Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Can I use measuring current transformers in protection
purposes?

Answers were Sorted based on User's Feedback



Can I use measuring current transformers in protection purposes?..

Answer / minu

no u cannot. this is because the metering and protection CT
cores are differently designed and r made up of different
materials. A Protection CT core is designed so as not to
get saturated at very high fault currents which can cause
mal-operation of the relay connected to that CT. Also, the
accuracy required in the metering CTs is higher than that
required in the protection CTs.

Is This Answer Correct ?    28 Yes 0 No

Can I use measuring current transformers in protection purposes?..

Answer / ramesh kumar k

Mr.Mohit & Ms. Minnu...

both of u be cool specially... it is not a war field
yaar... ha.. ha...

What ms.minnu said is correct...

u cant use the measuring CT for protection purpose...and
protection ct also can't be used for measuring purpose...
it is not safe...

So Mr. Mohit, from my point of view what you have might
done is.. u have used a CT which u have purchased for
measuring purpose, but still having a additional core for
protection and u might have shorted the metering core
terminals and used the protection core only.. if you have
not used so... I think your system is still safe because
there is not shortcircuit fault tilltime... its very
dangerous if any short circuit occurs... because a metering
CT core is designed in such a way that if there is any
shortcircuit.. it gets saturated and doesnot deliver any
output... if u use this for protection purpose your relay
will not get current(i.e. it gets 0 A which is nothing but
no load condition..). But your relay is set to operate only
in over current conditions... so now what happend.. even in
over current condition, your relay is not getting over
currents hence it will not send any signal to the circuit
breaker...

I suggest, in this regards, u please consult ur higher
authorities...

Ms. minnu, i think we have not studied enough on CTs & PTs
n our basic engineering study...

P.S:
I welcome u both for further clarifications, mail me at
rammy_233@yahoo.com

Is This Answer Correct ?    12 Yes 0 No

Can I use measuring current transformers in protection purposes?..

Answer / minu

Mr. Mohit,
i am working as a power system protection engineer in one
of India's biggest consultancy firms. wat u said abt
increasing the no. of cores of a ct does not mean that the
metering n protection cts are same. n i think u've
forgotten ur basic engineering study wherein we were taught
abt the basic differences in metering and protection cts. u
can still find them in any gud power system book.

p.s. its Miss Minu, not Mr. Minu

Is This Answer Correct ?    8 Yes 0 No

Can I use measuring current transformers in protection purposes?..

Answer / sangram

you can use a single CT but they have enclosed two
different cores which is desired one for metering & other
for Protection. the meaning of both words are very
different, we want to consider ISF( Instrument Security
Factor) for Metering & ALF( Accuracy Limit Factor) for
protection CT.

Is This Answer Correct ?    4 Yes 3 No

Can I use measuring current transformers in protection purposes?..

Answer / j.karthik(cce)

Mr.Ramesh kumar said answer is very correct..

We cannot use the Measuring C.T. for the protection
purpose.and we also cannot use the protection C.T. for
Measuring purpose.

Protection C.T Classes are:
CL 5P20
CL 5P10
CL PS

Measuring C.T Classes are:
CL 0.2
CL 0.5
CL 1.0

Generally the Measuring C.T's and Protection C.T's are
differentiate by using the C.T Classes..

Is This Answer Correct ?    1 Yes 0 No

Can I use measuring current transformers in protection purposes?..

Answer / mohit varshney

Mr. Minu.....
I am working as a commissioning engineer in in switchyard
in 2x600 MW thermal powerplant. i have myself done the ct
commissioning here. if u want i can send u proof of wht i
have answered to this question...so better check ur
credentials and dont mislead ppl.

Is This Answer Correct ?    2 Yes 6 No

Can I use measuring current transformers in protection purposes?..

Answer / mohit varshney

Yes u can....
u can increase the number of secondary cores....
for e.g. u can use 5 core CT in which 4 are used for
protection purpose and one is used for metering(measuring)
purpose.

Is This Answer Correct ?    6 Yes 17 No

Post New Answer

More Electrical Engineering Interview Questions

how can we check the earth resistance

3 Answers  


How can you test the vector group of power transformers?

2 Answers  


what kind of quetions will ask in BHEL in interview? Plz help me?

0 Answers   Bhel,


which starter is used for synchronous motor

18 Answers   APTransco, IBM,


A 100KVA SINGLE PHASE TRANSFORMER 10000/200V,50HZ REQUIRES 300V AT HV SIDE TO CIRCULATE FULL LOAD CURRENT WITH LV SHORT CIRCUITED.THE INTAKE IS 1000W.THE % OF REGULATION ON FULL LOAD AT 0.8 PF LAGGING WILL BE HOW MUCH AND THE SECONDARY TERMINAL VOLTAGE ON 0.8 PF LEADING WILL BE

0 Answers   IAS, TATA,


sir please send me previous year questions of jspl of electrical section through which i could prepare myself fpr the test.

0 Answers  


What is class ab operation?

0 Answers  


what is the difference b/w ground & virtual ground?

0 Answers   Accenture,


Draw an S.L.D of the main panel for a hospital, showing meter position. Essential loads are: 1) Equipment load 100 KW 2) Critical load 500 KW 3) Life AID Safety load 400 KW 4) NON-Essential load 200 KW 5) Other service loads 200 KW Calculate and suggest the size of the transformer, size of main cable, capacitor bank, and calculate the capacity of an emergency load having above first three mentioned loads is supplied by an emergency generator.

0 Answers   FEWA, HMK,


we convert 66kv to 33kv then 33kv to 11kv,11kv to 440v.why not we convert directly from 66kv to440v?

7 Answers   HCL, L&T,


when giving a supply to wounded coil it will get magnetised, but the same is not if it is not wounded on a core..and it is getiing short....why.......

3 Answers  


How do we calculate the out Put voltage of generator, after excitation being given?

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)