Answer / perservance
it is used for earth fault protection,this kind of C.T
covers all the phases ,the secondary side of it is
connected to trip coil of CIRCUIT BREAKER.Under no fault
conditions the vector sum of all the three phase currents
is zero so no output to c.t secondary but when there is a
earth fault ,the sum would not remain zero and the trip
coil would act and circuit breaker would trip.
the disadvantage being that it would not detect phase to
phase fault,seldom used,not seen anywhere in my plant.
Is This Answer Correct ? | 119 Yes | 13 No |
Answer / veerachary
CBCT stands for Core balance current transformer, it is
used in Main incommer pannels as of my experience.
Is This Answer Correct ? | 91 Yes | 28 No |
Answer / sarbani
Core balance CT (CBCT): The CBCT, also known as a zero sequence CT, is used for earth leakage and earth fault protection. The concept is similar to the RVT. In the CBCT, the three core cable or three single cores of a three phase system pass through the inner diameter of the CT. When the system is fault free, no current flows in the secondary of the CBCT. When there is an earth fault, the residual current (zero phase sequence current) of the system flows through the secondary of the CBCT and this operates the relay. In order to design the CBCT, the inner diameter of the CT, the relay type, the relay setting and the primary operating current need to be furnished.
Is This Answer Correct ? | 45 Yes | 7 No |
Answer / maharajan
CBCT is core balance c.t it is used at where we could not
use earth.because at balance condition Ir+Iy+Ib=0 when
balance will be distrube current will be induced in cbct
secondary.
Is This Answer Correct ? | 33 Yes | 13 No |
Answer / abhishek singh
Core balance CT (CBCT): The CBCT, also known as a zero
sequence CT, is used for earth leakage and earth fault
protection. The concept is similar to the RVT. In the CBCT,
the three core cable or three single cores of a three phase
system pass through the inner diameter of the CT. When the
system is fault free, no current flows in the secondary of
the CBCT. When there is an earth fault, the residual current
(zero phase sequence current) of the system flows through
the secondary of the CBCT and this operates the relay. In
order to design the CBCT, the inner diameter of the CT, the
relay type, the relay setting and the primary operating
current need to be furnished.
Is This Answer Correct ? | 16 Yes | 3 No |
Answer / parthsharathi
cbct is core balance current transformer it for earthfault .
sum of all phases zero it ok, if any difference . So trip bkr
Is This Answer Correct ? | 10 Yes | 3 No |
Answer / guru
first time i seen this core balance current transformer from mcc panel. all output cables from through via this cbct. because any earth fault occurs, this cbct generate a current and give to earth fault relay. this relay automatically switch off a rccd breaker.
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / srinivasan rengarajan
it is used for sensitive earth fault protection , especially when the feeder CT ratio is very large & max EF current to be sensed is very low as much as 5A or 10A.. This kind of C.T namely ring type CT encompases all the phase cables ,the secondary side of it is
connected to a sensitive EF relay, whose contact will in turn be connected to trip coil of CIRCUIT BREAKER.Under no fault
conditions the vector sum of all the three phase currents
is zero; so no output to c.t secondary but when there is an
earth fault ,the sum would not remain zero (it would be 3 I0- namely 3 times Zero phase sequence currents) and the trip
coil would act and circuit breaker would trip.
The fact that it would not detect phase to
phase fault,is not a disadvantage, because the very purpose of CBCT is that it is specifically designed for sensitive earth faut protection or earth leakage protection.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / sakka
cbct is very good device. i shall be very thankfull to who invent cbct.
thank u,
your obediently
yatin shah
Is This Answer Correct ? | 4 Yes | 4 No |
Answer / lola pondu
cbct is used to protect the system from earth fault or leakage earth current. Three phases cable passes through the inside the cbct and secondary of cbct connected to the earth fault relay.Under normal condition the vector some of three phases current will zero & while earth fault or leakage occurring the current will passes through the secondary of the cbct which sensed the relay and trip the breaker for protection.
Is This Answer Correct ? | 0 Yes | 0 No |
what is difference between differential protection and distance protection and how we calculate the sloop?
In a Dyn11 transformer, how are the 3 windings of the delta connected? Assume that R1-R2, Y1-Y2, B1-B2 are the 3 windings on the HV side.
Can any body describe me why a soft starter is used for 6.6kv induction motor instead of VFD ?
WHAT ARE THE SITE TEST APPLIED ON A SURGE ARRESTORS? DO MEGGER TEST APPLIED ON SURGE ARRESTOR? IF YES THEN WHAT ARE THE ACCEPTED IR VALUE REQUIRED FOR SURGE ARRESTORS FOR VOLTAGE LEVEL 11KV, 33KV, 66KV 132KV, 220KV AND 400KV?
can volts/Hz be relied upon to use 460v,60Hz electric motors on a 380v,50Hz power supply?
AC is the magnitude of sinosudial-wave but we use cose value to determine power factor instead of sine value.
how i calculate the syncrones generator NGR resistance .if we have a 6mw generator line voltage of generator 11kv also line current 393.3 ampere.
when generator of a power plant is not connected to grid , by increasing the mechanical torque speed of rotor increases but when it's connected to load instead of increase in speed current increases , why?
why most of the modern day type electrical appliance have 2 pins rather than 3 pins?
what type of euse we should use ? 1- High resistance & low temperature 2- High temperature low resistance
in control scheme dc logic wiring commonly using negative loop,what is the reason?if we use positive looping what will happen?
Why inverter rating in KVA?