What is the Diference between DYN 11 and DYN 5 .How to
change the Vector group from DYN 11 to DYN 5.
Answers were Sorted based on User's Feedback
Answer / rushi n. gajjar
dyn5 test of transformer in which some condition like U,V AND W. primary and sec. side we check
1U2W=1U2V;
1W2V<1W2W
1V2V=1V2W we found all this condition in dyn5 test.
dyn11 is vector diagram of 3 phase xmer phase difference 60 degree between R ND Y same way....
| Is This Answer Correct ? | 21 Yes | 8 No |
Answer / kobena wiredu
DYn means a delta-star connected transformer in which the primary is delta connected and the secondary is star connected. The number that follows tells us the position of the Red phase of secondary relative to the primary using the clock (primary Red phase at 12oclock).So Dyn11 means secondary is on the 11 oclock line and hence leads the primary by 30deg since anticlockwise is the convention.To convert from one DYn to the other you need to change both primary and secondary connections. You do this by drawing vector diagrams. By using vector diagrams i find that converting from Dyn11 to Dyn5 means: Change ABC to ACB and change abc to cba.
| Is This Answer Correct ? | 9 Yes | 0 No |
Answer / hemant dehariya
In DYN 11 & DYN 5 is DYN 11 is HV voltage is lead from LV by angle of 30 degree and in DYN 5 HV voltage leg fron LV voltage by 150 degree.we can change vector group from DYN 11 to DYN 5 by change primary winding connection of transformer.
| Is This Answer Correct ? | 21 Yes | 19 No |
what will happen when square wave is fed into input side of 3kva transformer and what you will get on output side.
i installed 100kva ups. what KVA genset they should provid in input side? plz any update formula or ans with reason.
A cotter joint is generally used to transmit
cable armor
Why the transformers making noise?
What is the function of Buchholz relay in transformer ?
Whats the purpose of neutral earthing?
5 Answers Electrical, Hindalco, TCS,
two bulbs of 100w and 40w respectively connected in paralel across a 230v supply.which bulb will glow bright and why?
A 100KVA SINGLE PHASE TRANSFORMER 10000/200V,50HZ REQUIRES 300V AT HV SIDE TO CIRCULATE FULL LOAD CURRENT WITH LV SHORT CIRCUITED.THE INTAKE IS 1000W.THE % OF REGULATION ON FULL LOAD AT 0.8 PF LAGGING WILL BE HOW MUCH AND THE SECONDARY TERMINAL VOLTAGE ON 0.8 PF LEADING WILL BE
is synchrnous pannel is need for two eqal rating transformers to run in parallel
What will happen if we give DC supply to AC motor?
one KVAR takes how much amps, and how to add power capacitors to electrical panels, for example if one of the MCC drawn 800amps means how much KVAR required
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)