Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


in GEAFOL Cast-Resin trnaformer of 11/.72kv which has
tapping of 11550v,11250,11000,10246v in primary side. To
obtain 700v. which tapping should be used of HV side as we
have 11000v/720v tapping now .



in GEAFOL Cast-Resin trnaformer of 11/.72kv which has tapping of 11550v,11250,11000,10246v in prim..

Answer / 7anoter4

If the primary voltage [supplied by Utility] it is NOW 11
kV and your transformer at no-load shows 720 V at its
secondary terminals the ratio primary/secondary voltage is
11/0.72=15.278. If you want to reduce the secondary to 700
V you have to change the ratio to 11/0.7=15.714.

Let's say the rated secondary voltage [at no-load] is 720 V.

That means the ratio 11250/720=15.625 it is the most
suitable and you'll get 11000/15.625=704 V at secondary
terminal [at no-load].

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

what is the difference between a race around condition and toggling?

1 Answers  


Which motor will you choose which can operate in both lagging as well as leading power factors?

0 Answers   HPCL,


What is double delta conection in AC Motor? And can we done the double RPM of the motor by double delta conection?

1 Answers   vguard,


What is the function of PMG in DG sets & how it works??????????

2 Answers  


WHAT IS OLTC OF TRANSFORMER? WHERE IS ITS USED EITHER ON PRIMARY OR SECONDARY SIDE OF TRANSFORMER?

2 Answers  


If the capacitor bank is installed in switchyard say 132/22kv then on LT side say 22kv/0.433kv is it necessary to install capacitor bank for maintaining power factor. if pf is maintained on HT side then will that be maintained on LT side as well.if not then how&why??????/ please explain...........

3 Answers   MacLellan,


how i prepare for the written test in mahagenco?

2 Answers   MahaDiscom, MahaGenco, Wipro,


why the starting voltage drop in a cable needs to be limited?what is percentage of the voltage drop allowed during starting?

0 Answers  


We have a 12MW power plant & we inject 5-6MW power to Orissa GRID. For this we have a 33KV/11KV switch yard having 12.5MVA power transformer. Some times we draw power during emergency. It is observed that during Export or Import for load less than 500Kw the power factor is decreasing to 0.3 . This is happening only during export or import. During island condition TG power factor OK.Our capacitor bank is provided with our Power plant auxilliary load. Please suggest how I can we improve our power factor during low load (GRID).

3 Answers  


What is difference b/w fuse and breaker?

3 Answers   Jindal,


Even when a particular generator in a generating station is under maintenance we are still able to maintain the same power output. How is this possible? Does the tie line between 2 generating stations have a role to play in it?

1 Answers   NTPC,


why ac supply neutral should earth not in dc (-)

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)