I have AC automatic voltage regulator 15KVA
What output currant?
Answers were Sorted based on User's Feedback
Answer / muzamil
if voltage regulator is single phage..in think its out put
I=kva*1000/230=65.21 amps...in full load,
if regulator 3 phage...I= kva*1000/415*1.732*pf*eff
=15*1000/415*1.732*.85*.85
=28 Amps.
Is This Answer Correct ? | 7 Yes | 2 No |
Answer / rajkumar
we should convert that kva to kw,
Power (KW) =KVA*pf
=15*0.8
P KW =12.
then,
P=1.732*V*I*COS*EFF
we need current,
I= P/1.732*V*COS*EFF
= 12/1.732*415*0.8*80%
= 17.7 A
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / deepanshu tiwari
for even 3-phase you don't divide "KVA" by p.f , so the current for 3 phase will be :
i= KVA/(1.713*line voltage)
i = (15 * 1000) / (1.713*line voltage(415V))
= 21.10 A
Is This Answer Correct ? | 0 Yes | 2 No |
. Draw the vector diagram and condition for the following: 1) Dyn1 2) Ynd0 3) YnYn0
Which contains in POLE ASSEMBLY of a 11KV Kirloskar-make SF6 (Model No-FP620A12)? Will u clarify with drawing?
Why 3 over-current and 1 earth fault relay is used on primary side of transformer? Why 2 over-current and 1 earth fault relay in used on secondary side of transformer?
1. Synchronization is not required A. Thermal B.Hydel C.Wind D.Nuclear
2 Answers APGenco, Birla Power,
WHAT IS THE USE OF STARTER AND CHOKE IN TUBE LIGHT?
how to crack cgpsc,which type of knowledge it is required,where i can get systematic study material and some tips?
DIFFERNCE BETWEEN DCS AND PLC? HOW IT WORKS?
which on of the transformer have more core losses and why? 1. Distribution Transformer 2. Power Transformer
What is nyquist contour?
In any plant or substation main incommer voltage RY - 415 V,YB - 400 V, BR - 387 V(in commer feed from transformer 11 Kv /0.415 KV) why found voltage differance in each phase? plant have not self power plant it is depend on outsource grid
why we can not use dc in our country( INDIA)
cb used in railway applications is?