Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


How open delta used for protection?

Answers were Sorted based on User's Feedback



How open delta used for protection?..

Answer / madhu

the neutral grounding transformer is star connected on the
primary and has an open delta on it's secondary.Open Delta
has two terminals.A resistor is conected across these two
terminals. whenever a fault occurs, an emf will be induced
in the open delta and there will be a voltage drop in the
resistor connected. this voltage drop will be sensed by the
potential transformer connected across this resistor. at
the secondary of the potential transformer we have the
neutral displacement relay which will give a trip signal or
an alarm whenever its settings exceed a particular value.

Is This Answer Correct ?    46 Yes 4 No

How open delta used for protection?..

Answer / m.babu

By giving these two wires to Neutral displacement relay.
in the event of earth fault condition some voltage appears
across the relay and it will trips the circuit breaker.
In healthy condition '0' volts across the relay.

Is This Answer Correct ?    26 Yes 3 No

How open delta used for protection?..

Answer / gunasekaran

at balance condition voltage appear across the open delta
connection is zero at fault candition no longer zero.
so we r using this open delta connection for resudial over
voltage protection.

Is This Answer Correct ?    23 Yes 0 No

How open delta used for protection?..

Answer / k.prakashchandra

This relay is used for stator earth fault protection for
generators.The vector sum of three phases in all corners of
delta connected PT secondaries is zero.One of the corners is
taken through a voltage relay.Operation is as above.

Is This Answer Correct ?    9 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

why skin effect is decreases with decrease with frequency? why skin effect occur

5 Answers   Kirloskar,


what is magnetizing current test in power transformer

0 Answers   ABB,


Why do we need ring main unit (RMU). what is its purpose and its advantages . what is the operating function of rmu

6 Answers   MahaDiscom,


there is an alternator 480 k.w, 400v,50hz, 4-wire running on load having leakage alternator body earthed current 38 A. is it within acceptable limit? if yes then give reference if no then how to bring within specified limit

0 Answers  


can u tell the difference between star-star transformer and delta to delta transformer.

3 Answers   Videocon,


what is the meaning of the HT LT transformer?

10 Answers   Sify,


in ACB breaker requireding 3200Amps. buscoupler getting OFF mode and again it reset and getting normal position give me a required answer?

0 Answers  


Why the transmision line are 11,33,63,132kv?

10 Answers   Power Grid,


Sir, Please tell me that how I will calculate the efficiency of rectifier. Because input is ac and output is dc. Is it right to put two unlike signal together.

2 Answers  


How can CALCULAT the current carrying capacity of aluminum and cOpper cables respective of that Sq.mm ? with formulas ?

12 Answers   Bajaj, Eagle, Godawari Power and Ispat, Havells, L&T, Mascot, Polycab, SGML, Sterling Wilson,


What is the permissible limit of shaft voltage for 6.6 KV motors ? Why? Is there any standard is available?

0 Answers  


How much allowable difference current between on three phases Dear sir, We have a 1870 KW HT motor, 11 Kv supply,FLA-120A,2870 rpm,2-pole squirrel cage induction Motor.And stator is connected in star connection with Liquid resistance stater to limit the starting current.It has coupled with Centrifugal air compressor.My question is it is loading 73% of FLA taking R-phase 86.7 A, Y-phase-85.4A,B-phase- 78.3A.why the B phase current is that much of difference.Is it allowable, or any one tell me how much allowable current.If any method to calculate.

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)