sigal phase supply is 230 v ac
two phase supply is 415 v ac
why three phase supply is 415 v ac why not 690 v ac
Answers were Sorted based on User's Feedback
Answer / prmeghwanshi
Because you measure voltage between onlt two point like RYB
when you connect N to any other RYB then voltage is 240V
(App.) this is called single phase.
when you connect one point into RYB(R) and other is also RYB
(other than R) is 440V this two phash. when you use three
phase voltage is measure in only two point like R to B R to
Y so it is also 440V. you can't measure voltage betwween
three point.
Is This Answer Correct ? | 15 Yes | 4 No |
Answer / vasi
If Phase-Neutral voltage is 230v then Phase-Phase voltage in
3ph system willbe sq.root of 3 X 230v
The 3 ph are displaced 0-120-240 degrees and the Pitagor
Theorem can be used to count up the Line voltage
Another way to count up the Line(Phase-Phase) voltage is to
use vector analysis
1st Phase 0 degree 230+j0
2nd Phase 120 degrees cos120*(230) + sin120*(230) this gives
-115+j199
3rd Phase 240 degrees cos240*(230) + sin240*(230) this gives
-115-j199
in the end ph1-ph2 398v, ph1-ph3 398v, ph2-ph3 398v
Is This Answer Correct ? | 10 Yes | 1 No |
Answer / arvind
its a very good question, see what we r measuring is phase
to phase voltage, in case of 3phase system,that means
beetween two phase is simple because we have two points of
voltmeter to measure the voltage.
Is This Answer Correct ? | 1 Yes | 5 No |
10Hp, 3-phase, 415v, 50Hz induction motor. The above motor is to run on Star-Delta connection, so how do i make following hardware selection 1) MCB, 2) Contactor, 3) Wire Gage (Depending on P-P current or Line Current), 4) OLR, Please tell in detail how to do the above, so as to get the ans. of it even if the Hp rating changes.
which type of motor is suitable for water pump?
How to calculat the ratio of HT\LT in energy meter
The following equipment are installed ia a plant 1. 110KW Induction motor 4 Nos 2. 30 HP motor 3 Nos 3 15 HP Motor 3 Nos 4 7.5 HP motor 4 Nos what is total load of plant if one of each is stand by.
What is four quadrant metering system.
160 kw motor running use 2R* 150 SQ mm cable
generator(Deutz 550kv)is runing for 2 hours with load of 900 amp and then it goes in shutdown with alarm fault messege of speed fault although heirtz reading fixed at 50,what does that mean
We know no of electron and proton in atom but how many Neutron are thire in an atom ?
WHY R USE IN BRUSH IN THE MOTOR?
Actually why the transformers ate rated in KVA.?
2 Answers Torrent Pharma, XYZ,
can a 12v dg starting battery(150 AH) be replace by 6 nos of 200AH batteries each of 2v connected in series.
why the efficiency of the dc machine is high ,when it is operated as a generator?