in GEAFOL Cast-Resin trnaformer of 11/.72kv which has
tapping of 11550v,11250,11000,10246v in primary side. To
obtain 700v. which tapping should be used of HV side as we
have 11000v/720v tapping now .



in GEAFOL Cast-Resin trnaformer of 11/.72kv which has tapping of 11550v,11250,11000,10246v in prim..

Answer / 7anoter4

If the primary voltage [supplied by Utility] it is NOW 11
kV and your transformer at no-load shows 720 V at its
secondary terminals the ratio primary/secondary voltage is
11/0.72=15.278. If you want to reduce the secondary to 700
V you have to change the ratio to 11/0.7=15.714.

Let's say the rated secondary voltage [at no-load] is 720 V.

That means the ratio 11250/720=15.625 it is the most
suitable and you'll get 11000/15.625=704 V at secondary
terminal [at no-load].

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

what is different between kvar & micro farad when its comes across the capacitor rating is it possible to convert kvar to mf or mf to kvar

1 Answers   Manipal University,


what is doubling factor in making current of a breaker?

0 Answers   BARC,


What are safety seals?

1 Answers   HSL,


List any four conventional sources of energy.

1 Answers  


1)How much current can a 3-1/2 core 100 mm wire carry? 2)What are the special cables required for explosion proof wiring? 3)In case you do not have coal and salt for earthing, how can you achieve good temporary earthing? 4)One horse power single phase motor is more likely to get hot than a one horse power 3 phase motor. Is it true or false, if true why? 5)What are the different types of soft starters for large motors?please explain?

0 Answers   TATA,






How can we measure MVAR of a 3 phase transformer.....???

1 Answers   JLL, UPPCL,


At what voltage domestic tubelight works?

2 Answers   Cigfil, L&T, MNC,


In ac circuit R,L,C are connected in series what is the output the circuit? explain

4 Answers  


what is the current law ?

4 Answers   Aster, TCS,


what type of euse we should use ? 1- High resistance & low temperature 2- High temperature low resistance

2 Answers  


How the Transformer oil testing is done & Why oil dielectric goes LOW & what is solution for that ??

3 Answers   NTPC,


Short circuit current of 2500 KVA 11/0.415 KV transformer both Secondary and primary side. best regards. Ali

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)