when motor taking high amp what happen.
Answers were Sorted based on User's Feedback
Answer / arockia doss
Reasons Behind :
1. Loose Connection
2. Three phase cut into two phase
3. Winding Failure
4. Mechanical Damage/Overlaod
5. Higher Voltage/Frequency
If its so ,Breaker should get trip. If not it will damage
the motor.
Is This Answer Correct ? | 17 Yes | 3 No |
Answer / pillay
that means the motor is finding it harder to maintain
the speed. it could be due to so many reasons as already said
by DASS and VENKAT.
What happens is if any of the motor protective devices dont
trigger the motor to stop than it will continue to run
until the windings give way due to overheat and finally insulation breakdown which is commonly known as burnt.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / venkatesh sk
moto should be terminal loose& connetion&load more &
frquency very&motor capacity low& voltage low
Is This Answer Correct ? | 7 Yes | 5 No |
Answer / gagan kumptar gua
when a motor take high current the wiring of the winding
will be burnt becouse H is proposnal to square of
current.it happens due to loose connection or over load and
change in frequency of voltage.
Is This Answer Correct ? | 1 Yes | 0 No |
Sir We have a REF relay connected to 10MVA(Y-Y) Transformer.on External earth fault REF relay trips along with earth fault relay.The REF relay has no complant as we tested relay.Why is it happening?
What is annunciator ?
what is the meaning of the HT LT transformer?
Why only sinusoidal ac voltages are generated?why not triangular or sawtooth?
what is the formula to calculate voltage drop/loss on 66KV Transmission Line?
differentiate between remote backup relay and local backup relay?
how many desk top computer can connect to a 25kva 3phase generator?
The SFC of an engine is 0.25 kg/kW hr. when the fuel used has a calorific value of 36000 kJ/kg. the thermal efficiency of the engine is
how to find the 2500 KVA transformer rated primary and secondary volt and current?
Why transformer is rated in kva?
anti pumping relay function
why three phase three wire system probably did'nt have neutral