Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


What is the reason for low voltage in houses?

Answers were Sorted based on User's Feedback



What is the reason for low voltage in houses?..

Answer / excellenceokoli

There are many causes
of low voltages. Some of
them are:
1). Overloading of a
particular phase.
2). Cable size.
3). Phase failure
4). Rust and worn out
cables.
5). Loose connections.
6). Neutral failure.

Is This Answer Correct ?    51 Yes 0 No

What is the reason for low voltage in houses?..

Answer / murali

* We using many indutive loads(FANS,ANY MOTORS)
so powerfactor is below 0.4 (leading current in voltage)
so produce voltage drops
* Using capacitors in parallel to the loads
improve the powerfactor
* loads are properly divided reduce the voltage drops

Is This Answer Correct ?    35 Yes 16 No

What is the reason for low voltage in houses?..

Answer / anand

Thhe probable reasons of low volage in houses are:
a)One of the phase on HT syde of transformer disconnected
because of breaking of jumper/HT fuse
b) excessive load on that particulr phase to which house is
conected
c)lower size of LT cable/ OH conductor selection resulting
in high voltage drop

Is This Answer Correct ?    18 Yes 7 No

What is the reason for low voltage in houses?..

Answer / renyrjn

i think inductive load might be the right answer

Is This Answer Correct ?    7 Yes 3 No

What is the reason for low voltage in houses?..

Answer / sakira

electricity is nothing but the energy generated at station.
when it is transfer to home it goes from stage to stage.
the potential difference is decreasing at every stage to
maintain the current going in back to ground.
1) Possible reason is poor grounding OR NEUTRAL.
2) In the area use of high power devices(floor mile, lath
machine)
3)low current capacity cable wiring in the house.

now a days electricity is stable at various places in the
villages it is still high or low voltage.
use the stabilizer (servo stabilizer) use some branded one
as even local one is cheaper they not use the protection or
the radition protection.

Ultimatly good design and manufacturing the with good
components are different.

Is This Answer Correct ?    6 Yes 2 No

What is the reason for low voltage in houses?..

Answer / ravi kumar

Excessive load of a conductor beyond its rated capacity
causes voltage drop at other end

Is This Answer Correct ?    18 Yes 15 No

What is the reason for low voltage in houses?..

Answer / sanjeet swarnakar

due to inductive load
power factor decrease

so voltage regulation is required to make up the loss of
voltage

please tell me ur email ID
my email ID is sanjeet.swarnakar@gmail.com

Is This Answer Correct ?    13 Yes 10 No

What is the reason for low voltage in houses?..

Answer / rk sharma

Inadeqately distribution of load in LT side.

Is This Answer Correct ?    6 Yes 5 No

What is the reason for low voltage in houses?..

Answer / arif pathan

There are many reason for using Low voltage(415V,3ph)in
Houses:
1) Due to use of 415v at LV side of tranformer the Fualt
level & short cicuit current will be less compare to HV
side , hence you will require small size of cables upto
your main distribution panel.
2) If your short circuit(kA)& fault Level(kVA/MVA)is less
you reqire small rating of CB or SFU for protection.
3) Due to 415V (L-L) your operating devices, equipment can
run on 230V (P-L) For which they are designed.

Is This Answer Correct ?    5 Yes 4 No

What is the reason for low voltage in houses?..

Answer / dk

1--h.t. side fuse of transfarmar
is disconnected
2--high inductive reactance equipment

Is This Answer Correct ?    4 Yes 4 No

Post New Answer

More Electrical Engineering Interview Questions

We have drive feeding an output contactor for a 5000 hp motor @ 5kV application. The motor FLA is 629amps x 1.25% service factor = 786.25 amps The cable that we current have in place between the drive and the output contactor is 350kcmil- MV-105 (parallel cables). Per the NEC table 310.60 (C) (69). This show the cable ampacity is at 615 amps per cable for a rating of 1230 amps. We have derated the cable for the cable tray and the multiple cables application and our calculations show that after the correction factor factor we are at 922amps. 1230 amps x .75% correction factor factor = 922.5 amps. The customer is driving us to then use another safety factor of .25% off of the already derated cable. Can you please provide a longhand calculation for your solution on this application?

0 Answers   Siemens,


Is there any rule to select the voltage of motor based on KW rating? What is the rating above which lt motor becomes the HT motor?.

0 Answers   DAE,


How can we check ELCB trip current sensitivity How can we check earth resistance value

2 Answers  


Briefly define and explain the following different types of Pulse Amplitude Modulation (PAM) with some examples. i) 2-PAM ii) 4-PAM iii) 8-PAM iv) 16-PAM v) Quadrature Amplitude Modulation (QAM)

0 Answers   UOG,


at what rate the micro controller increment its timer....is it 1micro seconds or 1/(12*10^6) seconds

0 Answers  


If 22 KV HT line, Current transformer is 25/5 then how to calculate multiplying factor.

0 Answers  


WHAT IS A BASIC DIFFERENCE BETWEEN THYRISTOR,TRIAC AND A DIAC.AND WHAT R THERE APPLICATIONS?

5 Answers   Petronas, TCS,


Why auxiliary transformers are not connected in parallel in primary stations?

0 Answers   Adweb,


What does quality factor depend on in resonance?

0 Answers  


how to calculate cable size with respect kw

0 Answers   SPMI,


whate is the meaning of balance/unbalance,in stabilizers type

0 Answers   TCS,


What is the min.& max distance between two earth spikes is required for measuring earth resistance of an earth pit? Is the manufacturer of Earth tester decides this? Pls explain.

3 Answers   ABB, HAL,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)