What is the calculating formula for HT and LT amps in a
transformer.
Answers were Sorted based on User's Feedback
Answer / lokesh ranjith
P=root3 v i cospie
I = P/root 3 . v. cos pi
Is This Answer Correct ? | 166 Yes | 35 No |
Answer / rajesh tewari
CURRENT IN LT SIDE
=KVA *1000/1.732*LT VOLTAGE*COSQ
CURRENT IN HT SIDE
= KVA *1000/1.732*HT VOLTAGE*COSQ
Is This Answer Correct ? | 176 Yes | 54 No |
Answer / baskaran.r
the rating KVA=Root 3*Vl*Il Apply primary and secondary
voltages to get the max. current
Is This Answer Correct ? | 93 Yes | 15 No |
Answer / s.l.bhatt
If the current of one side either primary or secondary is
known than the current of other side will be in same
proportion as the volotage ratio of primary and secondary
side.
For example -for a 1000 KVA 11kv/0.4 kv transformer if there
is 1 amp. current in HT side than current in LT side will be
1x11x1000/400 i.e almost 26 amps.
Is This Answer Correct ? | 55 Yes | 20 No |
Answer / thyagarajan
FOR EXP....
in 50mva trx mean
P= ROOT3 *V*I*COS
50*1000*1000=1.732*110*1000*I
I= 262.4 IN PRIMARY SIDE
50*1000*1000=1.732*33*1000*I
I= 874.8 AMPS IN SEC SIDE
Is This Answer Correct ? | 57 Yes | 25 No |
Answer / raju kumar singh
Let suppose u have taken 1500 kva transformer of 11kv to 415 v u wanna be the current calculation for the both HT side and LT side. But u also think that u have connect load of the transformer 1000 kw. In this case both HT & LT SIDE power drawn is same. But this is three phase so we take formula
P equal to SQ ROOT 3 *V* I COS phai
Remember cos phai is necessary becuse of we know KVA :::: KW/ COS phai
U have connect 1000kw and its drawn full lo
ad then it wil be calculate in HT SIDE
1000*1000:::1.732*11000*0.8* I(u take power factor as0.8)
I::::65.6A
WHILE calculating in LT SIDE IT wil be
1000*1000::: 1.732*440*0.8* I
I:::1739.05A
because power drawn HT & LT SIDE depend on load connected to the transformer
Is This Answer Correct ? | 31 Yes | 9 No |
Answer / balasubramanian
amps in LT side I=P/root 3 * v* cos pie
amps in HT side I=P/root 3 * v* cos pie
Is This Answer Correct ? | 37 Yes | 19 No |
How to convert KVA rating into HP rating?
WHAT IS THE USE OF TERTIARY WINDING IN A STAR/DELTA TRANSFORMER ?
what is accuracy ? in any meters , coils accuracy . how can u defined that ?
when we given 3 phase supply to ups system, but out put comes with 3 phase + neutral how it possible? pls explain.
3 Answers Enzen, Juniper Networks,
why would the rotor rotate at sub synchronous speed against the direction of rotating flux when d rotor of 3 phase IM is connected to 3 phase balanced supply and the stator windings are shortcircuited ??
i want all question & answers of the written exam
1 Answers Essar, L&T, MES, RRB,
how to calculate AH of a battery?
in HT service 3ph 4 wire service Y-phase voltage shows zero . whether it is meter fault? or what be the reason ? if y-ph voltage zero ,can current is recorded? reasons for failure?
dear all i am kumara now current working in electrical designing of control and relay panel i want learn some substaion design then any book are available. pls mention name and authour
what is the difference between grounding and earthing......how can we differentiate each other.....
What is a neutral
4 Answers Adani Ports, Dr Reddys,
Why temperature rise test is conducted in bus bars and Isolators?