 No |
Answer / aamod tripathi
This should not be done ideally (Parallel operation not
permitted) . However the load can be distributed exclusively
and independently on each transformer (Each Transformer
connected to indivisual (incomer) feeder and independent
loads(outgoing))
Is This Answer Correct ? | 4 Yes | 5 No |
acb(AIR CIRCUIT BREAKER)NOT CHARGING AUTO
Why transmission line carryiny high voltage and low current?
3 Answers apspdcl, Universal Power Controls,
Is it possible to get earth resistance value"zero" Ohm practically??? If yes,which type of earthing???
how to select size of hardware for linking aluminium busbar is it depend on area of busbar or current flowing through bus bar
what is Thermocouple? Type of its.
What is difference b/w Microwave and OPGW ??
how many mega ohms insullation of the cable can't be use when testing with megger tester for Low voltage cable 240V use?
mounting of bucholz relay engle on transformer
What is the PI test stand for transformer and what is the producer to do this test?
Is single load(eg: three phase motor) having all the components like positive,negative,zero sequence components during fault condition?
How do u term the word 'OF' in Megger Testing???
Can anyone explain, How will get positive to ground and negative to ground reference voltage in dc system