why hv winding is not placed near to transformer core
Answers were Sorted based on User's Feedback
Answer / ma.amulraaj,b.e. mba.,
The previous answer is wrong.Because irrespective of equipment,we have to manufacture any equipment economically.
If we provide the HV winding Near to the core,Suppose the HV voltage is 11000V.We have to provide the insulation between core and HV coil is 11000 V.Then in between HV and LV winding agin we have to provide insulation 11000 V.Here The insulation cost is very high.
In other way ,if we provide LV winding near by core,the LV voltage is 415V,we have to provide insulation for 415 V between core and LV winding only.So cost of insulation is considerabily reduced.
That is why HV winding is not placed near to core.
Is This Answer Correct ? | 86 Yes | 4 No |
Answer / raghavendran.r
One of the reason for that is the practical difficulty in
the arrangement of the Tap Changer, because Tap changer is
placed on HT side for voltage adjustment.
Also the insulation between the Core and the HT winding
has to be thick to withstand the stress.So the size of the
arrangement will be more bulkier.
Is This Answer Correct ? | 34 Yes | 8 No |
Answer / kharwar pritam
if you provide hv winding nearer to the core of the transformer....then the insulation betn core and hv will be THICKER....and hence the cost of insulation will increase..and also the size of the transformer ...after then you have to provide insulation betn hv and lv(it is compulsory to provide insulation betn lv and hv....whatever hv is nearer to the core or lv...but with lv there will be thin insulation betn core and lv...and about tapping.. you can provide taps on any winding..according to your need..).....this all just because of insulation consideration ..!!!!
Is This Answer Correct ? | 16 Yes | 2 No |
Answer / pranay bhaurao thengne
If we placed lv winding placed first to the limb and then hv former and hv winding ...
Due to this arrangement minimises the leakage reactance and leakage flux .
And improves mutual inductance between two windings ...
And also for cooling purposes...
And requires less amount of insulation...
Is This Answer Correct ? | 4 Yes | 1 No |
up to what extwnt of voltage the celing fan works?
IF THE OUTPUT OF A 100KVA, 415V GENERATOR IS STEPPED UP TO 11KV WITH A 500KVA TRANSFORMER,CAN THE TRANSFORMER BE LOADED ABOVE THE SOURCE GENERATOR RATING?
How many types of protection relays are there based on the characteristic?
why do we carry out winding resistance test?
0 Answers MahaGenco, MAHINDRA,
Whis machine is having higher efficiency Transformer or Generator
What is difference between MCB,MCCB,ELCB and RCCB? Brief description and why RCCB is costly?
What is the different between buchholz relay and pressure relief device?
what are the type of motors
What will happen when we will connect lamp in between phase and earth.
In brushless excitation system how generator field current is measure even if the slip rings are absent?
How we calculate the size of H.T cable for any transformer & rating of busbar for any L.T. panel?
What will happened if the neutral of secondary of Xformer ( Star point) Note it's above KVA rated Xformer