when we given 3 phase supply to ups system, but out put
comes with 3 phase + neutral how it possible? pls explain.
Answers were Sorted based on User's Feedback
Answer / vinaysuper2000
UPS Incoming supply Delta connection & Out put supply star
connection.
| Is This Answer Correct ? | 9 Yes | 1 No |
Answer / logesh kumar.a
the input given system has star connection .so it has 3
phase & a neutral
| Is This Answer Correct ? | 10 Yes | 5 No |
Answer / anusree
ups system is a delta star connection , secondary side
grounded in order to allow the flow of zero sequence
currents
| Is This Answer Correct ? | 6 Yes | 1 No |
why using 3 phase
What is mean CT Saturation? How to calculate?
What is gain margin?
I HAVE A INCOMING 100A MCCB TPN 25KA, CABLE LENGHT OF 80M 70MM CABLE SIZE FROM MAIN SUBBOARD TO NEW DB.BASE ON THE FAULT LEVEL SETTING OF 45KA.I WOULD LIKE TO FIND OUT 25KA ENOUGH KA. APPRECIATE IF SOMEBODY CAN ASSIST ME WITH FORMULA FOR THIS. FRM: JEFF
What are the commercial names of overhead conductors used in India?
what type circuit breaker is suitable for connecting 1000A load VCb,Mccb?
our factory is going under construction mean time transformer 1000 kva 2 nos &load break swithch 12 kv & 4 nos 750 kva 2 nos & 380 kva 2 nos generator to be errcted.how to arrange earth pits &how to earth connect & neutral pit how to calculate in earth bit size.
what is relation between HP & BHP
There are two nos of 33Kv/11Kv 5MVA transformers conecting through HT cable from substation having metering at substation itself.One transformer used at a time another remains stand by.Further 11 nos of 11Kv/440V transformers are attached on it and each transformer is having its own Power factor correction panel.Now one 33/11Kv transformer at no load condition/Stand by condition is having power factor in leading side upto 0.21 and while when another tranformer at same situation have power factor in lagging 0.42. Now one thing is clear that transformer one is having 1.5 Km long 33kv cable due to that PF goes in leading side and another is having only 250 mtr length remains him lagging. Now i want to know that how i can maintain the Power factor at no load/ stand by position though both are behaving in seperate manner.
Can we use MCCB with Auxiliary Contact in place of Contactor in a AMF System.
What are the safety equipments you should use while you are in a hvac switch yard
1 Answers GPSC Gujarat Public Service Commission,
What is partial discharge in power cable?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)