What is the Diference between DYN 11 and DYN 5 .How to
change the Vector group from DYN 11 to DYN 5.
Answers were Sorted based on User's Feedback
Answer / rushi n. gajjar
dyn5 test of transformer in which some condition like U,V AND W. primary and sec. side we check
1U2W=1U2V;
1W2V<1W2W
1V2V=1V2W we found all this condition in dyn5 test.
dyn11 is vector diagram of 3 phase xmer phase difference 60 degree between R ND Y same way....
| Is This Answer Correct ? | 21 Yes | 8 No |
Answer / kobena wiredu
DYn means a delta-star connected transformer in which the primary is delta connected and the secondary is star connected. The number that follows tells us the position of the Red phase of secondary relative to the primary using the clock (primary Red phase at 12oclock).So Dyn11 means secondary is on the 11 oclock line and hence leads the primary by 30deg since anticlockwise is the convention.To convert from one DYn to the other you need to change both primary and secondary connections. You do this by drawing vector diagrams. By using vector diagrams i find that converting from Dyn11 to Dyn5 means: Change ABC to ACB and change abc to cba.
| Is This Answer Correct ? | 9 Yes | 0 No |
Answer / hemant dehariya
In DYN 11 & DYN 5 is DYN 11 is HV voltage is lead from LV by angle of 30 degree and in DYN 5 HV voltage leg fron LV voltage by 150 degree.we can change vector group from DYN 11 to DYN 5 by change primary winding connection of transformer.
| Is This Answer Correct ? | 21 Yes | 19 No |
What is the Relation b/w star delta starter , DOL starter and two speed starter. if we want to rotate a 20 kw fan in 2 speeds which type of two speed starter we have 2 use?
We have 750KVA DG set, we want to introduce REF relay with 1250/1A,CL PS,Current transformers.The lead distance of 2.5mm copper flexible cable from CT to relay is around 5mtrs.We would like to know the knee point votage(VK) & IM calculion for CT's
what do u mean by PS-0.2-5P class of Ct
what is acceptance test in electrical engineering.
What is the tipical Online UPS input voltage for 20 KVA load ( 3 Phase or 1 Phase )? Why ? Explain it...?
how to measure the voltage drop in cables also give formulas to calculate.
how many BUSBAR is in electrical system?
Why indicated only R.Y.B to phase.
what is the importance of earthing system on the generators big capacity and small?
What is Chatoliq Protection ?
Why we use Carbon & graphite mixxed brushes in the DC motor?
what is the difference between the characteristics of two different phase bushing of any transformer
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)